      Not directly related to model enginnering per se, but the subject of electrics in the garage/workshop crops up from time to time….
      Now my son has a garage where he has a fish tank, needless to say there is water nearby…
      Where his tank is located along a wall, there is a double socket on the house ring.
      He has a spur off from the ring with a fcu/rcd and the 3 double sockets…
      All is good in terms of compliance, the fcu preventing any overload of the ring circuit, but the rcd is tripping the house rcd too…
      So my question is: if the house ring is rcd protected as it should be under current regs, and you use a lawn mower on an extension lead fed via a plug in type rcd what is the difference?
      Trouble is, if he does away with the rcd in the garage on the radial cct, if he trips the rcd in the house he may not know it has tripped….
      Edited By John Rudd on 16/09/2015 17:00:01
      #31801
      John Rudd
        @johnrudd16576
        #204571
        Les Jones 1
          @lesjones1
          Hi John,
          In a case like this both or either one of the RCDs could trip with an earth leakage fault. It will depend on the exact tripping current an tripping time. Both RCDs will probably be rated at 30 mA trip current. I can't remember the trip times. I do not see any point in having a second RCD if the circuit is already protected by one. He will know the house RCD has tripped if the item he is using stops. (If it stops until he goes to the consumer unit and checks if the RCD or the MCB has tripped he will not know if the loss of power is due to an earth fault or an over current fault.)
          Les.
          #204573
          Frances IoM
            @francesiom58905
            I presume the RCB covers a number of circuits – if they trip you have a fault (or in this case possibly multiple faults in that the fault current was already near tripping point and he has just added to it)
            the most sensible thing is to have it checked out by a professional electrician who has the necessary meter to measure the tripping current and to test leakage on the system – tripping RCBs indicate faulty wiring or equipment and should be investigated + remedied ASAP.
            Personally I would go over to individual RCBOs which protect individual circuits and put an individual circuit from the main box to the garage.
            #204581
            John Rudd
              @johnrudd16576
              Les,
              Just as I thought….
              Both rcd's are rated at 30mA….
              Ill tell him to get rid of the fish tank…..lol….
              #204592
              Brian Wood
                @brianwood45127
                John may care to adopt the solution my electrician installed. In our house; inadvertent tripping from an outside circuit can be potentially embarassing and the one that serves my workshop also serves two garden fountain pumps
                These are notoriously 'lossy' things at maybe 5mA each, even from new, so he installed a second earth trip housing in the supply leading outside. Crucially, this is earthed to a second ground rod at that point which is NOT connected back to the house earthing system.
                If there is a fault in the outer circuit, that will trip the second ELCB but leave the house fully operational
                #204604
                Muzzer
                  @muzzer
                  Surely it isn't going to matter if you have a second ground. Ground is ground is ground. The neutral is grounded at the substation, so ANY path from live to ground outside of the neutral should trip the RCD.
                  For this scheme to work, you would need to either run an unprotected live to the outside RCD or possibly use an isolation transformer and then ground the neutral and connect up the socket via an RCD.
                  Unless you have a dedicated garage consumer unit with its own master RCD or use individual MCBOs for each circuit there isn't a neat solution. The last thing you want is to trip the whole garage out, machines, lights and all when you are in the middle of a potentially dangerous operation.
                  I'm not convinced that a series of RCDs with reducing trip currents is the right solution either.
                  That's how it seems to me at any rate.
                  Murray
                  #204606
                  Alex Collins
                    @alexcollins55045
                    Hi All
                    I ran a business supplying electrical power to Outside Markets and the such for 15 years.
                    Earth Leakage Trips were required on all circuits but to lose lights presents another health and safety issue.
                    Most of the events I ran were all Generator power and some of the events ended up with 5+ KM of wiring attached.
                    The capacitance in the Cable on a warm dry day caused 300+ ma of natural leakage.
                    The only way to keep things running was to stack the trips.
