HF fluorescent lights
Home Forums Beginners questions HF fluorescent lights
  • #306778
    Robin Graham
      @robingraham42208
      House power went down yesterday – looked at the CU and the RCD on the half which supplies house power and workshop lighting had tripped as well as the workshop lighting MCB. Reset, and all well except one fluorescent (2x58W tubes) unit in the workshop was out. Is it reasonable to assume that this can only have been caused by the HF ballast in the fluorescent unit failing? And if so is it OK just to buy a generic 2x58W replacement and wire it in, or is there more to it than that?
      Sorry if this if a naive question – I suspect that the answers are yes, yes and no, but I've no previous experience of this type of lighting, so I'm not 100% on it.
      Thanks for any advice, Rob.
      #8785
      Robin Graham
        @robingraham42208
        #306780
        ega
          @ega
          I am awaiting with interest the experts' views on this as I have had rather similar problems: the ELCB trips when the workshop fluorescent lights are switched on, a problem which was apparently cured by changing the starter in one of the units.
          #306789
          Mark Rand
            @markrand96270
            As to the replacement of the dead unit. Yes, get another one of the same spec (or a spec that matches the tubes, if there is any doubt) and wire it in in the same way. It'll work. The switch mode power supplies in the HF ballasts can fail quite enthusiastically and draw enough current in a very short time to give circuit breakers a good short-circuit test. If an RCB/ELCB is tripping when a given device is turned on, it can be a sign that interference filters in the device are failing. It can also be because the breaker is failing and is tripping at a lower fault current than it should do.
            Had this problem a couple of times at work and used up our entire stock of obsolete Square-D ELCB's looking for good ones, after testing with a current/tripping-time device that we'd bought for testing office/lab mains supplies at foreign power station construction sites!
            #306832
            Gordon Tarling
              @gordontarling37126
              Just buy a couple of LED tubes to replace the fluorescents – easy conversion and no more ballasts to worry about. I did this in my workshop and it's well worth doing.
              #306838
              Andy Carruthers
                @andycarruthers33275
                Many years ago I was told not to use fluorescent lamps to illuminate rotating machinery as the stroboscopic effect can give the impression the machine is switched off
                Unless my memory fails me!
                #306840
                John Baguley
                  @johnbaguley78655
                  That only applies to ordinary fluorescents working at 50Hz. The modern high frequency ballasts work in the KHz range and don't cause any stroboscopic effect.
                  Andy Carruthers
                    Thanks John – how quickly knowledge becomes out of date!
                    #306855
                    larry Phelan
                      @larryphelan54019
                      Hi Andy,
                      No,your memory is not failing you,I was told the same.
                      #306863
                      Frances IoM
                        @francesiom58905
                        some LED drivers impose a slight to moderate stroboscopic effect – suspect that although they use switched mode power supplies the incoming 50Hz modulates the driver voltage and the eye is very sensitive to slight changes in intensity
                        #306864
                        Joseph Noci 1
                          @josephnoci1
                          As a Radio Amateur, I hate those HF FL Lamps with a vengeance! They generate so much EMI that the MW and SW frequencies are utterly decimated within many 10's of meters of the lamps. So the neighbors lamps have destroyed my Radio Amateur hobby! Did I mention I hate those lamps?
                          Joe
                          #306868
                            @mike89748
                            Even James Bond, and pretty well all other spies of fiction, knew to hold their confidential conversations under fluorescent lamps!
                            #306869
                            Andrew Tinsley
                              @andrewtinsley63637
                              Yes indeed you can get very good stroboscopic effects, if your chuck is turning in multiple fifties of RPM. So what? If anyone thinks that the chuck isn't turning when the racket of the lathe is pretty loud, then they make a big mistake.
                              I NEVER assume that the chuck isn't turning if I can hear all that racket. Yes even though I have a clutch fitted to my lathe. Never assume the chuck is stationary. In all the time I have had a lathe illuminated with fluorescent lighting, I have never seen a stationary strobe effect. Sure the chuck often looks as though it is going slow, either backwards or forwards, but I have never managed to get the picture in complete stationary sync .I think it is one of those urban myths.
