  • #26420
    Mike Poole
    Participant
      @mikepoole82104
      Advert
      #394169
      Mike Poole
      Participant
        @mikepoole82104

        I the book “Electric Motors” in the workshop practice series the author recommends using a screwdriver blade to short the supply that you have isolated to prove you have got the right circuit. If you have not succeeded in isolating the supply you could be showered in small bits of molten metal. I cannot support this technique of testing and if you do not have the means to check properly should you really be doing the job? I have had practical experience of converting a pair of cutters into more of a crimper than cutter and shorting a screwdriver does blow the end into oblivion. Accidents do happen even to people who do know the risks and what they are doing but no matter how careful you are the unexpected can still bite you.

        Mike

        #394179
        Howard Lewis
        Participant
          @howardlewis46836

          A Multimeter, set to the correct range, would be a safer and less destructive test method, surely?

          Even flashing a lamp in a holder across the supply would be better than what the book advocates.

          Howard

          #394181
          Neil Wyatt
          Moderator
            @neilwyatt

            You could use a pair of wirecutters. If there is a bang, sparks and part of the cutting edge of the cutters disappears accompanied by a burst of bad language, the supply is still live. A bonus is that you can now use the cutters as wire strippers for mains cable. Worked for me but I don't plan to repeat the exercise.

            Or much more safely, what about good old mains tester screwdrivers that glow when touched to a live wire (or the modern type with an LCD display)? They have the advantage you can test a single wire, you don't need to complete the circuit.

            Do get a reputable one (about £2.50 from Farnell) not a cheap one.

            Neil

            <edit> With the tester I always test before isolating to prove it is working, then disconnect and if it doesn't light up all is OK.

             

            Edited By Neil Wyatt on 01/02/2019 15:43:29

            #394182
            Phil Whitley
            Participant
              @philwhitley94135

              Quite agree Mike Poole far to dangerous doing it that way! use one of these https://martindale-electric.co.uk/martindale-vt12-voltage-indicator-p-1651.html No connection other than a very satisfied user for many years, and they are under £20, and test from 12v to over 600v safely. Although they have got a bad name for no reason at all, a neon screwdriver costs pennies, and is better than nowt, and much better than shorting across the terminals!

              #394183
              Martin Connelly
              Participant
                @martinconnelly55370

                I've got a non contact voltage indicator (Iso-Tech IVP-1) and would recommend them for anything to do with mains voltage electricity.

                Martin C

                #394186
                Georgineer
                Participant
                  @georgineer

                  Like this, Michael? That one took out the company's 100 amp fuse and spoiled my favourite screwdriver. Embarrassing it was, but no harm done except the bright green glow in the middle of each eyeball which took an hour to disappear.

                  Father taught me that with dry shoes on a dry floor and dry fingers (and your other hand in your pocket) it is quite safe to touch a live wire. If it is live, you feel a very mild tingle. It's never done me any harm – yet! Obviously if you touch the other wire at the same time, all bets are off!

                  There is of course the neon mains tester as an alternative, which can even detect mains voltage through a single layer of insulation if applied with a dab of 'monkey juice'.

                  I came across an American book of about the 1940s which recommends testing for mains voltage by putting the wires to your tongue, though it admits that some sensitive souls might find it a bit much. Of course, their mains voltage is lower than ours.

                  George

                  bangy!.jpg

                  #394192
                  Mike Poole
                  Participant
                    @mikepoole82104

                    When apprentices came to our department they would be in their third or fourth year, it was remarkable how much they would struggle to explain the isolation and testing procedure for single and three phase circuits and many would say use a multimeter when a proper Martindale tester and proving unit were available. The argument against using a multimeter is that it is easy to select the wrong range and the design of the meter does not make a failsafe device. I feel there is a definite pecking order of devices to test with and the purpose made testers have to be at the top, anything else has some reservations but are better than nothing. Getting it wrong could be fatal.

                    Mike

                    #394193
                    Andy Carruthers
                    Participant
                      @andycarruthers33275

                      Half a lifetime ago I worked on a valve Non-Directional Beacon and managed to get 3 belts within 30 minutes, each one hurt more than the first

                      Not doing that again

                      #394198
                      Old Elan
                      Participant
                        @oldelan

                        Sadly quite a few of 'that' series are no longer fit for purpose and should be removed from sale in my opinion.

