Hi Manny/John
I understand the way VFDs convert the incoming supply to DC before synthesising the three phase output. I have found various information regarding running 400 V converters on supplies other than true three phase. Some authors suggest derating the VFD (by up to 50%) for rotary converter supply. Jim Cox in his book on Electric Motors (2nd ed. Workshop Practice Series) states that some VFD manufacturers accept that their product can be powered in unorthodox ways, for example using an autotransformer to step up a 240 V single phase supply to 480 V single phase, whilst others expressly forbid it.
Reading the manufacture's handbook (Control Techniques) I can find no mention of 400 V class drives being capable of running from single phase supply, but they do produce 200 V class drives that can be run from either single or three phase supplies.
The only reference I can find in the handbook is a statement that:
"(Input) phase imbalance not to exceed 2% negative phase sequence"
What sort of phase imbalance might I expect from a rotary inverter?
I have also noted that if an input phase is lost the drive will trip out and report the PH trip code. This suggests to me that the VFD should not destroy itself if supplied from the rotary converter, but it might trip out. The VFD is rated at 4 kW and since my motor is rated at 1.2/1.6 kW depending on its configuration I think the VFD is very conservatively rated.
Bob