Linisher cuts out, what to do…?

Linisher cuts out, what to do…?

Home › Forums › Help and Assistance! (Offered or Wanted) › Linisher cuts out, what to do…?

Viewing 25 posts - 1 through 25 (of 54 total)
  • Author
    Posts
  • #314037
    Richard Harris 5
    Participant
      @richardharris5

      My dad had an Axminster 150 x 2000 belt linisher arrive this morning but he can't get it starting… and as Axminster aren't open now until Tuesday, I thought I'd ask here to see if any kind folk might be able to point us in the right direction

      This model: http://www.axminster.co.uk/axminster-engineer-series-150mm-belt-linishers-ax942736

      It is single phase.

      We bought the correct cable, plug and fuse but when we start it up, it begins for less than a second but then cuts out immediately and won't start again – the fuse is blown. A new fuse just repeats the problem, it keeps blowing. Nothing trips.

      Here are the details we're given on the electrics via the manual (you can also download the manual via the link above)

      Voltage
      The input power supply of the machine is 1/PE, AC220V for JSG75A and
      JSG100A.
      The input power supply of the machine is 3/PE, AC380V for other models.
      !10 / 1! 5
      If it is necessary to transport the machine after using, please protect cables
      firstly and discharge the scrap iron.
      ■ Frequency
      0.99~1.01 times of rated frequency ( 50 Hz , continuous working)
      0.98~1.02 times of rated frequency(50Hz, short period working)
      ■ Harmonics
      The sum of 2nd-5th distorted harmonic must not exceed 10% of RMS of
      voltage. An additional 2% of RMS of line voltage is allowed to for the sum of
      6th-30th harmonic.
      ■ Unbalanced voltage
      Neither negative nor zero sequence component is allowed to exceed 2% of the
      positive sequence component.
      ■ Short-circuited protection and incoming cable
      The machine should have short-circuited protection device at the power supply end by
      the end-user. The rated current is recommended as 10A, and the diameter of the
      incoming line must not be less than 3×1.5mm2(Black) +1.5mm2(PE, Green-and-Yellow).

      A couple of photos of the plug that he wired below. L/+ means live, we assume??

      Any ideas what could be going wrong here? The cable is 5 meters by the way, I assume that alone wouldn't have any effect on the fuse ?

      We're a bit lost as it seems we've done everything right… He was quite excited when it arrives but the enthusiasm has vanished since it won't start up

      #33057
      Richard Harris 5
      Participant
        @richardharris5
        #314042
        Keith Long
        Participant
          @keithlong89920

          What is the rating of the fuses that you keep blowing? Can you pull the belt over by hand, or have you tried starting up with the belt tension off?

          There seems to be a discrepancy between the blurb in the catalogue that suggests a 10 amp fuse and the wiring diagram in the manual that suggests a 12 amp fuse. If the full load power is 3kw and the voltage is 230 volt then that is 13 amps continuous. Looks like you should try a heftier (but not silly big) fuse. It's most probably the initial start up current that's popping the fuses.

          #314043
          Richard Harris 5
          Participant
            @richardharris5
            Posted by Keith Long on 26/08/2017 15:54:39:

            What is the rating of the fuses that you keep blowing? Can you pull the belt over by hand, or have you tried starting up with the belt tension off?

            There seems to be a discrepancy between the blurb in the catalogue that suggests a 10 amp fuse and the wiring diagram in the manual that suggests a 12 amp fuse. If the full load power is 3kw and the voltage is 230 volt then that is 13 amps continuous. Looks like you should try a heftier (but not silly big) fuse. It's most probably the initial start up current that's popping the fuses.

            Thank you Keith! I appreciate your help.

            The belt turns easily by hand, but I could maybe try removing the belt and seeing if it start's without this (although I don't know why that would cause a fuse to blow, and it is 3HP, so you'd think if the tension was too high it would still move).

            I hadn't noticed anything re the fuse difference, what page are you seeing the diagram on? I'll suggest trying a 13am fuse in a moment to him and see what happens…

            #314044
            Mike Poole
            Participant
              @mikepoole82104

              I would think that starting a 3.0kw motor on a ten amp fuse is likely to pop the fuse, try removing the abrasive belt and see if it will start off load. Personally I would be inclined to up rate the fuse and see if it starts, switch off quickly if it does not start. The ideal solution would be to check the motor does not have a fault before deviating from the recommended values. As it is brand new it is probably best not to do anything to invalidate the warranty and wait till Tuesday. Slipping the abrasive belt off will not invalidate the warranty.

