Hi Daniel ,
It’s so long ago I last looked at a direct on line starter like the one you have
I’ve forgot the finer details.
but if you look at the contactor from the other side you should see the thermal overload
rotating the red spindle sets the overload current and pushing it down manually
opens the switch for stop (and reset)
you need to confirm you have a 440v coil for 3 phase and not 240v for single
phase. ( should be printed on the coil , they can be bought separately)
with the square start switch you need to wire the one phase via the
normally open contact to the coil
then from the coil via the overload / stop switch to another phase
to complete the circuit.
without an auxillery contact as on new contactors
I think you will find the start switch is mechanically held down when
the contactor is energised.
if no one has the info for your contactor
post a picture of the overload and stop switch and
I’ll draw and post a diagram of what I expect the wiring to be
John