                    If you have 2 trips as described the natural leakage in the house will cause both trips to fail if you exceed 30ma in the workshop.
                    Either put the Workshop on a non RCD'd Circuit. Most modern consumer units are split.
                    I appreciate that this will mean running a separate cable back to the consumer unit.
                    Or put a delay trip on the House side.
                    This will however slightly compromise the overall safety of the House.
                    Alex.
                    #204611
                    Les Jones 1
                      @lesjones1
                      Hi Frances,
                      I think your understanding of how an RCD works is wrong. It does not measure current in the earth conductor. If it did that it would only trip with leakage to the EARTH CONDUCTOR. It would not trip if there was leakage from live to some other item that was at ground potential. Such as a water pipe or through you to damp soil.
                      The RCD works by comparing the current in the live and neutral conductors. If they are not the same then there must be current flowing to ground. Which is anything grounded by any route. So in this case the example of current flowing through to damp soil will trip the RCD. I agree with all of the comments made by Murray.
                      John, Just putting a neon indicator in the garage fed from the ring main would solve his problem. (Or a relay which sounds a buzzer if the power to its coil is removed.
                      Les.
                      #204612
                      Brian Wood
                        @brianwood45127
                        Hello Murray,
                        The important point in the system I described is that the supply cablie earth is terminated in an isolated terminal at the second earth leakage trip box, but the supply continues out to the workshop area. The workshop earth is now referenced back to the second earth rod.
                        We tested the system out in the workshop with a deliberate short to earth on both live and neutral in two tests
                        In each case the second earth leakge trip operated as expected and In neither of these tests did the house supply get interrupted. So it works just as I was told it would. Not all grounds are at identical potential therefore, the two earth rods in our installation are about 70 feet apart on sandy/loam soil.
                        Edited By Brian Wood on 16/09/2015 20:38:20
                        #204617
                        Frances IoM
                          @francesiom58905
                          I think I know how a RCB works – on difference between Live and return neutral currents – my original comment may have been too simple but for standard UK houses with short cable runs and earth as supplied by Elec Company the capacitive leakage is probably not serious and trips would indicate a side path between live or neutral supply leads to earth (often caused by poor insulation) – possibly an immersed pump in one of the tanks has poor insulation?
                          I was assuming garage is very close to the house and that earth is that supplied by the Elec company – if you are in a rural (long supply) and/or long spur out to garage then you need significantly different earthing arrangements than if you are in town or suburb housing estate – in that case the installer would have provided the necessary separation between house + garage supplies
                          Edited By Frances IoM on 16/09/2015 21:11:59
                          #204618
                          John Rudd
                            @johnrudd16576
                            Posted by Les Jones 1 on 16/09/2015 20:23:25:
                            Les.
                            Les,
                            That was something that had been considered as a workaround…..
                            I think the solution is to leave the second rcd out, leaving the existing unit in the board.
                            Thanks to all who contributed to this…
                            #204622
                            Phil Whitley
                              @philwhitley94135
                              Woody, Congratulations on finding a sparkie who knows his stuff, they are rare nowadays!
                              Phil
                              #204626
                              Les Jones 1
                                @lesjones1
                                I have just realised I looked at the wrong heading in my last reply. (Sorry Frances.) I was actually referring to Brian's post at 18:39. I was also reading its as the second RCD being fed from the original RCD. (It is not clear if this is the case or if the second RCD is fed from before the original RCD) If the second RCD is fed from the first I do not see how using a separate earth can solve the problem. If the second RCD is fed from the feed side of the first RCD then I believe this fixed the problem and not the alternative earth.
                                Les.
                                #204641
                                Martin Kyte
                                  @martinkyte99762
                                  Primary point. Anything connected should not be tripping the breakers at all. It's a fault and needs to be fixed.
                                  Secondary point. Either fit a separate consumer unit in the garage with a feed from an MCB on the main board in the house fed from the supply side of the house RCCB or just rely on the protection on the main board in the house and don't use a plug in.
