  • #228425
    Roland Mann
    Participant
      @rolandmann14066

      I have recently bought a Schneider Altivar 61 on ebay, from a dealer 'Drives Direct'. It was advertised as being able to power a 3/4hp motor, single to three phase.

      When it arrived I downloaded the instructions, which showed that the inverter was rated at 0.5hp with a single phase input. The higher power rating was for a 3 phase 240v input.

      I questioned this, and was told that this drive had been 'uprated'. Having spoken to Schneider technical support they told me this was not possible.

      This I reported back to the seller, who informed me (after some hassle, I must say) that he had reprogrammed the trip rating from half to 3/4hp, and this was a 'trade secret'.

      The seller has attempted to cancel the transaction and refund my money, but I am concerned to know whether this practice is common and/or safe.

      In the listing the item was described as new, and no mention was made of reprogramming it. He claims to have sold more than 60 of these to satisfied customers.

      The datasheet for the exact model is here: http://www.datasheetlib.com/datasheet/778647/atv61h075m3_square-d.html

      Any thoughts?

      Advert
      #24418
      Roland Mann
      Participant
        @rolandmann14066
        #228732
        jason udall
        Participant
          @jasonudall57142

          A couple of points.
          Single phase has a rms ( basically a measure of the work the inverter/motor can do) of 230-240 volts

          A three phase input inverter for reasons beyond this post has an equivalent voltage that is larger..( phase to phase not phase to neutral)
          So imagin the motor is expecting this larger voltage.phase-phase voltage..well clearly you get less out of the motor.

          Now there are ways round this.
          Manufacturers build in whats called a buck converter/booster.
          Or “after market”
          1) modify reported power…look this knob goes up to 11…having no effect on motor power

          2) modify current limits..which allows a say 2 hp motor to be used on say a 1.5 hp inverter to deliver the reduced (from 2 to 1.5) capacity ..

          You must judge what is being done in your case

          #228734
          MW
          Participant
            @mw27036

            If hes changed the rated output from what you believed the original product should normally produce, then its miss-selling you, I'd get your money back and stay clear. Its not right for the customer, thanks for the heads up though.

            Ps. This is a big no-no because when you buy a motor for use with an inverter, it's best to get an inverter that can handle 25%-50% more than your motors rated output so that it will operate well under sustained duty cycles. It will just keep overheating after more than maybe 30-40minutes usage. 

            Michael W

            Edited By Michael Walters on 07/03/2016 10:09:26

            #228740
            Martin Connelly
            Participant
              @martinconnelly55370

              The dealer has probably got away with this because most motors do not run at full rated power all the time. Who, for example, has a lathe cutting at maximum metal removal rate 24 hours a day? I agree with Michael W. Always get a bigger inverter than the motor requires, it may be re-purposed or the motor replaced with a larger one.

              Martin

              #228741
              Martin 100
              Participant
                @martin100

                There is also the possibility that the hardware could be totally identical to one with a larger output capability, but knobbled to a lower level by the firmware. It's often far easier to run one larger volume production line with the exact same bill of materials and just apply a different label and level of firmware before it exits the factory gates. Such an approach has become quite common in recent years with test equipment such as oscilloscopes.

                #228742
                Ajohnw
                Participant
                  @ajohnw51620

                  Inverters I have bought have an overload capability well over their rated power. Sounds he has used some or all of that up. Not a good idea. As some one has suggested the rather large high quality and expensive capacitor these things use will be over rated.

                  Tell him to get ********* and send it back. If it was ebay it deserves a negative and why in the feedback. I had some dealings with who I think now is drivesdirect when he started up. I was impressed. He was helpful and thoughtful about what he sold. I contacted him later for a new manual – he wanted a silly amount of money for what he could just leave for downloading on the web.

                  There is a person on homeworkshop.org who regularly sells inverters and seems to have many happy customers. He's in Worcester. It might be worth contacting him.

                  Sounds like when people buy inverters now they had better check that the specs tie in with the seller's.

