I have the RCD tripping issues when using my pillar drill with a Parker (Eurotherm) VFD installed. The Telemecanique VFD on my lathe has never caused a problem. Both have an EMC filter installed. My property has a 'TT' earthing system, as the power is brought in on overheads with no direct link back to the substation for the earth, other than that provided by an earth electrode in the ground. As such, the incoming supply is wired through a standard 30mA 80A RCBO, and the entire house goes into darkness when the supply is tripped by the VFD.
I am looking to split the incoming feed, have a time delayed 100mA RCBO installed to protect the installation between incomer and workshop, then install separate 30mA RCDs in the workshop for the sockets and machines. The domestic side of the installation will still be protected by the existing RCBO.
My installation also has 10mm sq SWA cable running between the current consumer unit (via a breakout/junction box) and the workshop. Having undetrtaken a 16th edition course on system design, verification and testing in the past, when sizing the cable there are a number of factors to take into account, not just the current carrying capacity of the cable. These are (but not limited to):
* How is the cable installed. What effect will bundling/installation within walls have on the temperature rise of the conductor and in turn the cable insulation
* What is the voltage drop over the length of the cable run (live AND neutral!) and is it within limits at expected current loading
* What is the earth loop impedance? Will this impedance allow a fault at the far end of the installation trip the protection device within the required time? Will the current let-through cause unacceptable temperature rise in the cable?
Often after working through these calculations, the cable size has to be a lot larger than first expected!
Regards,
Anthony