    Michael Gilligan
    Participant
      @michaelgilligan61133

      Better logic than mine, I think, Simon

      Yes, of course the Blue and Brown should be the 230v input pair

      < blush >

      MichaelG.

      Advert
      #712842
      Ian Parkin
      Participant
        @ianparkin39383

        I’m sure there must be a fault with the transformer…it was sold to my friends as a freeby with the range…its a bugger to get together and i wonder if its not been used since it broke…i wonder if someone had unwired the tranny looking for a fault… the way it looks like its wired to 240v permantely just waiting for the hood to be turned on..not sure that i would want that

        the supply goes straight to the tranny then onto the hood switches

        I’ll see what the company who made it say when i ring back

        #712846
        noel shelley
        Participant
          @noelshelley55608

          Testing the insulation at 3v or there abouts will show a direct short but not a leakage, for this there are tools to do the job, the generic term is megger, though it is also a trade name ! On an RCD circuit if the leakage is about 30Ma or more it will drop. If the unit has been stored in damp conditions, this is possible.  I’ve done my best ! Good Luck Noel.

          #712847
          Maurice Taylor
          Participant
            @mauricetaylor82093

            Hi,

            if the 240volt mains does not power anything other than that transformer ,you could borrow a 110volt site trans to see if the equipment works correctly . A new site transformer could be bought to power it permanently.

            It would be safer as well

            Maurice

             

            #712849
            Ian Parkin
            Participant
              @ianparkin39383

              IMG_5221Well success

              there must have been a loop or wire between the 2 0v’s on the terminal block

              so neutrals to blue 240v to brown

              join the whites together and thats the 110v out

              #712854
              Ian Parkin
              Participant
                @ianparkin39383

                Is putting my meter set to ac current on the input wires …it measures 1/2 amp with no load connected

                is this valid?

                so that could be 3 kw a day?

                #712859
                Robert Atkinson 2
                Participant
                  @robertatkinson2

                  I had not noticed the the connections were unknown. In that case, given the continuity testing and logic of colour codes you have two windings that need to be in series with the two white wires connected together and forming the 115V output, brown wire is 230V “live” input and blue wire is neutral common to bothe output and input.

                  If you have a low voltage transformer, say around 12V output and an AC meter you can check the auto transformer more safely by connecting the mains input (brown & blue) of the autotransformer to the output of the 12V transformer. You should then get 6V AC between blue and white (actually half of the voltage measued between brown and blue).

                  Comment on 60Hz stands.

                  Robert.

                  #712861
                  Ian Parkin
                  Participant
                    @ianparkin39383

                    I was going to put in  a push button to start a contactor with a timer set to say 90 mins so the transformer wasn’t connected permanently

                    so when they wanted to use the hood or lights just press the push button and it would be live for 90 mins then switch off with no-one forgetting to turn off the supply

                    as its just in a domestic environment

                    #712867
                    noel shelley
                    Participant
                      @noelshelley55608

                      I would be cautious of your solution ! Is there 110V on BOTH whites ? So ? Link neutral to both blue (0v) and 0v, 110v is on both whites and fitted to 115v terminal and powers the hood with the 0V and brown is to 230v and to mains supply ? Noel.

                      #712872
                      Ian Parkin
                      Participant
                        @ianparkin39383

                        This is how it’s wired now. Would you say this is wrong?IMG_2109

                        #712874
                        Ian Parkin
                        Participant
                          @ianparkin39383

                          So 240 in to blue (0v) and brown (240v)

                          and 115 out from blue (0v) and the pair of whites

                          #712878
                          Robert Atkinson 2
                          Participant
                            @robertatkinson2

                            Obviously I didn’t type fast enough 🙂

                            Half an amp of no-load current is not unreasonable. However this does not equate to 120 Watts ( I assume you meant 3kW hour per per day). It is not real power because the voltage and current are not in phase so the correct tern is VA (Volt Amps) not Watts. Fortunatly your domestic electricity meter only responds to real power. There is some real power consumption due to the resistance of the copper wire and magnetic losses in the transformer core. Maybe 10-20W still significant,  80 – 100 kWh (units) per year.