              Mike

              #314045
              JasonB
              Moderator
                @jasonb

                What have you got on the other end of your 5m lead, a 13amp plug top? You really want to wire that 16A socket directly

                #314046
                Richard Harris 5
                Participant
                  @richardharris5

                  Update: Tried 13 amp fuse, no real difference. Begins to start then cuts out immediately. ..

                  #314047
                  Keith Long
                  Participant
                    @keithlong89920

                    The manual I was looking at was the download suggested in the Axminster catalogue (on-line). The wiring diagram is on page 16, shows what I take to be fuses (12A) in the live and neutral legs feeding the machine. A 13 amp fuse certainly shouldn't cause any problems, that's the minimum I'd be using for a 3kw machine on a normal 240v single phase supply. The motor could well be trying to draw several times its full load current briefly on start up so be prepared for the 13 amp to pop as well!

                    Edit

                    I see it did!!!

                     

                    Edited By Keith Long on 26/08/2017 16:21:15

                    #314048
                    Richard Harris 5
                    Participant
                      @richardharris5
                      Posted by JasonB on 26/08/2017 16:13:48:

                      What have you got on the other end of your 5m lead, a 13amp plug top? You really want to wire that 16A socket directly

                      Wire it directly into a 16A socket? Would that make much difference? We haven't yet committed to a location to keep it, but would be able to do this eventually.

                      #314049
                      Richard Harris 5
                      Participant
                        @richardharris5
                        Posted by Mike Poole on 26/08/2017 16:04:02:

                        I would think that starting a 3.0kw motor on a ten amp fuse is likely to pop the fuse, try removing the abrasive belt and see if it will start off load. Personally I would be inclined to up rate the fuse and see if it starts, switch off quickly if it does not start. The ideal solution would be to check the motor does not have a fault before deviating from the recommended values. As it is brand new it is probably best not to do anything to invalidate the warranty and wait till Tuesday. Slipping the abrasive belt off will not invalidate the warranty.

                        Mike

                        Thanks Mike. I have no idea how we'd test the motor unfortunately. I may try slipping off the belt and testing with a higher amp fuse if we have some around, thank you for the suggestion.

                        #314050
                        Neil Wyatt
                        Moderator
                          @neilwyatt

                          If its rated 3kW @ 230V, that's about 13 amps. It's a bit like trying to run a fan heater on full heat AND a kettle on the same plug.

                          As Jason says, it should be wired directly to a suitable amperage supply with a 16A socket. Even a 13A fuse will be pushing you luck and almost certain to overheat even if it doesn't keep blowing.

                          Axminster's website says: "N.B. These machines are designed to be bolted to the floor for stability, and we recommend that they are hard wired by a competent electrician."

                          Neil

                          Edit the manual is confusing as 10A fuses would be OK for 3-phase use, but not single phase.

                          Edited By Neil Wyatt on 26/08/2017 16:38:05

                          #314051
                          JasonB
                          Moderator
                            @jasonb

                            If you are going to be using machines that will draw these sorts of current then get some 16A wall mounted socket outlets wired back to your fuseboard on a dedicated circuit.

                            The start up current is likely to be more than a 13A fuse in a 3 pin plug can take.

                            #314052
                            Neil Wyatt
                            Moderator
                              @neilwyatt

                              I've deleted a post which made totally unfounded criticism of the supplier.

                              Neil

                              Edited By Neil Wyatt on 26/08/2017 16:30:49

                              #314054
                              Frances IoM
                              Participant
                                @francesiom58905

                                even on a 16A supply you will probably need a type C RCBO (ie a slow overcurrent trip) to allow for the starting inrush current

                                #314058
                                Richard Harris 5
                                Participant
                                  @richardharris5
                                  Posted by Neil Wyatt on 26/08/2017 16:25:14:

                                  If its rated 3kW @ 230V, that's about 13 amps. It's a bit like trying to run a fan heater on full heat AND a kettle on the same plug.

                                  As Jason says, it should be wired directly to a suitable amperage supply with a 16A socket. Even a 13A fuse will be pushing you luck and almost certain to overheat even if it doesn't keep blowing.

                                  Axminster's website says: "N.B. These machines are designed to be bolted to the floor for stability, and we recommend that they are hard wired by a competent electrician."

                                  Neil

                                  Edit the manual is confusing as 10A fuses would be OK for 3-phase use, but not single phase.

                                  Edited By Neil Wyatt on 26/08/2017 16:38:05

                                  Thanks Neil. It is confusing… not really sure what amp the fuse should be for Single Phase. But you are right, i think this should be hard wired in.

