  • #372234
    Roderick Jenkins
    Participant
      @roderickjenkins93242

      We have just moved to sunny Christchurch in Dorset. The new workshop is considerably bigger than my last home, being 5m x 5m.

      ws0.jpg

      ws1.jpg

      ws2.jpg

      ws3.jpg

      The plan is to replace the up and over door with a 2/3 1/3 side hinged door.. The walls are single skin, mostly concrete block but with a brick front, semi detached on one side – all painted now. Reading the various threads on the forum have led me to plan to batten the walls and infill with 25 mm polystyrene, then use a polythene vapour barrier and line out with OSB painted white. I'm less clear on what to do with the ceiling. I'm currently inclined to go with Celotex (or similar) fastened to the rafters (thus making use of the reflective surface to enhance lighting). I understand that It would be a good idea to ventilate the area between the Celotex and the roof boards – how would I go about this? Any other comments on the scheme would be most welcome.

      Cheers,

      Rod

      Advert
      #26191
      Roderick Jenkins
      Participant
        @roderickjenkins93242

        Advice and comments please

        #372240
        Bazyle
        Participant
          @bazyle

          1 inch of insulation isn't nearly enough. Minimum of 4 and I'd prefer 6in. Then you can happily heat 24/7. The underside of the roof shouldn't need ventilation provided your vapour barrier works. I suggest having a close look at he floor to make sure it is on a dpc and think about boarding it out for a bit of insulation.

          #372241
          JasonB
          Moderator
            @jasonb

            For the walls I would try and go for 50mm Celotex/Kingspan rather than 25mm, not much more costwise and will take the same effort to fit but will keep you a lot warmer. If you can get the formwork OSB with one smooth surface that paints up better and does not collect the dust.

            For the ceiling I would go 50mm Celotex/kingspan between rafters which will leave you a 50mm airgap above. Then 25mm Celotex under the rafters so the whole area is covered, Ali tape on the joints and that with the foil face will give you your vapour barrier. I'd probably ply over that too which I what I have on mine.

            #372245
            Clive Foster
            Participant
              @clivefoster55965

              Much as I hate using the stuff hafta say that glass fibre over OSB boarding is probably the easiest effective way to insulate under the roof. Unless the roof edges are carried right round and sealed against the walls there will be sufficient gap for ventilation.

              Same with side walls. If the structure is breeze block, thermalite or similar the walls will have a reasonable degree of natural insulation properties so a couple of inches of insulation will be fine. Agree 1 inch is a bit thin unless you go for one of the "super-blanket" types.

              Personally I'd avoid so called "vapour barriers" like the plague. Proper application in any random set-up is much harder than it appears. Its very easy to trap moisture the wrong side.

              Four coats of brilliant white emulsion on OSB makes a nice bright wall or ceiling. But don't forget to properly seal the cut edges with a couple or three coats of paint before putting up to guard against creeping moisture. I mixed up all the saved half and quarter tins lying around. Totally revolting colour and took a while to go off but boards are sealed.

              Clive.

              #372247
              Martin Lowe
              Participant
                @martinlowe20701

                For insulation material, look on the Secondsandco website (https://www.secondsandco.co.uk) and give them a ring. They sell seconds and overstock Kingspan and the like for much less than other places. I've bought from them twice – once for my original workshop and then for an extension – both times they were excellent prices and very helpful delivery drivers.

                I agree with Jason about using ply rather than OSB, much better finish and much easier to drive screws into when fitting shelves.

                Hope this helps

                Martin

                #372250
                Martin 100
                Participant
                  @martin100

                  Decide if you want to be able nip out for an hour or two 'whenever' and at any time of year, do some work in normal clothes rather than multiple layers of thermals and then come back inside when you choose, not when you freeze / melt.

                  Decide how much time/money/effort you want to spend on 'heating' No time/money/effort is often the best.

                  Do you prefer to be sweating all through a hot summer with a fan trying to cool the place down?

                  Do you prefer to be a gross polluter for the rest of the year with a woodburner affecting the health of everyone in the vicinity?

                  Some fit resistive heaters or incandescent lamps to every bit of machinery to stop them rusting when getting the insulation and ventilation right fixes the problem 'forever' with no ongoing energy usage. But some people always go for really cheap nasty 'fixes' rather than properly addressing the fundamental issues.

                  Proper insulation is expensive but needs buying and fitting just once. Do it right and occupancy heat, maybe topped up with that from a freezer can easily be enough to keep the place comfortable all year round.