                  John

                  #228743
                  Roland Mann
                  Participant
                    @rolandmann14066

                    Thanks very much guys for the opinions. My initial reaction was that I was being conned, but being unwilling to jump to conclusions I kept asking for more information about this 'uprating', and why it was not revealed in the listing. The thing I find interesting here is that this a not apparently a bunch of cowboys. He says:

                    <We have 30 years expertise in inverters from 0.1HP up to 1 Megawatt and not only do we sell these but we service and repair the whole range down to component level and we are Teco's UK service agents, we get asked by Teco and other inverter suppliers to give advanced technical support so when we supply an item we know what we are doing…>

                    In one of the latest messages (after I said I had spoken to Schneider's technical department) he says:

                    "These people at technical departments you seem to think know everything have to deal with a vast range of products and the knowledge of any specific range is limited and they can then only go by the information they had and in 99% of cases thats the manual you have, and reading that it says nothing about upgrading etc,
                    The makers want you to by an expensive new model at £250 so they will tell you it can not be upgraded and if you want to do that then thats fine,

                    Only the factory design engineers who like us understand every working area of the unit and also know the software inside out would know how to upgrade products BUT they would not tell you and likewise we would not tell you how its done but its out there in the market on all sorts of products, for example i drive an Audi Q7 and by going into the ECU, the computer that runs the engine i have reprogrammed it to give me an extra 100HP of power, the makers will not tell you that can be done and the technical department will tell you its not possible, we have here a range of IMO inverters, the i-drive 1.5KW unit is designed to run motors up to 2HP, you call IMO and tell them you want it to drive your 3HP motor and they will tell you to purchase a more powerful unit BUT send that same 2HP unit to us and in 5 mins it will be a 3HP unit !"

                    I am at a loss to understand why a company which has apparently a considerable business and track record should be doing this. It is extremely odd.

                    Roland

                    #228746
                    Roland Mann
                    Participant
                      @rolandmann14066
                      Posted by Martin 100 on 07/03/2016 10:21:44:

                      There is also the possibility that the hardware could be totally identical to one with a larger output capability, but knobbled to a lower level by the firmware. It's often far easier to run one larger volume production line with the exact same bill of materials and just apply a different label and level of firmware before it exits the factory gates. Such an approach has become quite common in recent years with test equipment such as oscilloscopes.

                      That, it seems, is what the dealer is suggesting.

                      #228748
                      John Stevenson 1
                      Participant
                        @johnstevenson1
                        Posted by Roland Mann on 07/03/2016 10:32:36:

                        He says:

                        for example i drive an Audi Q7 and by going into the ECU, the computer that runs the engine i have reprogrammed it to give me an extra 100HP of power, the makers will not tell you that can be done and the technical department will tell you its not possible,

                        Roland

                        .

                        .

                        Drives an Audi: Says it all…………………………….

                        #228750
                        Ajohnw
                        Participant
                          @ajohnw51620

                          Some one who hasn't been involved in electronic just wouldn't understand why electronic components can appear to be well under rated. What he is basically doing is taking something that has been designed for continuous industrial use and removing some or all of the allowances that have been made for parts variations. Electronics bits and pieces vary even the same part numbers from the same manufacturer. In practice due to supply companies who build may at times buy the same part from more than one manufacturer and there will be variations. Industrial items like inverters will have been designed around worst case figures.

                          Industrial ratings of components are also often different. Taking a simple item there was a lot of 1/2 w resisters that couldn't be used for the product at work so we could help ourselves. Later I bought some 1/2w resistors and was gob smacked by how hot they got. In my terms these 1/2w resistors were barely 1/4w. T ransformers are another area where this happens, the max current rating of many is a joke. Active components for commercial use are often rated at 0 to 70C. Automotive -40 to +85C, military even more than that. Some people are inclined to think the only difference is the labelling. If only.

