  • #577209
    Roger Davies 4
    Participant
      @rogerdavies4

      Thank you Clive. I’ll check these in the morning. Much appreciated.

      Advert
      #577213
      Neil Lickfold
      Participant
        @neillickfold44316
        Posted by Clive Brown 1 on 28/12/2021 21:39:00:

        Err 1 indicates keypad operation error. The instruction say that parameters 00-05 & 00-06 must be set to 0 to enable the keypad as frequency source

        .Also 13-06 locks the keypad if not 0.

        Have you checked these?

        However, I would have expected the factory reset to have set these values.

        The factory reset only effects the 02- parameters. silly I know. You wold think that it would reset all of the parameters to the factory default, but not on this one that I could see. I am only going by the manual and what it mentions on the parameter to reset 1250. I am sure it is just a few things that are over looked is the issue. I am not very familiar with the 3 wire remote control that this one is being set at. Mine is the 2 wire control and for me seemed to be the more simple way of doing things, using a 3 way switch in the original control box that came with my lathe from 1972. Centre is open, left hand is closed forward. Righthand is closed reverse. This one uses a push button On S1 , and push button Stop S2 , with forward and reverse being either open or closed for the direction on S3. In amongst it will be a conflict of parameter settings that have been inadvertently over looked and can take quite some time to find the issues.

        Edited By Neil Lickfold on 28/12/2021 22:16:01

        Edited By Neil Lickfold on 28/12/2021 22:16:36

        #577238
        Clive Brown 1
        Participant
          @clivebrown1

          This is one of the diagrams I used for the remote panel for my Teco510 a while back. All components from Inverter Drive Supermarket. They seem to have now removed this particular pdf.

          Pencil refers to my own wiring colours.

          img_20211229_0001.jpg

          #577239
          Roger Davies 4
          Participant
            @rogerdavies4

            Thank you Clive. I think that’s what I’m aiming for. Moat grateful.

            Roger

            #577311
            Roger Davies 4
            Participant
              @rogerdavies4

              So thank you all for your help. I sat down this morning and went through every parameter, top to bottom. I then did a factory reset… on then returning to the 00 parameters, they were wrong, and would not change giving loads of error messages…. Very frustrating. I almost gave up. But I persisted, reset the motor parameters at 02 and on returning then to the 00 parameters was allowed to change them. Lo and behold (its christmas!) the lathe the ran in the right direction. I can control from the remote stop and start buttons, and the fwd/rev switch. The only thing that isnt working yet is

              #577312
              Roger Davies 4
              Participant
                @rogerdavies4

                the potentiometer on the remote, but the one on the vfd works for now. I’ll return to that in due course. Thanks to all for your kind help, suggestions and support. 

                Edited By Roger Davies 4 on 29/12/2021 16:11:42

                #577313
                Roger Davies 4
                Participant
                  @rogerdavies4

                  So,for the record the answer to my problems was:

                  1. factory reset

                  2. enter motor parameters (correctly) at 02.

                  3. Only then set the 00 parameters.

                  doing 00 before 02 doesn't work.

                  Roger

                  #577314
                  Clive Brown 1
                  Participant
                    @clivebrown1

                    For the remote pot.

                    00-05 = 2.

                    Pot goes across 10v and AGND with the wiper to AVI.

                     

                    Edited By Clive Brown 1 on 29/12/2021 16:22:34

                    #577319
                    Roger Davies 4
                    Participant
                      @rogerdavies4

                      Thanks Clive, I’ll give that a go tomorrow.

                      cheers, much appreciated

                      Roger

                      #577328
                      noel shelley
                      Participant
                        @noelshelley55608

                        The motor IS configured for 220V 3phase ? Star not Delta 415 ? The 1.5A is the FLA for 415V not the no load current for 220V.  Noel.

                        Edited By noel shelley on 29/12/2021 17:11:25

                        #577352
                        Roger Davies 4
                        Participant
                          @rogerdavies4

                          Hmm, thanks Noel, I’ll double check.

                        Viewing 11 posts - 26 through 36 (of 36 total)
                        • Please log in to reply to this topic. Registering is free and easy using the links on the menu at the top of this page.

                        Advert

                        Latest Replies

                        Home Forums General Questions Topics

                        Viewing 25 topics - 1 through 25 (of 25 total)
                        Viewing 25 topics - 1 through 25 (of 25 total)

                        View full reply list.

                        Advert

                        Newsletter Sign-up