                                  Plug in RCD's were a good idea when the majority of domestic installations were wire fuse and earth leakage protected only. With a lawn mower the biggest risk is a cut cable which does not always generate an earth fault and on the old installations could give you a belt without tripping the earth leakage trip.
                                  Just as a side note, current spikes caused by inducive loads switching on and off and non sinusoidal waveforms caused by chopper control of current can cause protection devices to misbehave.
                                  MCB = Miniture Circuit Breaker (electronic fuse)
                                  RCCB= Residual current Circuit Breaker (detects faults by imbalance between the live and neutral conductors)
                                  RCD = Residual current device
                                  #204646
                                  Frances IoM
                                    @francesiom58905
                                    Les
                                    I suspect the garage had a standard small switchbox added (eg as sold by B+Q) that comes with a RCB + 2 or 3 MCBs wired as a spur back to main box which is probably a split RCB tho older boxes did have a non-RCB section (used amongst other things for freezer circuits) – however if the RCB is tripping I come back to my point there is a fault or faults in some equipment or wiring that should be corrected – insulation faults generally get worse with time. If the garage circuit causes the house + garage RCB to trip then the combined leakage is above 30ma if moving the garage spur to a non-RCB connection in house stops the tripping then to me this indicates that there is some near tripping leakage current in both the house + the garage – potentially 2 separate faults
                                    #204652
                                    Brian Wood
                                      @brianwood45127
                                      Hello Les,
                                      I can see the debate continuing for some time, I hope my second posting made my installation a little clearer.
                                      Just to clarify any confusion I may have caused.
                                      The arrangement here before change was completely conventional, the workshop supply cable is protected from excess current with a miniature 32 A circuit breaker; the whole board of the consumer unit is protected from earth leakage fault by a 30 mA residual current device. Earthing at the consumer unit is referenced back to a standard earth rod close by
                                      The new arrangement differs only in the provision of a second 30mA residual current device supplying the workshop and garden circuit alone; that is now referenced back to the second earth rod separated from the other by about 70 feet. There is now no direct connection back to the earth as seen at the consumer unit.
                                      When this new arrangement was tested with direct phase to earth faults in the workshop, we also took measurements of the tripping current for both live to earth and neutral to earth. I don't remember the individual values now but they were in the range of 28mA and 31mA, but as I said in posting 2, the house supply continued to work uninterupted on both these tests—exactly what I had been told and expected it to do.
                                      I think Alex Collins has added useful insight to all this with his long cable runs and the induced votlages that can build up accordingly, earthing to the planets surface will have variability from water content alone and cannot therefore be at equal potential at all points. Each point of earthing is still however equally valid as a reference point from which to measure current loss. As Phil Whitley has observed, I think I am fortunate to have a sparkie who knows his stuff.
                                      Edited By Brian Wood on 17/09/2015 09:45:31
                                      #204680
                                      Les Jones 1
                                        @lesjones1
                                        Hi Frances,
                                        I agree that cause of the tripping needs to be investigated and fixed.
                                        Hi David,
                                        Although you have tried to clarify the situation you have not said if the second RCD is fed from before or after the original RCD An RCD does not know (Or need to know.) the route of any earth leakage that trips it. I think what you are saying is that the earth to the sockets in the workshop is supplied by a second earth rod. This rod will only pass the fault current if the leakage is to the metalwork which is connected to it. If the leakage is from a garden tool (Which will probably be double insulated and not have an earth wire.) which has become damp then the leakage will be via the dampness on the tool and then though the user then through damp leather soles of his shoes and directly to earth.
                                        Les.
                                        #204684
                                        Brian Wood
                                          @brianwood45127
                                          Hello Les,
                                          I don't know who David is but I suspect your comments were aimed at me!
