My myford 254 has just started tripping the house RCD as soon as I plug it in, I've traced the fault to the 110v control system but that's the limit of my electronics knowledge.
It is possible that the problem lies elsewhere, rather than on the 254. A 30mA RCD will trip when the TOTAL earth leakage current hits 30mA – and there are lots of sources of leakage current. Switched mode power supplies in computers, TV, wall warts, flourescent and CFL lights, wiring, workshop equipment (VFD's can be problematic) …. everything contributes a bit, there's always some of it around. Eventually something adds another piece of straw to the camel's back, and it trips. So something else could have caused an increase, brought the RCD near the limit, then when you plug the 254 in with its 'natural' leakage, the RCD decides to go home to mummy.
Of course, it might be a real problem with the 254, but it might be on some other piece of equipment around the house/workshop. Easy enough to check – disconnect everything else by removing ALL fuses except the one to the workshop, then unplug anything and everything left on that circuit, house & workshop. Including lighting!
Then plug the 254 in – if the RCD trips, you have a problem on the 254. If it doesn't, then you have the 'last straw' situation. Which could be more difficult to resolve!