                                  #314059
                                  Richard Harris 5
                                  Participant
                                    @richardharris5
                                    Posted by Frances IoM on 26/08/2017 17:03:54:
                                    even on a 16A supply you will probably need a type C RCBO (ie a slow overcurrent trip) to allow for the starting inrush current

                                    Would the best solution be to hard wire it into a 16amp socket, and then put a Type C RCBO in front of that? Is that how it would work? We do have an electrician we use, but if it's relatively simple my dad is quite competent at doing smaller tasks.

                                    #314060
                                    Richard Harris 5
                                    Participant
                                      @richardharris5
                                      #314061
                                      Richard Harris 5
                                      Participant
                                        @richardharris5
                                        Posted by JasonB on 26/08/2017 16:26:05:

                                        If you are going to be using machines that will draw these sorts of current then get some 16A wall mounted socket outlets wired back to your fuseboard on a dedicated circuit.

                                        The start up current is likely to be more than a 13A fuse in a 3 pin plug can take.

                                        Thanks Jason. This certainly seems to make sense as to why it begins to start up and then cuts off immediately (and blows the fuse)

                                        #314063
                                        Neil Wyatt
                                        Moderator
                                          @neilwyatt

                                          No, you would replace the appropriate trip back at the fuse board.

                                          Neil

                                          #314067
                                          Richard Harris 5
                                          Participant
                                            @richardharris5
                                            Posted by Neil Wyatt on 26/08/2017 17:29:22:

                                            No, you would replace the appropriate trip back at the fuse board.

                                            Neil

                                            Ah I see… I'm not sure this could be done on the fuse board in the house… this is running to an outbuilding (which has no fuse board). Would it be feasible / make sense to add a fuse board in the outbuilding?

                                            #314068
                                            SillyOldDuffer
                                            Moderator
                                              @sillyoldduffer

                                              The motor is rated 3kW at 220V. Doesn't that mean it would be a 3.6kW motor at 240V? If so that's nearly 15Amps.

                                              My guess is that the machine's motor is too big for a standard 13A feed hence Axminster's recommendation to have it wired by an electrician. .

                                              Dave

                                              #314069
                                              JasonB
                                              Moderator
                                                @jasonb

                                                Yes best bet is to have a separate fuse board in the workshop with circuits for lighting, sockets and also the heavier machines. Talk with your electrician as you may well now be drawing more current from the house than you were before so cable sizes etc need to be right.

                                                Had the machine been able to run off a 13amp plug then I'm sure Axminster would have supplied it with one rather than the 16A

                                                That screwfix one is too low an ampage.

                                                Edited By JasonB on 26/08/2017 18:28:51

                                                #314070
                                                Frances IoM
                                                Participant
                                                  @francesiom58905

                                                  this machine + whatever other machines you run are too much for what sounds like a trailing cable fed from a domestic 13A socket – you need to get a professional electrician to look at your set up – certainly I suspect a separate fuse board will be required but also the correct supply cable + earthing which will depend on the distance to the outbuilding.

                                                  #314071
                                                  Neil Wyatt
                                                  Moderator
                                                    @neilwyatt
                                                    Posted by Richard Harris 5 on 26/08/2017 17:58:32:

                                                    Posted by Neil Wyatt on 26/08/2017 17:29:22:

                                                    No, you would replace the appropriate trip back at the fuse board.

                                                    Neil

                                                    Ah I see… I'm not sure this could be done on the fuse board in the house… this is running to an outbuilding (which has no fuse board). Would it be feasible / make sense to add a fuse board in the outbuilding?

                                                    Yes.

                                                    My shed has a 32A (IIRC) spur from the main board and a small distribbution box with 3-way+ RCCB (lights, ring main, heater or could be a 16A outlet) .

                                                    Neil

                                                    #314098
                                                    Richard Harris 5
                                                    Participant
                                                      @richardharris5

                                                      Thanks all for your help, it is appreciated. I'll pass this info onto my dad. He has been speaking for a while about sorting out the electrics in the outbuilding and having the electrician take a look at it, so this seems like a prime opportunity to get it sorted…

                                                    Viewing 25 posts - 1 through 25 (of 54 total)
                                                    • Please log in to reply to this topic. Registering is free and easy using the links on the menu at the top of this page.

                                                    Latest Replies

                                                    Viewing 25 topics - 1 through 25 (of 25 total)
                                                    Viewing 25 topics - 1 through 25 (of 25 total)

                                                    View full reply list.