                          John

                          #228751
                          mark smith 20
                          Participant
                            @marksmith20

                            I bought a 3HP IMO Jaguar inverter to drive a bandsaw , off him on ebay several years ago, it worked for a few days then went dead. I got no refund despite sending the item back .I wouldnt deal with him at all because if anything goes wrong he doesn`t really want to know .Thats my experience .

                            I got the impression that if you were only a private buyer and not spending thousands then you weren`t worth helping with the problem.

                            Edited By mark smith 20 on 07/03/2016 11:06:55

                            #228760
                            Michael Briggs
                            Participant
                              @michaelbriggs82422

                              Hello All,

                              I have worked with inverters since they first appeared on the market, that probably encompasses a few thousand of them. The seller is wrong and should be avoided, you can run a motor with a slightly under rated inverter if it is lightly loaded but it is not good practice.

                              On the other hand I don't agree with comment from Michael Walters, the only time an inverter needs to be over rated is when it is used with equipment that requires a very high starting torque such as a mixing machine that has stopped mid cycle.

                              In my workshop I have a lathe, miller and bench drill, all inverter powered. They all generally start under no load so there is no need to de rate the drive, don't waste your money.

                              Michael

                              #228767
                              MW
                              Participant
                                @mw27036

                                I think it's interesting, because i've run a 750 watt motor on a 750watt inverter on a lathe into a long piece of 1" square mild steel on a 1mm cut, on the leadscrew auto feed gear train and a tailstock centre and through coolant running, got about half way through it and the overload warning comes on. I've done the same thing with a 1.5kw inverter, motor no different and it doesnt complain. So duty cycle can be important.

                                 

                                Obviously i'm not the judge of what other people need to do, but i needed this to do that, so all i can say is buyer beware. I should add that i think my named counterpart has some good points, its true that it doesnt start under load and this new inverter was fan cooled rather than totally enclosed, so i could be wrong but it worked anyway.

                                Michael W

                                Edited By Michael Walters on 07/03/2016 12:40:22

                                #228768
                                Michael Briggs
                                Participant
                                  @michaelbriggs82422

                                  My comment regarding under rating inverters should have included applications where there are very high torque requirements at times during the machine cycle.

                                  Michael

                                  #228770
                                  Michael Briggs
                                  Participant
                                    @michaelbriggs82422

                                    Hello Michael,

                                    Inverters should be able to run at 100% load 24/7. I would check the motor current, either you had a faulty inverter or you are overloading your motor, the latter will end in tears.

                                    Michael

                                    #228777
                                    Ajohnw
                                    Participant
                                      @ajohnw51620
                                      Posted by Michael Walters on 07/03/2016 12:34:36:

                                      I think it's interesting, because i've run a 750 watt motor on a 750watt inverter on a lathe into a long piece of 1" square mild steel on a 1mm cut, on the leadscrew auto feed gear train and a tailstock centre and through coolant running, got about half way through it and the overload warning comes on. I've done the same thing with a 1.5kw inverter, motor no different and it doesnt complain. So duty cycle can be important.

                                      Obviously i'm not the judge of what other people need to do, but i needed this to do that, so all i can say is buyer beware. I should add that i think my named counterpart has some good points, its true that it doesnt start under load and this new inverter was fan cooled rather than totally enclosed, so i could be wrong but it worked anyway.

                                      Michael W

                                      Edited By Michael Walters on 07/03/2016 12:40:22

                                      The first thing people should do with an inverter is enter the values on the motor plate into the firmware so in some ways the inverter rating doesn't matter other than some may only allow some minimum current to be entered. In other words it might not be possible to enter the correct values for a 1hp motor in a 2hp inverter.

                                      On the inverter on my lathe overloads are handled in 2 ways. From memory the inverter itself is happy with a 50% overload but also models the thermal behaviour of the motor – that is a facility that has to be enabled. The 50% is built in and may have some limits applied. I was more worried about my motor burning out rather than the capabilities of the inverter. Again from memory the inverter will allow it's power rating to be dropped via setting by 1/4hp but no more. No idea why but it could be down to emissions.