                                          I thought all was clear, but on the point you raise, The second RCD, which now protects the service to the workshop and garden area, is interposed into the supply from the house consumer unit. So, technically, the phase connecrions through it are from the RCD ptotected supply and the 32 Amp circuit breaker on the house board.
                                          The earth reference back to the house RCD is disconnected and that reference now comes from the second earthing rod.
                                          You will I hope remember that the requirement for this arrangement was to maintain the house services intact in the event of an earth fault in the outer circuits. It does what it said on the box and rather well I think.
                                          Does that make things clear now?
                                          #204704
                                          Les Jones 1
                                            @lesjones1
                                            Hi Brian,
                                            My second mistake reading a post heading. I'm still not clear if the second RCD is fed from the original RCD or from the busbar in the consumer unit that is directly on the output of the main switch. (I am assuming this is a split consumer unit.) I will try by asking a different question. If the original RCD is tripped or switched off does the workshop supply also go off or does it remain on ?
                                            Les.
                                            #204706
                                            John Rudd
                                              @johnrudd16576
                                              Posted by John Rudd on 16/09/2015 16:59:37:
                                              There is a spur off from the ring with a fcu/rcd and the 3 double sockets…
                                              Just to clarify…..
                                              The house has a split board…the 2 ring mains are on the rcd side.
                                              The socket in the garage is on the ground floor ring main.
                                              From this socket there is a radial spur as detailed before….
                                              We tripped the rcd in the garage by accident, this then led to the discovery that the house rcd had tripped also..Not something desirable..
                                              Edited By John Rudd on 17/09/2015 18:28:26
                                              #204735
                                                I found an excellent explanations here: http://www.napitonline.com/downloads/CP%201%2007%20P%2010-11%20RCD%20Unwanted%20tripping.pdf
                                                This would seem to suggest using a 100mA time delayed RCD for the main board with 30mA RCDs for the entirely separate garage circuit and house ring mains.
                                                Muzzer
                                                  @muzzer
                                                  That's what we had in Cambridge, as our house had a TT earthing systems due to the overhead power lines which came in without a ground. In a TT system, a local ground is essential for the RCD to work into.
                                                  I had a garage consumer unit with separate RCDs for the lighting and power so that earth leakage trips due to my machines didn't plunge me into darkness (alternatively, individual RCBOs would have done the trick). I think the main incomer RCD was actually something odd like 130mA but it came from The Ark. The local ground was provided by the water pipes but luckily the water and gas incomers were all plastic, rendering the main RCD rather useless. Let's just say I later fitted a ground rod after some interesting experiences.
                                                  Sort of questionable whether there is any point having the 100mA RCD in a normal TN-S system where you have separate local RCDs for the house and garage. The only obvious benefit is that the spur to the garage has RCD protection, in which case you may as well just use the 100mA trip for the garage spur alone.
                                                  Certainly, unless you insert an isolation transformer in the spur, fitting an local ground spike for a local RCD is pointless and can't be counted on to operate as hoped for. Sounds as if that electrician has succeeded in selling The Emperor's New Clothes.
                                                  Modern consumer units now have multiple (usually 2) RCDs to prevent the whole house losing power if there is a ground fault. And an additional RCD isn't expensive if you shop somewhere like Screwfix.
                                                  Murray
                                                  #204782
                                                  Brian Wood
                                                    @brianwood45127
                                                    Hello again Les,
                                                    My consumer unit is not split, the whole set of miniature circuit breakers, including that to the workshop and garden are protected by the one RCD.
                                                    So, you are correct in saying that a house trip will also plunge the workshop into darkness, just at it would have done before. The reverse situation however is now different, a workshop trip leaves the house unaffected when before it would have taken the house down too.
                                                    I hope that clears it up for you.
                                                    #204787
                                                    Les Jones 1
                                                      @lesjones1
                                                      Hi Brian,
                                                      I don't understand how it can work connected in the way you describe.
                                                      Les.