                            Robert.

                            #712888
                            Ian Parkin
                            Participant
                              @ianparkin39383

                              So would you ignore the power consumption and just leave the transformer permanently connected?

                              #713018
                              Michael Gilligan
                              Participant
                                @michaelgilligan61133
                                On Ian Parkin Said:

                                IMG_5221Well success

                                there must have been a loop or wire between the 2 0v’s on the terminal block

                                so neutrals to blue 240v to brown

                                join the whites together and thats the 110v out

                                How infuriating … that’s the suggestion that I edited-out  in this earlier post:

                                https://www.model-engineer.co.uk/forums/topic/auto-transformer-help-please/#post-712822

                                … Glad you have sorted it, Ian

                                MichaelG.

                                #713095
                                Robert Atkinson 2
                                Participant
                                  @robertatkinson2
                                  On Ian Parkin Said:

                                  So would you ignore the power consumption and just leave the transformer permanently connected?

                                  No.
                                  If the existing switch in the hood is rated for 240V AC I would connect the transformer after the switch. If it’s not 240V rated I would by-pass the existing On-Off switch and have a switched, fused outlet feeding the supply to the transformer so they have to switch it off.

                                  Robert.

                                  #713111
                                  Ian Parkin
                                  Participant
                                    @ianparkin39383

                                    Robert

                                     

                                    the whole hood is 115v

                                    so I’m sure the transformer was wired into the supply..it has a great big fan 2 heat lamps @250 watts each and 3 tungsten spots. @ 50 watts each

                                    so the transformer is supplying quite a load if everything’s on

                                    i dont want to leave the transformer on all the time and again don’t want to rely on someone switching it off hence my idea of a timed contactor.

                                    heres the diagram for the hoodIMG_5227IMG_5226

                                    #713115
                                    Martin Connelly
                                    Participant
                                      @martinconnelly55370

                                      If you wire it up so one/some of the lights is/are on whenever there is power to the transformer it will encourage people to switch it off when not in use.

                                      Martin C

                                      #713118
                                      Nicholas Farr
                                      Participant
                                        @nicholasfarr14254

                                        Hi Ian, one thing I’ve noticed in your photo above, is the fan blades look as if they have a layer of crud built up on them, this reduces the efficiency of them, and should really be cleaned off, and of course, they will draw a little more power with the extra weight.

                                        Regards Nick.

                                        #713135
                                        SillyOldDuffer
                                        Moderator
                                          @sillyoldduffer
                                          On Martin Connelly Said:

                                          If you wire it up so one/some of the lights is/are on whenever there is power to the transformer it will encourage people to switch it off when not in use.

                                          Martin C

                                          Looking at the circuit diagram, I think it already has that feature.  (Possibly not if they are 3-position switches, centre OFF.)  On the face of it, one switch selects either the right or left heating lamp, so one of them is always on.  And the Halogen lamps are always on, except operating the switch puts a diode in circuit, so the lamps run dim at half-power.

                                          Otherwise, the circuit doesn’t help Ian much because it doesn’t show how the unit is normally connected to the mains.

                                          Judging by the size of the hood, it’s meant for a seriously big kitchen, perhaps a restaurant, and normally part of a planned installation with a dedicated switch-board and distribution system.   The hood might simply be switched on and off with all the other cookers when the restaurant opens and closes.   Not rocket science, but could be a bit more complicated than just plugging it into a socket.

                                          Seems a couple of notches more difficult than fitting an ordinary domestic cooker hood.  Doesn’t help that it’s a US unit with 115V 60Hz internals, needing that transformer AND making replacement bulbs mildly painful to source.

