Yaskawa VS mini J7 inverter

Advert

Yaskawa VS mini J7 inverter

Home Forums Help and Assistance! (Offered or Wanted) Yaskawa VS mini J7 inverter

Viewing 12 posts - 1 through 12 (of 12 total)
  • Author
    Posts
  • #255625
    john fletcher 1
    Participant
      @johnfletcher1

      I have a Yaskawa VS J7 mini series inverter it is in working order. I would like to communicate with other Yaskawa users as I have a problem with altering the program. Please send me a PM and I will reply with our phone number and email address.John

      Advert
      #32779
      john fletcher 1
      Participant
        @johnfletcher1
        #255858
        Bikepete
        Participant
          @bikepete

          Hi John,

          I hope someone has helped you by now. If not, I fitted one of those to my drill a few years ago and would be happy to have a go at assisting you – but I would very much prefer to do so in public, here, so that others can chip in too and so that other readers can possibly benefit from reading about the problem and solution. If you could post a description of the problem then I'm sure I or someone else will be able to assist.

          You probably already have it but the user manual is available here on the Yaskawa website.

          If there is some reason it absolutely must be done by private correspondence then please feel free to message me.

          Cheers

          Pete

          #255862
          Ian Parkin
          Participant
            @ianparkin39383

            I have a few of these fitted to various machines

            so if you want to post what you are having trouble with or you can pm me for my phone number

            I find them one of the more problematical inverters to program however

            #255870
            Rik Shaw
            Participant
              @rikshaw

              I have a Yaskawa V1000 which I bought of ebay and which is sitting in a cupboard waiting for me to install on lathe or shaper – cannot make my mind up at mo. for various reasons – apart from which I am windy about *sparks* work. So I'll be watching this thread with interest..

              Rik

              #255871
              john fletcher 1
              Participant
                @johnfletcher1

                To all readers, my inverter is up and running as has been for several years. At the moment I have variable speed from around 950 rpm to about 2500. I would like to have around zero rpm upwards. Reader Quill ,has already come to my rescue and suggested looking at setting 42 which I have done and no change. I have been through the setting and written them up but cannot publish them here. If any one would like to check them out for me, please send me your details via a PM with your email address and then I'll forward you a copy.John

                #255915
                Martin 100
                Participant
                  @martin100
                  Posted by john fletcher 1 on 14/09/2016 17:34:36:

                  At the moment I have variable speed from around 950 rpm to about 2500. I would like to have around zero rpm upwards.

                  Check parameter N14

                  #255920
                  John Stevenson 1
                  Participant
                    @johnstevenson1

                    Agreed N14

                    Used to fit loads of these before we moved on the IMO's

                    Never had a problem with them and they programmed up fine.

                    #255945
                    Ian Parkin
                    Participant
                      @ianparkin39383

                      After seeing johns list of settings it's iikely to be N31 which over rides N14

                      #255946
                      John Stevenson 1
                      Participant
                        @johnstevenson1

                        Could be but only if it's set higher that N14.

                        Most people only change to first few parameters and ignore the later ones but still a good point to check.

                        I was going to post a table of parameters we used to set to but unfortunately they are saved in an early version of page plus and none of my current versions will open it. surprise

                        #255969
                        Ian Parkin
                        Participant
                          @ianparkin39383

                          John it's set to 50% according to johns list defaults zero so a previous owner has set it high

                          #256015
                          john fletcher 1
                          Participant
                            @johnfletcher1

                            Many thanks to Ken, Ian, Andy and any others who may have contacted me. It was item 31, once adjusted it works like a dream. I was given the inverter 10/15 years ago, its was part of a printing machine being scrapped and at the time I was very happy to be able to run a 3 phase motor with some speed control. I didn't dare to fiddle with the program, obviously not much better now. Great to know that helpful people are still around.John