Hi Roger
On the IMO Jaguar VXR units if you want to have external controls / switches you need to change function F01 to 1 by default it is set at 0.
This now activates the external inputs, if you do not want a full pendant function just a stop button.
then it is wired between terminals PLC (which is +24 volt) and terminal FWD (forward)
IN Addition if you do not need the speed control then a wire link (insulated) is needed between terminal 12 and terminal 13. (this will set the inverter to max speed as set by the programing).
When the stop button is pressed the inverter will stop the motor quickly as reactive braking is applied, but NOT so quick as to spin the chuck or what ever off the nose.
If you use a contactor to remove the power input to the inverter, Firstly the machine will take a lot longer to stop ( not good if you are tangled up in it !) and second you stand a good chance of damaging the inverter.
Just a further point the time taken to get to speed and to slow to a stop is fully controllable in the software setup.
Hope this helps