                              Right. I am waiting for the explosions to fall around me!
                              Andrew.
                              #306873
                                @mike89748
                                I did once get this "static chuck" phenomenon in a very noisy training room when I was doing evening classes. Got – quite rightly – admonished by the instructor for not first ensuring the clutch of the Harrison toolroom lathe was disengaged, and for not switching on the spotlamp before pressing the start button.The lathe was new, and quiet.
                                #306889
                                Harry Wilkes
                                  @harrywilkes58467
                                  Posted by Andy Carruthers on 12/07/2017 11:26:55:
                                  No your memory is ok I remember many years ago I worked with the works electrician and our job was to wire up a new machine shop he explained that the lighting was to be spread across the 3 phases because of said problem smiley
                                  #306894
                                    Posted by Joseph Noci 1 on 12/07/2017 14:44:26:
                                    Joe
                                    I recently did an EMC review of my workshop and was surprised to find my tubes (2 x conventional plus 1 HF) were "clean", unlike the lathe VFD. Of course my test was quick and the antenna crude, so I might have missed something. Even so, like everything else, presumably not all lamps are made to the same standard.
                                    Man made electronic smog around my house makes amateur radio difficult at all times. It's amazing how much crud disappears when I get the chance to listen on battery power during a power cut. I don't know whether to be pleased or annoyed that power cuts are so rare here!
                                    Joseph Noci 1
                                      @josephnoci1
                                      Dave, I couldn't agree more! All the really cheap AC-DC converters in every house hold appliances these days, printers, fax-machines, modems, mains driven LED lighting, FL lighting, etc – most of these are open frame switchers, in plastic housings and so it goes on! Like you, when there is a power failure I rush to the HF radio..My desk in the shack has a 2 tube HF FL light above the desk, which I turn off when trying to listen to HF and use a plain incandescent desk lamp instead! I suppose we are suppose to to Hamming via internet these days – whats with this HF nonsense!
                                      Joe
                                      #306917
                                      Robin Graham
                                        @robingraham42208
                                        Posted by Mark Rand on 12/07/2017 00:07:03:
                                        As to the replacement of the dead unit. Yes, get another one of the same spec (or a spec that matches the tubes, if there is any doubt) ….. The switch mode power supplies in the HF ballasts can fail quite enthusiastically and draw enough current in a very short time to give circuit breakers a good short-circuit test.
                                        Thanks Mark – sounds like my guess that HF ballast must be the culprit seems reasonable.
                                        Thanks also to others who replied.
                                        I have never had any problem with strobing – the guy who wired up my dungeon knew it was to be a workshop, and recommended HF for this very reason. They run at tens of kHz I think.
                                        I've considered replacing the fluorescent lighting with LED tubes (I think there is a discussion of these elswhere on this site), but as I have 16 x 5200 lumen fluorescents in total, it would be expensive up-front. I'm not sure about the benefits in terms of running costs either. There seems to be law of diminishing returns in terms of lumens per watt with LEDS – just had a look at simplyled.co.uk and the replacements they offer for 58W 5ft T8 tubes are rated 24W / 2550 lumens. Only £11.51 / tube mind, cheaper than when I last looked around. Maybe all lumens are not created equal though – I've replaced most of the GLS bulbs in the house with LED versions, and subjectively they seem brighter than their lumen rating compared with incandescents would suggest. I imagine perception of brightness varies between individuals though.
                                        Robin.
                                        #306919
                                        duncan webster 1
                                          @duncanwebster1
                                          This thread has prompted me to replace my workshop flourescents with LED. There seems to be a humungous choice, do I go for tubes, or that continuous strip? What colour temp. Anyone out there who knows?
                                          I've already replaced a lot of tungsten and CFL bulbs in the house with LED. In one fitting which has three BNC candle bulbs (ToolStation code18765) I get a lot of flickering. Is this because there are three bulbs close together, or just rubbish bulbs. I don't have a dimmer, and I tried replacing the switch to no avail.
