      The consumer unit in the hut has a 6a and 32a MCBs



      In the hut I am running a hobby mill and lathe. The mill has a powered feed for the table and if I quickly switch from forward to backward the MCB trips. However its not the MCB in the hut but the one that the armored cable is attached to in the house which is also 32A.



      I am wondering if I should change the MCB in the hut to say a 20a/25a MCB?

      Advert
      #26206
      petro1head
      Participant
        @petro1head
        #373470
        Frances IoM
        Participant
          @francesiom58905

          might be worth checking what type of MCBs(eg a slo-blow might be better at house end of cable) you have at each point

          #373472
          Brian G
          Participant
            @briang

            Do you know what type of MCBs are in each consumer unit? A type B MCB should trip before a type C, which in turn should trip before a type D of the same rating. If the consumer unit in the house is a type A, and that in the workshop a type B or C, simply swapping them may stop the trips.

            That still doesn't solve the cause of the trips, which appears to be a momentary current of at least 90A. I wonder if you could prevent this by pausing before reversing, perhaps using a reversing starter with inbuilt delay?

            Brian

            #373473
            petro1head
            Participant
              @petro1head

              Yes waiting for the feed to stop before changing direction is what I do but sometimes forget.

              Just don’t want to have to walk back to the house to reset the mcb

              They are both type b, so the other alternative was to replace the house one with a type c?

              so which would be best, rapace house with type c or replace hut with 20/25a mcb?

              Edited By petro1head on 27/09/2018 09:12:34

              #373474
              Roger B
              Participant
                @rogerb61624

                You would need more details of the circuit before replacing a type B with type C. Possibly the house end mcb is at the low end of the specification tolerances. If they are both the same make you could swap them.

                #373479
                Brian Wood
                Participant
                  @brianwood45127

                  Petro1head,

                  The cheapest option is to employ a little discipline and pause between switching to reverse the feed; either that or get used to the trek back to the house!

                  Why not make a cover for the switch instead which you have to lift or move aside to delay the action enough to avoid the problem.

                  Regards

                  Brian

                  #373480
                  petro1head
                  Participant
                    @petro1head
                    Posted by Brian Wood on 27/09/2018 10:10:18:

                    Petro1head,

                    The cheapest option is to employ a little discipline and pause between switching to reverse the feed; either that or get used to the trek back to the house!

                    Why not make a cover for the switch instead which you have to lift or move aside to delay the action enough to avoid the problem.

                    Regards

                    Brian

                    Honest guv, I do, but on the odd occasion my exuberance gets the better of me …………………

                    #373481
                    V8Eng
                    Participant
                      @v8eng

                      Removed contents overtaken!

                      Edited By V8Eng on 27/09/2018 10:19:20

                      Edited By V8Eng on 27/09/2018 10:47:13

                      #373483
                      SillyOldDuffer
                      Moderator
                        @sillyoldduffer
                        Posted by Brian G on 27/09/2018 09:06:32:

                        That still doesn't solve the cause of the trips, which appears to be a momentary current of at least 90A. I wonder if you could prevent this by pausing before reversing, perhaps using a reversing starter with inbuilt delay?

                        Brian

                        Picking up on Brian's point, I think more information would help to pin down the cause. Is popping the MCB simply caused by a current spike due to abruptly reversing a motor or is something else wrong as well? We don't know.

                        No clue in the original post about the size of the mill – 500W or 5000W? How much power does the mill's main motor consume, and how powerful is the traversing motor? Is anything else connected to the same MCB?

                        One way of reducing the 'bang' on throwing a reversing switch is to use a three-way switch with a distinct detent in the central OFF position. Not only does the switch add more physical delay allowing motors to slow down, it reminds the operator not to push his luck when reversing! I've also seen circuits with a relay that broke the power entirely until a reset was pressed : you can do a lot of damage by reversing a machine without allowing it to stop first.

                        Another solution if you have a SWMBO handy. Tell her you need help breaking a bad habit. Every time you pop the MCB she gives you six of the best with a garden cane. It only works if you don't enjoy that kind of thing…

                        smiley

                        Dave

                        #373484
                        not done it yet
                        Participant
                          @notdoneityet

                          Following the motor instructions is, by far, the better (and most obvious) solution. Or common sense, if there are no instructional warnings.

                          You are at risk of damaging your motor by such tricks, so there is also a financial incentive to follow the sensible route and make sure the drive has stopped before reversing it. The power feed motor is not that powerful and taking most of that 32A will certainly not do it any good.

                          #373485
                          Brian Wood
                          Participant
                            @brianwood45127
                            Posted by petro1head on 27/09/2018 10:16:07:

                            Honest guv, I do, but on the odd occasion my exuberance gets the better of me …………………

                            Learn to control it , you will be doing the feed motor no good either by such practice and in the end it will cost you!