                        On the subject of the cutters, my builder employed a 'qualified' sparks who left live tails in my garage from the utility room next door. Silly me, I thought they were from the CU that he had installed for ALL the garage/workshop power which was isolated.

                        Melted cutters as above.

                        Qualified? Hmmmm

                        Edited By Old Elan on 01/02/2019 16:52:42

                        #394203
                        Howard Lewis
                        Participant
                          @howardlewis46836

                          As an Apprentice, during my year in the Electronics and vibration lab, with a floor insulated to 5 Kv, before going home for the night, I pulled the top off a 13 amp plug. Fingers and thumb neatly across Live and Neutral (240 Volts AC ) Obviously not fatal, but a shock in all senses of the word! Made sure that the plug top was secure next morning!

                          And, Yes it is possible to ruin a multi meter by putting across the mains when set to the wrong range!

                          Howard

                          #394206
                          David Davies 8
                          Participant
                            @daviddavies8

                            If anyone wants to read further on this subject I suggest searching on the internet for ''Electrical test equipment for use on low voltage electrical systems'' Guidance Note GS38 (Fourth edition). This is a 9 page HSE document, available free as a PDF, which is aimed at the workplace but is still relevant at home.

                            Cheers

                            Dave

                            #394211
                            Jeff Dayman
                            Participant
                              @jeffdayman43397

                              If tests are planned to be done with screwdrivers, the trick is to use your neighbour or co-worker's screwdrivers! devil

                              #394214
                              SillyOldDuffer
                              Moderator
                                @sillyoldduffer

                                Before touching the bare 3-phase overhead wires in my street the men always seem to hook a hefty earthed pole with an insulated handle on the wires to make sure the power really is off. Once they did it and there was a loud bang when one of the giant fuses at the top of the pole exploded. Yes they were embarrassed!

                                Friend of mine who repaired valve TVs for Radio Rentals used to test for mains with his thumbnail. Reckoned he could sense the wire was hot without getting an actual belt. I chose not to try it…

                                As for father saying it's OK to touch a live wire, I agree 250Vac isn't very dangerous but surely it's not worth the risk? So much depends on your state of health, age, weight, skin resistance, time the shock lasts, and the path taken by the amps through your body.

                                Make a good article for MEW though. devil

                                Can I have 100 volunteers to sign a liability disclaimer please? After strapping these heros into a wet chair and connecting the mains via crocodile clips for a full 30 seconds I'll write up the results. There will be interesting graphs and colour photographs. I think there's a good chance of stopping a few hearts, plus perhaps a death or two due to complications resulting from burns. Most likely all participants will suffer psychological damage, and some will be permanently affected. There's a world of difference between briefly touching a live wire and what happens if the victim is held in contact until someone cuts the power.

                                The advantage of using a screwdriver rather than relying on a sophisticated test-set is that the instrument can't go wrong! When working on the mains, I check first with a neon screwdriver and then short the wires as well.

                                Dave

                                #394215
                                Mike Poole
                                Participant
                                  @mikepoole82104

                                  Glad there was no lasting damage with the screwdriver modification George. Dave that document sums things up nicely, much better info than the advice to short a hopefully dead circuit. The electricity at work act is quite a brief document but is quite onerous if taken seriously. When it came out all electrical personnel in our company were trained on its impact on electrical maintenance, around 130 people were trained. I noticed over the years that personnel, both managers and shop floor changed and the importance was forgotten. I suppose when the accident happens as it surely will they will wake up with a little kick from the HSE.

                                  Mike

                                  Edited By Mike Poole on 01/02/2019 18:10:06

                                  #394217
                                  An Other
                                  Participant
                                    @another21905

                                    There was a time I could have done with some insulation – more years ago than I care to remember, I was working on an old rotating coil PPI radar display. (This generated the rotating 'sweep' on the tube by mechanically rotating the coils carrying the sweep generation signal – it was a long time ago!). I was following all the accepted safety rules of the the time – one hand in pocket, nothing dangling loose, etc, etc.