                                          Edited By duncan webster on 12/07/2017 21:05:56
                                          #306925
                                          Frances IoM
                                            @francesiom58905
                                            I used cool white in the workshop + kitchen, warm in the living room – all were led panels – however there are now many more choices in colour temp from daylight thru to warm – if possible buy from a place with demo units or who is willing to swop panels once you have tried in situ – the candle leds unless they were designed with a ‘candle like’ flicker should not behave that way tho it is often difficult to find dimmers that will handle low wattage leds without flickering at low light levels.
                                            #306966
                                            Gordon Tarling
                                              @gordontarling37126
                                              Robin – I thought the same as you regarding lumen ratings until it was explained to me by a US pal. A standard fluorescent tube radiates light around its entire circumference and much of the light which goes above the horizontal is lost unless you are using some kind of reflector above the tubes. An LED tube only radiates light below the horizontal, so the perceived brightness is a bit higher. I had standard Tri-phosphor daylight (6000k) tubes rated at 5200lm in my shop and am replacing them with 24W Cool White tubes that are rated at 3230lm – the LED ones definitely make the shop brighter, though that could just be my perception.
                                              Duncan – I used 4000k Cool White LED tubes at the suggestion of a friend and find them just about right. Don't buy self-adhesive strips, as they have no built in reflector and they've always seemed dimmer to me anyway. As for your flickering three – suggest you try some different bulbs first. Dimmers specifically rated for LED use are readily available and those which I've tried work well.
                                              #307174
                                              Robin Graham
                                                @robingraham42208
                                                Posted by Gordon Tarling on 13/07/2017 11:27:04:
                                                Thanks Gordon, that makes sense. Where are you sourcing your tubes? As I've not yet got round to replacing the driver for the fluorescent unit, it may be worth using this as an opportunity for experiment. – but is it possible to use the old housing, or do I need to replace the whole shebang? The simplyled.co.uk people offer a plug and play LED driver to replace the ballast, but it's obviously designed for 50Hz lights with the ballast you just plug into the side of the unit.
                                                .Robin
                                                #307207
                                                Gordon Tarling
                                                  @gordontarling37126
                                                  Robin – these **LINK** are the tubes that I'm using. They don't require a driver, just a simple wiring modification to bypass the ballast. Diagram supplied with every tube. You may well have a TLC branch near you.
                                                  #307213
                                                  Andrew Tinsley
                                                    @andrewtinsley63637
                                                    Just a thought or two on LED lighting. I spent some time in the lighting industry and also did development work on LEDs at the beginning (40 odd years ago).
                                                    The one thing that some LED manufacturers don't tell you, is that the quoted lifetime of LED lighting refers to the lifetime of individual LEDs tested as individual units.
                                                    Now LED lifetime is critically dependent on temperature, so if you have LEDs in a group. Then the local temperature rises and down goes the LED life.
                                                    For example if you have an LED replacement bulb (like the old household lamp) and you put this in say a lamp shade that has no means of convection, then the bulb life is critically compromised. I have such reflectors and major brand LED light bulbs do no better than 1000 hours lifetime.
                                                    I have changed over to LED lighting and would not go back to GLS or compact fluorescent lamps. But beware of the smooth sales talk of the lighting manufacturers. You MUST keep the local temperature down otherwise the lifetimes are much reduced.
                                                    Andrew.
                                                    #307357
                                                    Robin Graham
                                                      @robingraham42208
                                                      Thanks for the link Gordon – no TLC branches near me (I'm in Derbyshire – they seem to be SE oriented), but presumably I can get similar things locally. Not found anything with that lumen/watt ratio yet though. Good to know they can be wired into standard housings, I think this may be the way to go.
                                                      Andrew – yes well aware of the hype, but the GLS bulbs I've replaced with LED's, whilst not lasting anywhere near quoted 'average life' have been cost effective. Interesting that temperature is critical. I'd assumed that it was the drivers that failed first but maybe not so?
                                                      Rob.