                            Brian

                            #373487
                            Martin Shaw 1
                            Participant
                              @martinshaw1

                              There is more to this than meets the eye and changing breakers willy nilly is not the solution. Reducing the size of the local MCB will not allow discrimination, that is a fault current that trips a say 20A MCB will likely enough also trip the 32A one in the house. Changing the from a type B to a type C is a possibility but there are additional factors that require determination before that can be done, loop impedance is critical, the size of the supply cable has a bearing as does it's length. Without that information it's impossible to make any sensible suggestion and if the OP can't work that out then an electrician is required.

                              Regards

                              Martin

                              #373488
                              Mark Rand
                              Participant
                                @markrand96270

                                Swap the house one for a D curve breaker and the problem should disappear. No building regs approval needed for this.

                                #373489
                                Martin 100
                                Participant
                                  @martin100

                                  The rating and type of the MCB's will, if the system has been properly designed , be correct to protect the cable (at the head end) and separately the installation at the hut end, with discrimination such that a 'local' fault stays just that.. To have MCB's identically sized is not ideal and may be totally incorrect, indicating that the installation was possibly just guesswork.

                                  If you are only using one bit of machinery at a time the 32A MCB in the hut could be sensibly replaced by one rated at 16A but that won't necessarily stop the tripping problem.

                                  A physical check of all connections (phase neutral and earth) from end to end plus checking earth integrity on the equipment is a good idea.

                                  MCB's can be supplied or even go trip happy so a direct 1:1 replacement of all the existing protective devices might possibly 'fix' the problem.

                                  Simply swapping the an MCB from a type B to a type C or even a type D without being fully aware of the implications of such a change is not a sensible idea. It might not provide enough discrimination which is what you are after and it could degrade the effective level of protection on the cable from the head end to the hut end.

                                  But as ever, without having sight of the installation, the earthing arrangements and measurements of the fault level most of this advice is just 'guessing'

                                  #373493
                                  Brian Wood
                                  Participant
                                    @brianwood45127

                                    I'm sorry gentlemen, but I have already solved the 'problem' without any of these erudite concerns and listed it earlier. I wasn't alone in giving the same advice either.

                                    All the OP has to do is take a pause and let the feed motor run down to stop,

                                    All these high powered observations are worth nothing against just a modicum of patience on his behalf which costs him nothing at all. Why oh why must such an issue escalate into such high powered and rather pointless discussion?

                                    Taking cover now

                                    Brian

                                    #373494
                                    petro1head
                                    Participant
                                      @petro1head

                                      Interesting.

                                      Out of interest the small hut consumer unit came fitted with the 32a mcb and it never got thought about, but I would agree it’s possible over rated. Considering the plugs are 13a, maybe, from a safety point of view, the mcb should in fact be 16a

                                      however Brian is indeed correct and best practice is patience and waiting for the motor to stop before reversing.

                                      #373495
                                      Muzzer
                                      Participant
                                        @muzzer

                                        In the UK we use ring mains and a lot of double sockets so the 32A MCB is normally what is required (see the building regs). No harm fitting a smaller MCB but surely that would be the opposite of an improvement.

                                        Murray

                                        #373499
                                        Martin 100
                                        Participant
                                          @martin100

                                          The MCB's , like fuses should always be rated to protect the cable. An appliance you plug into a '13A" socket will often as not have a flexible cable rated at lower than that, hence lower fusing in plugs such as 3A. Meanwhile in the rest of the world, with unfused plugs and radial circuits such devices are protected only by a 16A MCB and an RCD.

                                          If you have a ring main run in 2.5mm^2 Twin and earth or singles in conduit then 32A might be appropriate. For a radial circuit (i.e. one cable from the consumer unit to each socket in turn without another cable returning to the consumer unit) again using '13A' sockets or BS4343 'industrial' sockets 16A would often be more appropriate. A 16A MCB might indeed operate before a 32A MCB and a B rated breaker before a C rated breaker before a D rated breaker, but they are not strictly interchangeable and the type and level of fault could mean they all operate together, regardless of rating and trip curve within a few hundred milliseconds and thus provide no effective discrimination

                                          Downrating an MCB from 32A to 16A does not enhance 'personal' protection, the Residual Current Device and the earthing does that. Segregating the lighting and power to equipment is a good thing but a fault on the equipment could still plunge you into darkness, with resultant injury from trip hazards. Hence why RCBO's (a combined MCB and RCD) on each circuit are preferable, further enhanced with the lighting split across two circuits. Of course if you have windows on your workshop and only work in daylight this is not really an issue

                                          Yes you could let the feed stop before reversal but equipment shouldn't routinely trip protective devices regardless of what the user does so this discussion is IMHO far from being 'pointless' and a wrongly sized breaker can be a fire hazard, an incorrectly earthed installation in an outbuilding can be a shock hazard. Because it hasn't killed you in 30 years does not mean it won't kill you tomorrow

                                          #373501
                                          Anonymous
                                            Posted by Brian Wood on 27/09/2018 11:57:34:

                                            I'm sorry gentlemen, but I have already solved the 'problem' without any of these erudite concerns and listed it earlier.