                                    The testing required the power to be on – about 18 kV supply to the tube if I remember correctly. A colleague walked past behind me, and accidentally pushed me – I touched the HV. The resulting shock flung me back against a wall so I cracked my head, and I bit deeply into my tongue. It took about an hour or so to stop shaking, and seeing red and blue spots. I think I was lucky to to suffer more serious injury.

                                    Nothing to do with insulation, but I guess it shows a need to take care with high voltage.

                                     

                                    Edited By An Other on 01/02/2019 18:16:29

                                    #394218
                                    Brian G
                                    Participant
                                      @briang

                                      My father (a dockyard wireman) taught me to touch potentially live wires by sweeping my (moistened) finger down quickly at arm's length so I touched them in passing but the momentum of my arm would take my hand away. I still do that even after testing the wires with a neon screwdriver, voltage tester or multimeter as I would rather not find out that the neon etc. had failed by getting a proper jolt.

                                      Even after testing it is still not a bad idea to short the circuit, as it could just be dead because of an intermittent fault and on domestic circuits you cannot just put a padlock on the breaker. You can also use a live circuit just to make sure that whatever you tested with really works. (I have a healthy paranoia about electricity ever since I first encountered busbars instead of cables in the pit at a substation).

                                      Brian

                                      EDIT: And whatever you do, don't reach down to a potentially live cable!  If it gets you, you want to fall away, not toward…

                                      Edited By Brian G on 01/02/2019 18:21:27

                                      #394220
                                      Mike Poole
                                      Participant
                                        @mikepoole82104

                                        I have worked with quite a few people who lick their finger and do the dab test, not a check I would endorse. I expect when they do it on a live circuit they will give up doing it.

                                        Mike

                                        Edited By Mike Poole on 01/02/2019 18:33:37

                                        #394222
                                        john fletcher 1
                                        Participant
                                          @johnfletcher1

                                          It's almost 70 years since I started in the electrical industry and how I wish others wouldn't be so flippant regarding electricity and electric shock. Each and every one of us is different in make up, so what is a shock to one is not to another, I'm reliably told its hand to hand shock which are the killer and its our hearts which are vulnerable. I've always worked on the basic SWITCH OFF and test with the appropriate tester to prove it and test the tester from time to time. Some of our lads failed the AM2 test as they attempted to test 240 volts with a broken tester. Keep one hand in your pocket. Also just because you have an RCD it won't give you exemption from a shock. DISCONNECT. John

                                          #394241
                                          Phil Whitley
                                          Participant
                                            @philwhitley94135

                                            And of course, we all need to remember that the first thing you test is the test equipment! EVERY TIME!

                                            #394246
                                            peak4
                                            Participant
                                              @peak4

                                              Someone sent me this via Facebook the other day; Don't try this at home as they say. surprise

                                              #394257
                                              Samsaranda
                                              Participant
                                                @samsaranda

                                                I would disagree with the comment that 250 Vac is not very dangerous, back in the early 60’s when I was in the Air Force, a colleague of mine took a hefty 230 volt shock which nearly killed him. It happened one morning when a group of us were gathered round a workbench discussing how we could sort out the world, one of our number had an electric drill in his hands, one of the old Wolf drills with the metal casing, he also had a small dumpy screwdriver in his hands and his mind must have been somewhere else because he used the screwdriver to gradually unscrew the small plastic cap located at the rear end of the drill casing which was the cap holding one of the motor brushes in place. The cap unscrewed easily and the spring holding the brush in place caused the cap to fly off, at the same time the screwdriver blade was propelled into the brush holder hole, this caused the whole drill casing to become live and suddenly our colleague was leaping around clutching the drill and shouting as if in pain, well this particular colleague was well known for practical jokes and so all of us in the group believed it was one of his jokes again. It very soon dawned on us when we saw sparks leaping out of the drill casing that this was for real and not a stunt, one of us swiftly switched the drill off at the socket and ripped the plug out of the socket, our afflicted colleague collapsed into a semi conscious heap on the floor, we summoned the medics who took him away and attended to him, he came back to work later that day and was certainly looking very pale, the medics confirmed that he was nearly a goner, if we hadn’t disconnected the power when we did he wouldn’t have made it. No such thing as earth leakage trips in those days, even fuses on circuits were pretty crude usually being only fuse wire, no such things as slow blow or rapid blow. Since that day I have always respected live electrics, doesn’t mean I haven’t had the occasional belt, have had to use various voltages up to 200kv and currents up to 1200 amps, albeit the high currents were pretty low voltages.

