I wonder if some electrical engineers could look over my attempts to improve the lift motor’s power supply:
Lift – 2.7-tonne, screw-type, two-poster. Motor is a custom 3ph 400V 4-pole 3.5kW unit.
Supply – single phase 240V to rotary converter, nominal 7.5 kW (or kVA). Voltage drops all reasonable.
Problem: near capacity (2.6-tonne RR sport) it struggles and stalls.
I’m not buying another rotary due to expense. My assertion here is the power’s there, just not being used efficiently:
Motor plate: 400V, 50Hz, 11A, cosphi 0.65, (giving a phi of 49.5*)
Now, lifting a 2-tonne car at 30 mm/s puts only about 600W of gravitational potential into the car, so this is a hugely inefficient machine, tempered by only being used for seconds in the hour.
Taking the motor plate values, I get:
Apparent power, |S| = (sqrt3)VI = 7.62 kVA
Real power, P = |S|cosphi = 4.95 kW
Reactive power, Q = Ptan(phi) = 5.80 kVAr
So, under rated conditions, a lot of the power is just bouncing back and forth. I assume this holds similarly for the real-world conditions of my lift, running on the rotary.
So, I thought power factor correction capacitors, ‘injecting’ some VArs, might help harness that useless power:
Target cosphi = 0.95, phi = 18.2*. Assume real power is constant:
P = 4.95 kW from above.
|S| = P/(cosphi) = 5.21 kVA
Q = Ptan(phi) = 1.63 kVAr
kVAr needed = actual – target = 5.80 – 1.63 = 4.17 kVAr, or 1.39 kVAr per phase.
Given Q = V^2/Xc and cap. reactance Xc = 1/2(pi)fC, we get C = Q/V^2.2.(pi).f
With a Q=1.39 kVAr, V=400, f=50, the required capacitance per phase = 27.7 uF.
Apparently, overcompensating can lead to LC oscillations and voltage spikes in the windings, so I decided to go with 20 uF in a delta across the motor windings.
It seems to have worked – it just about lifts the RR sport, and the line currents during lifting have reduced by 20-25%. No voltage spikes detected using the Fluke on peak detect.
If anyone has bothered to trawl through all that, I’d welcome thoughts/comments/improvements. Cheers.