                                          Anyway, I recommend Ian asks the owner what he needs the hood to do.  When is it on, when is it off, and does the way the owner intends to use it require anything more complicated than an on/off switch?  Designing the controls after nailing the requirement avoids discovering flaws in the real word by burning the house down or getting a massive surprise electricity bill!

                                          The cut wires are an alarm.  One reason is that the deinstaller rushed the job and didn’t care because it was going in a skip or because there was a commercial objection to the item being sold second-hand.  That’s OK.   But a major reason wires are cut like that is to stop the item being re-used because it’s faulty or unsafe;  I’d think about that possibility because the installer is held responsible if it goes wrong.

                                          Dave

                                           

                                          #713145
                                          Robert Atkinson 2
                                          Participant
                                            @robertatkinson2

                                            Your transformer is not big enough to supply the lights in that hood.
                                            It needs significant work to use on 240V
                                            It also has a “speed control” for the fan which is another worry on 50Hz.

                                            Have they changed the lamps to 240V versions?

                                            Robert.

                                             

                                            #713170
                                            Peter Cook 6
                                            Participant
                                              @petercook6

                                              Sorry not paying attention!

                                              #713172
                                              Maurice Taylor
                                              Participant
                                                @mauricetaylor82093

                                                Hi
                                                The mains input colours are USA white for neutral and black for live,which are the colours on the diagram.

                                                Like I said before try it with a site transformer .

                                                As usual,every post gets complicated.

                                                Maurice

                                                 

                                                #713178
                                                Ian Parkin
                                                Participant
                                                  @ianparkin39383

                                                  It came from a domestic installation sold on eBay as a freeby with the range the uninstaller i assume had a right job taking this hood apart hence the cut wires and missing screws

                                                  i’m guessing its 60 kg in all

                                                  heres as it was in situ at previous owners

                                                  IMG_0292

                                                  The transformer is rated at 1200VA so what can it supply at 115v

                                                  the motor and bulbs are all controlled by dimmer type switches the diagram suggests switches..

                                                  i agree bulbs will be hard to get but they are available online..i could rewire to 240v..

                                                  this is what i started with

                                                  IMG_6477IMG_6476IMG_6478IMG_6479IMG_6480IMG_6481

                                                  #713196
                                                  noel shelley
                                                  Participant
                                                    @noelshelley55608

                                                    sOME ARE COMPLICATING THIS ISSUE BY NOT PAYING ATTENTION ! One of the first pictures shows the capacity of the transformer to be 1200VA, to some extent born out by later pictures and the gauge of wire in the windings. The lamps could be rewired with 240v bulbs, the fan after a good blow out to clean it since it has been working on 50Hz should be OK on the 115 at 50HZ from the transformer. The original wire may well be heat reistant in which case I would reuse it if sound. Check out how the light switches work – are they centre off ? The fan motor will consume very little, the halogen bulbs may be 50W each the heat lamps ? The wires on the transformer were not cut just disconnected and 1200VA has worked – so why not now ? Whether the project is worth the candle is for Ian to judge, he has a wiring diagram ! Noel.

                                                    #713198
                                                    Robert Atkinson 2
                                                    Participant
                                                      @robertatkinson2

                                                      OK,
                                                      I read the transformer as 200VA I gues the terminal block was hiding a leading 1.
                                                      If changing the lights you almost certainly need to change the holders as well. North American light sockets are generally not adequately insulated for 240V.
                                                      Make sure al exposed metalwork is properly connected to the protective ground.

                                                      Robert.

                                                    Viewing 25 posts - 26 through 50 (of 50 total)
                                                    • Please log in to reply to this topic. Registering is free and easy using the links on the menu at the top of this page.

                                                    Advert

                                                    Latest Replies

                                                    Viewing 25 topics - 1 through 25 (of 25 total)
                                                    Viewing 25 topics - 1 through 25 (of 25 total)

                                                    View full reply list.

                                                    Advert