Posted by Hywel Evans on 02/02/2017 11:46:02:
Dear All,
Returning to this thread, I have now installed a 0.75 kW 3 phase motor with 1P to 3P inverter on my Viceroy lathe.
….
The full-load current rating for the motor is 3.1 A at 50Hz/230 V. The inverter is set to trip at 5.6 A (180% of full-load current), so when I approach 100 Hz the motor starts to pull about 5.6 A and the inverted trips.
…
This is an armchair offering as I know more about electronics than motors!
It strikes me there are a couple of things that might explain why excessive current is being drawn at 100Hz, whilst all is well below that.
If your motor is a 50Hz type not designed to work with a VFD, taking it up to 100Hz could upset it in various ways.
One possibility is that high voltages generated by the pulse action of the VFD are causing something in the motor to breakdown at higher frequencies. This could be a capacitor, the windings, the cabling, an EMC filter, or some less obvious route to ground. You should be able to detect flashover by putting a LW/MW radio tuned between stations near the motor. (FM and digital radios aren't suitable.) A harsh ripping noise is typical of breakdown; an unpleasant whine is more likely to be the VFD in good health. Also, sparking may be visible if you run the lathe in the dark (but take care) If this is the cause, the cure is to either replace the motor or to keep the frequency below 100Hz.
A second possibility is that the windings are resonating electrically. It's a complete guess because I don't know what the inductance of a motor is. Same cure as above.
As high frequency AC behaves in odd ways the cable between VFD and motor should be as short as possible; reflected volts could confuse the VFD into miscalculating the current.
Dave