                  If you can only afford 25mm of polystyrene on the walls then don't bother, wait until you can afford at least 75mm and preferably 100mm or more of PIR

                  While PIR is supposed to be 'safe' and class O, bare PIR on the roof is not a good idea if you have any intention of having a naked flame in the workshop. Trying to justify leaving it bare to enhance lighting is daft. Put some more lights in instead, preferably ones that direct the light downwards, they are really cheap.

                  The floor will also loose lots of heat, cold feet can be fixed with insulation in the structure too

                  #372254
                  not done it yet
                  Participant
                    @notdoneityet

                    Semi-detached to another garage? If so, that connecting wall might allow a little less insulation. I would go with 100mm of polyurethane foam with stout timber battens between the sheets (to allow for shelf fixings etc). Ideally needs a fire resistant covering. Non-flam rock wool or glass fibre would need rather more thickness than the foam sheets for tequivalent insulation.

                    The roof would need ventilation, IMO. Any condensation remaining in any of those spaces would be bad news.

                    I’ve gone for no windows – not that they were there in the first place – and rely on lighting. The costs are less, compared with heating and there is less heat loss. Solar panels supply leccy for lighting in the summer months and there is not a lot of difference in the winter, as lighting is needed anyway.

                    My workshop is only vented when I choose. That way, it is kept dry (and a little warmer) by a desiccant dehumidifier in the winter months.

                    At 5 x 5m you may have the option of separating your machines from bench grinders, etc – which might reduce the heating costs.

                    If connected to your house, an extra radiator from the central heating system would be good, and thoughts on heating costs, now rather than later, might be a good move. I would stick to leccy heating, unless a balanced flue gas heater was possible…

                    It looks like a good sized workshop. Arrange for storage elsewhere, before if gets cluttered.smiley The rest of my garage is totally cluttered!

                    #372290
                    geoff adams
                    Participant
                      @geoffadams14047

                      sent you a pm

                      Geoff

                      #372307
                      Bazyle
                      Participant
                        @bazyle

                        If it is attached to the house you should use 2 layers of plasterboard for fire regulations I think.

                        Humans sweat up to 6 pints per day. Your dehumidifier needs to handle that.

                        A full 11in cavity wall is equivalent to just 1 in of expanded polystyrene which is the highest insulator next to that space shuttle covering. Celotex etc is about 90% as good, rockwool about 75%, a single brick 4in wall does little more than stop the wind as it has to absorb a lot of heat before it even starts providing insulation.

                        #372329
                        Buffer
                        Participant
                          @buffer

                          Ian

                          My workshop is brick and timber 5m x 2.5m with no permanent heating.

                          I put 100mm of Celotex under the concrete floor and 70mm on the brick walls. The walls were then lined with 1/2" ply. The ceiling has loft type rollled insulation blanket from Wickes. I haven't worried at all about all the thermal bridging, vapour barriers and all the other stuff you hear.

                          It is a nice cool temp in the heat of summer and cold in winter (as it had no heating).

                          I bought a Firefly 2Kw 3 bar quartz electric outdoor patio heater and stuck it on the wall over the bench.

                          When I go into the workshop I get instant heat on me and in only a few minutes I am turning the bars down to just 1 and then it stays quite comfortable in there. I have tried 2kw fan heaters and I think they are useless as they take an age to feel any noticeable difference. If you get one or two of these quartz heaters you really will feel the benefit instantly.

                          I never had any damp problems but I now also run a small Ebac dehumidifier over the winter on a permanent drain and I have never had any damp, condensation rust or any problems at all.

                          I personally would not get a wood burner unless you are lucky enough to spend the day in there because of the time it will take to get going etc.

                          Hope this has been of some help.

                          Rich

                          #372330
                          Clive Foster
                          Participant
                            @clivefoster55965

                            Ian

                            Don't overthink it. Anything half decent will work pretty well. In my career as a scientist / R&D engineer working mostly to cover the gap between "sprawls all over the lab" to "field testable version so we can sort the design rules" this sort of discussion tends to focus on the edge cases which generally have little effect in practice.

                            Mine is 4" fibreglass in the walls which are OSB both sides with shiplap outside cladding, 4" fibreglass between OSB ceiling and standard flooring board loft floor finally 2" polystyrene sheet under steel sheet roof. Household standard double glaze windows and doors.

                            It works.

