Posted by Mike Poole on 04/02/2019 19:02:47:
I suppose in most domestic situations the prospective fault current is going to be fairly low unless you live next to the substation so shorting the supply might not produce too big a bang. In a factory you are going to get a much more impressive bang and rather than save your life you might end it. Isolating and testing should be done properly and with proper equipment. If the proper process is followed then you should avoid having the “accident” if there is such a thing.
Mike
Mike,
Distance from the substation is not a factor – I have seen downed 12.KV distribution lines lay on the ground and continue to arc for quite a while( and cutting a trench in the asphalt street in the process) until utility crews arrived to disconnect them
The fault current is based on the full load current of the power transformer and it's %Z (impedance). All transformers have impedance, and it's generally expressed as a voltage percentage. This is the percentage of normal rated primary voltage that must be applied to the transformer to cause full-load rated current to flow in the short-circuited secondary. For instance, if a 480V/120V transformer has an impedance of 5%, this means that 5% of 480V, or 24V, applied to its primary will cause rated load current flow in its secondary. If 5% of primary voltage will cause such current, then 100% of primary voltage will cause 20 times (100 divided by 5) full-load-rated secondary current to flow through a solid short circuit on its secondary terminals. Obviously, then, the lower the impedance of a transformer of a given kVA rating, the higher the amount of short-circuit current it can deliver.
Certainly the current rating of a transformer feeding a group of residences is less than would be found in an industrial environment, but it is still large enough to be a very significant hazard.
Tim