                                      I don't know what lathe or tooling or speed you are using Michael but my Taig / Peatol would take that cut – if it was square bar though it would shake it about a bit.

                                      John

                                      #228779
                                      jaCK Hobson
                                      Participant
                                        @jackhobson50760

                                        I had good experience with Drives Direct, but probably 5 or more years ago. They have certainly been going a long time and have certainly sold a lot of inverters.

                                        However, now, if I need an inverter, I take a risk on a second hand one from ebay. So far I'm up on the deal.

                                        #228780
                                        MW
                                        Participant
                                          @mw27036

                                          Maybe i've been a bit daft or something because i dont remember needing to enter current rating into my inverter, it only stipulates the frequency. I'm using an IMO idrive2 so maybe i've gotta flick back through that cryptic manual and see if i missed a setup step quite important and just willfully overlooked. perhaps i'm not getting what i should out of it because of my operational error.

                                          Michael W

                                          #228782
                                          Neil Wyatt
                                          Moderator
                                            @neilwyatt

                                            The IMO Jaguars can be uprated by 135% with F11.

                                            Neil

                                            #228785
                                            AlanW
                                            Participant
                                              @alanw96569

                                              Hacking equipment to operate outside of the design parameters will more than likely invalidate the 'CE' marking.

                                              Simplistically, for EMC (electro magnetic compatibility) emissions tests, equipment is (or should, if done correctly) be tested in a worst-case condition which usually coincides with maximum supply current being drawn. I have no experience of testing inverters but, in my opinion, pushing them to operate beyond their design parameters will likely result in conducted and/or radiated emissions limits being exceeded.

                                              Alan

                                              #228788
                                              Martin 100
                                              Participant
                                                @martin100
                                                Posted by Michael Walters on 07/03/2016 14:05:21:

                                                Maybe i've been a bit daft or something because i dont remember needing to enter current rating into my inverter, it only stipulates the frequency. I'm using an IMO idrive2 so maybe i've gotta flick back through that cryptic manual and see if i missed a setup step quite important and just willfully overlooked. perhaps i'm not getting what i should out of it because of my operational error

                                                It may vary (I've personally not used IMO drives) but OMRON inverters drives for example have a parameter n036, Motor Rated Current, 0.0 to 999.9 "Set to the rated current from the nameplate." which in conjunction with parameter n037 and n038 is used for motor thermal overload protection.

                                                Users Manual Here
                                                **LINK**

                                                #228793
                                                MW
                                                Participant
                                                  @mw27036

                                                  Just an update,

                                                  I just entered the current, voltage and wattage (oddly stated as 0000.0kw?) as well as RPM of the motor into my inverter. Interpreted from the plate as the 230v delta configuration.

                                                  The settings were only a little off but it seems to run slightly smoother, doesnt whine as much as it used to on low frequencies.

                                                  And so i didnt intend to, but i've learned my lesson today.

                                                  It's like trying to read aramaic in my manual. It isn't sign posted very well.

                                                  Ajohn, I took a look at the peatol machine and laughed when i saw it, reminds me of the sherline lathe i have (but dont use) and that couldnt take a cut out of anything remotely hard blush. Its a clarke cl430; brute of a thing. If what you say is true then mines a wimp.

                                                  Michael W

                                                  Edited By Michael Walters on 07/03/2016 15:26:15

                                                  #228796
                                                  Roland Mann
                                                  Participant
                                                    @rolandmann14066

                                                    Thanks again for all the opinions. Very interesting.

                                                    I'm new to this forum, so I'd like to say I'm impressed by the fantastic range of expertise here!

                                                    Roland

                                                    #228815
                                                    mark costello 1
                                                    Participant
                                                      @markcostello1

                                                      You ain't seen nothing yet!

                                                    Viewing 25 posts - 1 through 25 (of 48 total)
                                                    • Please log in to reply to this topic. Registering is free and easy using the links on the menu at the top of this page.