OK, I looked it up!
BS7671 does not say either way. However, Regulation 134.1.1 is “Installation must follow manufacturer’s instructions.”
“Don’t twist” is implied by these MK and Scolmore instructions: they don’t mention twisting as an option. Twisting is not expressly forbidden by them, even though BS761 enjoins us to “not twist the strands of a stranded conductor before inserting it into a terminal, unless the terminal manufacturer specifically permits it.“.
Scolmore “Cables should be prepared to the appropriate lengths (as stated within these instructions) so that the conductor reaches into the terminal, and the circuit protective conductor is the longest. The terminals should be tightened to their appropriate torque value. Do not over tighten.”
MK
IET GN1 says “You should not twist the strands of a stranded conductor before inserting it into a terminal, unless the terminal manufacturer specifically permits it.“. GN1 does not forbid twisting solid core cable. However, twisting solid core is considered poor practice. “Solid (single-core) conductors are not intended to be twisted before insertion into a terminal.”
Comment:
The guidelines aren’t black and white. Nonetheless, strong evidence that trainers considers twisting to be bad practice, the concern being the copper might be scored, stressed or unevenly clamped.
I note the emphasis in the guidance and manufacturers instructions on getting the torque right. No figures given – just “don’t overtighten”. And also the expectation that electricians will read the manufacturers instructions, not just rely what they were taught in their youth. Apparently some terminals are designed to take twisted wires, which changes the guideline.
The worst wiring I’ve seen was all in domestic homes, the best in warships. They’re done to a much higher standard and inspected, or should be! Computer rooms pretty good, though one was found dangerously wired with phases mixed inside an aisle. Aircraft and industrial wiring are outside my experience.
Dave