                            Essentially no continuous heating needed in main workshop until down to below 3°C or so ambient but maybe an hour or so when starting knock the chill off once below 10°C or so. How long depends on what I'm doing. 8 ft by 8 ft office section has a thermostatic oil radiator to hold 20°C. Never on full time even below 0°C.

                            Bottom line is maximum inside to outside temperature difference will be around 25°C so thermal energy transfer won't be great anyway. Whats important is to avoid direct conduction over continuous surfaces and, especially, convective scrubbing.

                            Standard building insulation heat transfer maths didn't work any sense back when I was a Thermal Imaging, Target Detection and Camouflage specialist. Nothing I've seen since suggest its go any better when in comes to real world situations. Quoted figures for various materials seem intended more to confuse than enlighten which really doesn't help.

                            My thermal camouflage work suggested that breaks between layers are much more important than conventional insulation theory allows. Hence three breaks in my walls. OSB to fibreglass to OSB to timber cladding. Convection control is also important. Hence insulation under the roof and under the loft floor which seriously reduces the thermal gradient driving convection. Similar break & space strategy was shown to work pretty well at reducing thermal signature of a just parked up Chieftain tank.

                            Clive.

                            #372332
                            Journeyman
                            Participant
                              @journeyman

                              Can't do the maths for you Ian, but can say from experience that insulation works! This is my workshop:-

                              jws.jpg

                              I built it from scratch over 35years ago, it is still standing and the routine maintenance includes re-roofing 3 times and regular coats of timber treatment on the outside. It is plain timber with no vapour barrier or other lining. The walls have 2" rockwool insulation and the roof has 4" rockwool, heating by a wall mounted 1kw thermostatically controlled fan heater. which doesn't run very often. The inner walls and roof are lined with printed hardboard sheets to hold the insulation in place (with hindsight thick ply would have been better) There are a couple of high level ventilation grilles that I open in the summer. The windows are a couple of second-hand double glazed units.

                              No rust, although I keep the machinery oiled, warm in winter and cool in summer (except this year when it got up to about 35C) More info *** HERE *** if interested.

                              Edit: Add photo

                              Edited By Journeyman on 19/09/2018 11:52:55

                              #372334
                              JasonB
                              Moderator
                                @jasonb
                                Posted by Bazyle on 19/09/2018 09:32:17:

                                 

                                A full 11in cavity wall is equivalent to just 1 in of expanded polystyrene which is the highest insulator next to that space shuttle covering. Celotex etc is about 90% as good, rockwool about 75%, a single brick 4in wall does little more than stop the wind as it has to absorb a lot of heat before it even starts providing insulation.

                                Are you sure about those percentages, I thought PIR (Celotex, Kingspan etc) was about 40% more efficient then EPS (expanded poly) for the same given thickness.

                                PIR thernal conductivity is 0.022W/m.K and EPS between 0.029 to 0.038W/m.K

                                That makes PIR upto 40% more efficient than EPS in my book

                                Edited By JasonB on 19/09/2018 12:13:53

                                #372338
                                Swarf, Mostly!
                                Participant
                                  @swarfmostly

                                  Plus one for: 'For insulation material, look on the Secondsandco website (https://www.secondsandco.co.uk) '.

                                  Best regards,

                                  Swarf, Mostly!

                                  #372341
                                  Martin 100
                                  Participant
                                    @martin100
                                    Posted by Bazyle on 19/09/2018 09:32:17:

                                    If it is attached to the house you should use 2 layers of plasterboard for fire regulations I think.

                                    Humans sweat up to 6 pints per day. Your dehumidifier needs to handle that.

                                    A full 11in cavity wall is equivalent to just 1 in of expanded polystyrene which is the highest insulator next to that space shuttle covering. Celotex etc is about 90% as good, rockwool about 75%, a single brick 4in wall does little more than stop the wind as it has to absorb a lot of heat before it even starts providing insulation.

                                    No, the exact opposite

                                    EPS 0.037W/mK

                                    Rockwool 0.035W/mK

                                    PIR 0.023W/mK

                                    Lower is better

                                    #372352
                                    Georgineer
                                    Participant
                                      @georgineer

                                      By the time I've installed all the recommended thicknesses of insulation and the gaps between, on walls, floor and roof, there won't be space enough to get into my workshop and stand up.

                                      George

                                      #372364
                                      Neil Wyatt
                                      Moderator
                                        @neilwyatt
                                        Posted by Roderick Jenkins on 18/09/2018 19:49:42:

                                        We have just moved to sunny Christchurch in Dorset. The new workshop is considerably bigger than my last home, being 5m x 5m.