                                                Dave W

                                                #394258
                                                Robert Atkinson 2
                                                Participant
                                                  @robertatkinson2

                                                  Anything over 50V AC is potentally lethal. Just because you touched xxV and lived to tell does NOT make it safe. Unfortunatly the people who died are not on here to tell you how it went wrong. You can't be lucky everytime. Relying on dry hands, shoes etc is just plain stupid. Yes skin is the main thing that limits current but a burr on a screw head or wire strand can poerce your skin and bypass that.

                                                  The correct way to check for a dead circuit is to use a test lamp and a proving unit (low current battery operated 200V supply) 1st you check the lamp work with the proving unit then test the circuit with it. Next best is a multimter with low impedance like a Fuke with VoltChek, a contactless voltage detector or a neon screwdriver.

                                                  Ideaally have an isolator switch in the feed to the workshop, turn it off, and iif anyone else is around put a padlock on it. Over the top? Nanny state? Heleth and safety overkill? maybe, but you only get it wong once!

                                                   

                                                  Robert G8RPI.

                                                  Edited By Robert Atkinson 2 on 01/02/2019 21:38:59

                                                  #394267
                                                  Andy Carruthers
                                                  Participant
                                                    @andycarruthers33275

                                                    All well and good to check circuits have discharged using a brinkley stick before touching high voltage. I used to work on RADAR with 28.5kV for EHT to the Magnetron, after power down, we would test the brinkley stick (100 ohm resistor to earth) before use – but none of us ever tested after each individual use, there were several points to "de-bollock" before work commenced

                                                    Occasionally the resistor would need replacing before first use, meaning the resistor had blown at some point

                                                    #394270
                                                    SillyOldDuffer
                                                    Moderator
                                                      @sillyoldduffer
                                                      Posted by Samsaranda on 01/02/2019 21:16:55:

                                                      I would disagree with the comment that 250 Vac is not very dangerous, back in the early 60’s when I was in the Air Force, a colleague of mine took a hefty 230 volt shock which nearly killed him. …

                                                      Dave W

                                                      Ah but Dave, your colleague wasn't killed!

                                                      By 'not very dangerous' in the context of a mains electricity, I meant that large numbers of people are shocked every year, including children and sick people, and almost all of them survive with no ill effects. While I don't imply electric shocks are safe, I do say domestic electricity isn't as relatively dangerous as many other common activities, perhaps because it's normally well contained and the pain teaches people not to repeat the experience.

                                                      The risks vary by age and country. In the west, much more likely to kill you than electricity is smoking, using the road, rich diet, booze, sport, drugs, suicide, sex, disease, or your job. Fishing is the most dangerous occupation, then construction, and farming. Professional driving isn't healthy. Many other dangerous jobs are relatively safe because sensible precautions are taken.

                                                      Although many accidents occur during ordinary life, most preventable accidents occur on the roads. Then come things like poisoning (mostly drugs and alcohol), drowning, and falls. Roofing is a dangerous occupation for youngsters, but falling gets even larger numbers of older people as we age and get wobbly! In the USA accidental discharge of firearms is a top ten killer that doesn't figure in the statistics of other developed countries. However firearms aren't as dangerous as smoking which kills over 400,000 Americans annually, or medical errors (about the same number).

                                                      Domestic electricity isn't a common cause of death or injury though it does happen. Safe enough provided you don't mess with it, and no-one should.

                                                      Dave

                                                    Viewing 25 posts - 1 through 25 (of 60 total)
                                                    • Please log in to reply to this topic. Registering is free and easy using the links on the menu at the top of this page.

                                                    Advert

                                                    Latest Replies

                                                    Home Forums General Questions Topics

                                                    Viewing 25 topics - 1 through 25 (of 25 total)
                                                    Viewing 25 topics - 1 through 25 (of 25 total)

                                                    View full reply list.

                                                    Advert

                                                    Newsletter Sign-up