Before jumping in at the deep end, assuming the motor is toast and reprogramming the VFD etc, does this machine have safety interlocks? Look for wires leading to switches on moveable safety screens and doors – these are often arranged to stop the machine if the operator does something unexpected. There might be an interlock on the perspex spindle screen. These are often removed leaving the switch in the safe position, and the switch might have been moved since. I see the mill has a powered traverse; this usually means two interlock switches arranged to stop the motor winding the table off the machine! Quite often interlocks are arranged in series, so opening any one of them stops play. Not usual for interlock switches to vibrate loose and rotate rather than switch as expected. Make sure they are firmly in position. All interlocks have to be closed, so check them all.
I recommend debugging from the input end, not back from the motor. A multimeter is needed, and a circuit diagram is very helpful, plus the VFD manual.
Anyway, is mains reaching the VFD? If not:
- check fuses, including inside the control box and the VFD cabinet
- The NVR often doubles as an emergency stop: make sure it’s been reset to go.
- check the No Volt Release Switch. Fairly common for these to fail. Sometimes the machine will work if the switch is held down manually. If that happens replace the NVR.
If the VFD has mains power:
- look for loose wires: vibration can loosen terminal screws (likely) and might break crimped/soldered connections (unlikely).
- check for damaged insulation, usually where wires go through a hole or a clamp.
- speed control pots wear out or fill with dirt. (likely) If the pot fails open circuit the VFD won’t power the motor. A multimeter should show twirling the speed control varies the voltage control it applies to the VFD. Probably between 0 and 5vdc. If the voltage doesn’t vary, fit a new pot, not difficult.
- might be a contactor in the circuit. If so check it for loose wires, burnt out coil or bad contacts
Check all three output wires from the VFD to the motor are firmly connected at both ends. Very bad things can happen one is loose – it can puncture insulation inside the motor and/or destroy the VFD’s output transistors. Or, with luck, the VFD is clever enough to detect the fault and refuses to start until the wires are all present and correct.
Do you know the history? Be good to know if the motor ever emitted magic smoke, or if anyone tried to reprogram the VFD, or has been at the wiring and switches before. Or maybe used a megger on the motor whilst the VFD was still connected, that being a good way of killing electronics! If it stopped working after a move, then the fault is probably loose wire simple. If it failed during a heavy session, then either the VFD or the motor could be cooked, or both.
Les describes the light-bulb method of testing a VFD so try that. If the bulbs work, then replace the motor. Shouldn’t be difficult – power is known and I;’d bet the farm on it being 230v delta, not 400v. They have standard mountings, so measure them and compare with a catalogue – MachineMart might do.
If the VFD is deceased, might be worth resetting it (manual required), otherwise replace with a new one. Not too difficult on a simple machine because most cheap VFDs come with ready to go factory defaults and a basis wiring diagram – not necessary to re-program them.
Advice as for eating an elephant – one mouthful at a time. Step through logically until something wrong is found, and don’t be afraid to ask again. Photographs are very helpful.