                                        You used to live in a bedsit?

                                        Neil

                                        #372375
                                        Buffer
                                        Participant
                                          @buffer

                                          Ian

                                          I don't know what your budget is but for this sort of thing I use roof batten from a roofing supplies company. The last lot I got was 2" x 1" x 3.6m @ 45p a metre and its already treated. I think the blue stuff is cheaper than the red. Smaller sections are available for even less.

                                          Regards

                                          Rich

                                          #372383
                                          Roderick Jenkins
                                          Participant
                                            @roderickjenkins93242

                                            I was just waiting for someone to spot the missing ‘at’. Why am I not surprised it was you 😉

                                            #372387
                                            Mike Poole
                                            Participant
                                              @mikepoole82104

                                              Quite a range of ideas here but something has to be better than nothing as most people report satisfaction with their scheme. The horror stories of walls filling with condensation probably relate to a domestic situation where multiple occupants are breathing, cooking, bathing and showering and not ventilating the house. In our workshops we are usually sole workers and the shop is probably empty the majority of the time. Rapid changes of temperature and humidity seem to be the greatest enemy to our machinery so controlling the rate of temperature change and humidity are helpful. The other issue is making the workshop comfortable to work in and this will probably need some heat in the winter. Insulation goes a long way to help with temp.stability and make heating more economical. You probably can’t have too much insulation but too little will not work as well as the optimum amount. Working out the optimum amount must be possible as there are figures available for types of construction and insulation values but I gave up trying and are just going to fit what goes in easily. So far I insulated the roof with 2” of polystyrene and it is surprising how much cooler it is in the summer but still b cold in winter. THe vapour barrier thing seems complex to me, it seems that a temperature differential across the insulation forces moisture from one side to the other and it condenses as it cools so a barrier on the warm side prevents the transfer but in Britain the warm side will be inside in the winter but could be outside in the summer, it probably all works out because the dew point in the summer won’t be an issue.

                                              Mike

                                              #372389
                                              Dave Halford
                                              Participant
                                                @davehalford22513

                                                Ian,

                                                New sectional wooden buildings when tongue and groove type are made from freshly treated timber and therefore quite wet when delivered. Expensive ones are no different either. It's best to let them dry out for a few weeks before insulating them.

                                                Foam insulation boards are quite strong and only need the odd block every 2ft or so to space them off the walls.

                                                My last workshop was a tin shed and it would rain inside with condensation, simple old 2nd hand suspended ceiling sheets stopped that and thereafter the roof was dry.

                                                PS you will soon see how useful Fan heaters are at keeping you warm.

                                                Edited By Dave Halford on 19/09/2018 19:10:48

                                                #372397
                                                Roderick Jenkins
                                                Participant
                                                  @roderickjenkins93242

                                                  Ian,

                                                  No problem at all. My moving situation is very similar to yours. I just managed to take some pics of the garage before the removal guys filled it with my stuff. I'm doing some comparative U value calcs at the moment – I'll report back in due course.

                                                  Cheers,

                                                  Rod

                                                  #372407
                                                  Former Member
                                                  Participant
                                                    @formermember32069

                                                    [This posting has been removed]

                                                    #372412
                                                    not done it yet
                                                    Participant
                                                      @notdoneityet

                                                      Rod,

                                                      To completely cover all the walls and ceiling, of your garage, with 100mm polyurethane insulation board (similar to celotex but secondhand, and likely without a covering like celotex), could have cost me less than £200, at the hammer.

                                                      That would be including covering the doors and windows! Celotex/Recticel new would be a horrendous cost, in comparison. Mine came as 1200 x 1200mm and 1200 x 600mm pieces, but there were piles with larger pieces on offer when I bought mine at a regular dispersal sale.

                                                      I could not get any larger bits into/onto my car. To cover your garage walls and ceiling would have required five of my totally crammed (overloaded, maybe) car loads, so a Luton van full, probably.

                                                      I acquired mine because the guy who bought the rest of the lots (yes, a large lorry load) wanted one less lot than knocked down to him. I paid £46 + commission, I think. The bulk of his lots were twice the height as the one I went home with and probably much larger sheets. so his cost/unit area was much less than half of mine. That means I could have bought enough insulation to cover your garage for far less than £200 – possibly as little as £100.

                                                      Most on here would, undoubtably, source it new from Jewson, Wickes or elsewhere. New is easier to fix, but the far more expensive route for the same insulation material….

                                                    Viewing 25 posts - 1 through 25 (of 46 total)