To answer NDIY first:
These systems are NOT intended to feed power back into the network for an number of reasons including grid stability. That is one of the reasons why they are limited to one 800W system per circuit.
Some actual legislation that make plug in solar legal links:
https://www.legislation.gov.uk/uksi/2026/848/made (plugs and sockets regulations)
https://assets.publishing.service.gov.uk/media/6a60a03c47af652afa0c89f5/plug-in-solar-final-_interim-product-specification.pdf
Noting that BS7671 (Requirements for electrical installations) is NOT legislation despite what IET want you to think. There is a change in Amendment 4 to allow it.
Basically you can have one system* less than 800W. battery storage is not allowed. and the equipment has to meet the UK product specification.
Of particular note they cannot use a standard 13A plug to connect to the system:
“The inverter should be designed to isolate the output if the grid frequency lock is lost according
to Clause 6.2.3.3 preventing hazardous voltages from being present at accessible plug pins. In
event of failure of the circuit providing this primary contact protection, additional contact protection shall be achieved by one of the following measures:
• A mechanical solution employing a locking mechanism, protective covers or enclosures,
shutter system or equivalent means preventing access to plug pins or other live parts unless the power output from the inverter has first been disconnected.
• An electromechanical solution providing automatic disconnection or separation of hazardous voltages during insertion or withdrawal of the plug. This must operate independently of the main method of anti-islanding as described in Clause 6.2.3.3.3. This shall remove any dangerous voltages from the contacts within 2 seconds ofdisconnection.”
Effectively this means some kind of cover over the live and neutral pins or a electrical cutout in the plug.
In any case the plug must be to to the latest edition of BS1362:
“2.—(1) Regulation 8 of the Plugs and Sockets etc. (Safety) Regulations 1994(3) is amended as follows.
(2) After paragraph (3) insert—
“(3A) Notwithstanding the provisions of paragraphs (1) and (2), a type of standard plug intended to be fitted to or supplied for use with a plug-in microgenerator may be approved by a notified body if when determining an application for approval, the notified body is satisfied that—
(a)plugs of that type do not conform to BS 1363 because BS 1363 contains a provision which prohibits or restricts the use of the plug for the connection of an electricity-generating device to a socket-outlet;
(b)except in respect of that prohibition or restriction, plugs of that type conform to BS 1363;
(c)plugs of that type comply with the Plug-in Solar Device Interim Product Specification; and
(d)by means of inspection or testing of samples of plugs of that type, the manufacturer of the plug may reasonably be expected to ensure that normal production and design of the plug will result in plugs of that type corresponding with the samples.”.”
Note the need for the plugs to be approved by a notified body.
It is not allowed to use a unit designed for use in europe or elsewhere and simply change the plug to a standard 13A one.
I would not pay too much attention to the Jonathan Tracy youtube like posted above. In one of his other videos https://www.youtube.com/watch?v=HN_hZwU17ro he plugs in an illegal home madea system. Not an authoritative source. For a start he says the legal units will connect using “a standard British 3 pin plug” when clearly they cannot.
Not allowed on wooden balconies. Proper attachment no cable ties or bungee cords etc.
Robert.
*product spec says one per circuit (ring main or radial) but GB network connection requirements
restrict this to one per household until corresponding amendments to Engineering Recommendation G98 are implemented.