                                            I'm afraid you've done nothing of the sort; you've just ignored the problem.

                                            Due to a damaged extension cable I recently had a phase to neutral short in the cable – a bright flash and a big bang. But it didn't trip the 16A breaker in the distribution panel. I regularly switch the motor on my repetition lathe from full speed forward to full speed reverse with no pause. That doesn't trip the breaker either. So why should a hobby power feed trip a bigger breaker? Something is wrong with the wiring installation or the power feed. If it isn't found and fixed it may well cause more serious problems at a later date.

                                            Andrew

                                            #373502
                                            Robert Atkinson 2
                                            Participant
                                              @robertatkinson2

                                              The primary purpose of an MCB (or fuse) is to protect the wiring so it should be rated to the wiring. A 32A MCB is only appropriate to a ring main wired with 2.5mm Twin and earth cable or a spur wired with heavier cable. So if the 32A MCB in the hut only has one 2.5mm wire connected to its output it's oversized. If this is the case change it to a 16A MCB MAXIMUM. The size of the one in the house depends on the cable feeding the hut. It should be the same or larger rating than the largest in the hut without exceeding the cable rating. I'd hope the hut is fed with 3 core 2.5mm Steel Wire Armoured (SWA) cable. if so a 32A breaker is OK. If it's just a length of 2.5 twin and earth you need to change the breaker to a 16A and think about a new feeder.

                                              You should really use a "C" rated MCB on a motor circuit but has been mentioned the earth impedance needs to be low enough to allow it to trip quickly in the case of a short circuit. This really needs a measurement.

                                              The other easy and safe fix is to fit a 16A "B" MCB in the house and a 10A "B" or 6A "C" MCB in the hut.

                                              Robert.

                                              #373505
                                              petro1head
                                              Participant
                                                @petro1head

                                                The cabling to the hut is proper 3 core 2.5mm steel wired armour cable like this **LINK**

                                                The garage/hut consumer unit is this one **LINK**

                                                The sockets are configured as a ring main

                                                This is the power feed I am using https://www.warco.co.uk/power-feeds/303231-wm18-milling-machine-power-feed.html

                                                Hope this helps

                                                Edited By petro1head on 27/09/2018 13:28:29

                                                #373511
                                                Swarf, Mostly!
                                                Participant
                                                  @swarfmostly

                                                  Slightly off-topic (but not too far, I hope) :

                                                  I read somewhere that the current rating of a twin 13 amp socket is 13 amps, TOTAL.

                                                  That is, if I'm drawing 10 amps from one socket, I mustn't draw more than 3 amps from the other one! And likewise for other share ratios.

                                                  Best regards,

                                                  Swarf, Mostly!

                                                  #373519
                                                  not done it yet
                                                  Participant
                                                    @notdoneityet

                                                    SM,

                                                    The power rating should reflect the supply. A single 13A outlet (only) should be connected to a 2.5mm^2 spur. Twin 13A sockets are only permissible on a 2.5mm^2 ring main (ie a 30 amp total). One should not be able to overload the supply if that line is not fused seperately.

                                                    #373526
                                                    Martin 100
                                                    Participant
                                                      @martin100

                                                      Legally it's 13A total regardless of whether the socket is one way or two way. Three way sockets are also available but are sub fused at 13A in the faceplate.

                                                      The BS approval test on a double is 20A (with a 70/30 split) with a limit of 1 deg C rise

                                                      BS1363 sockets from reputable manufacturers will actually accommodate 3 x 2.5mm^2 or 3 x 4mm^2 or 2 x 6mm^2 conductors.

                                                      Petrolhead that cable isn't Steel Wire Armoured, this is SWA

                                                      We might possibly be into can of worms territory here…

                                                      For anyone seeking guidance here is a good place to start (although getting a bit dated now)

                                                      Electrical Installations – a supply to a detached outbuilding

                                                    Viewing 25 posts - 1 through 25 (of 46 total)
                                                    • Please log in to reply to this topic. Registering is free and easy using the links on the menu at the top of this page.

                                                    Advert

                                                    Latest Replies

                                                    Home Forums General Questions Topics

                                                    Viewing 25 topics - 1 through 25 (of 25 total)
                                                    Viewing 25 topics - 1 through 25 (of 25 total)

                                                    View full reply list.

                                                    Advert

                                                    Newsletter Sign-up