      Hello I'm looking for guidance on wiring e.stops in to a new electrical, circuit. I have a inkling but just wanted reassurance or putting right.

      I've got a kjd17 5 pin with a link on one of the terminals to the 5th pin. Supply in and supply out I get but where the separate link goes from the negative to A1, is this where I run E.Stops from taking the link of and running through every E.Stop and back to the terminal.?

      I'm wondering why it's the negative wire I would of thought it would be the live, but I suppose the negative is just the return of live

      #32021
      Grant Allen 1
      Participant
        @grantallen1
        #408371
        Andy Carruthers
        Participant
          @andycarruthers33275

          Hi Grant

          Assuming you have fed live through the NC connections of an emergency stop switch (if fitted)

          A1 is the "hold on" supply for the No Volt Release

          Feed live to pin 23 – when Green button is pressed, without live to A1 the live supply will drop out as soon as the Green button is released

          Link pin 24 to A1 taking live to your motor, if mains drops out, the "hold on" drops out rendering the circuit safe

          #408373
          Bikepete
          Participant
            @bikepete

            *deleted"

            Edited By Bikepete on 09/05/2019 10:46:50

            #408375
            Grant Allen 1
            Participant
              @grantallen1

              So which terminals are live and neutral, this basic wiring is suggesting 13 and 24 are live, and 23 and 24 with a1 coming from the neutral out to the motor is this correct?

              With relation to link wire is it this that runs from 24 through each stop button and back to A1 so if the circuit is pressed it cuts at any of the stops ?

              #408381
              Andy Carruthers
              Participant
                @andycarruthers33275

                neutral side.jpgemergency stop.jpglive side.jpg

                #408396
                john swift 1
                Participant
                  @johnswift1

                  KJD17 E-stop wiring diagram

                  kjd17  e-stop wiring.jpg

                  #408402
                  Grant Allen 1
                  Participant
                    @grantallen1

                    So I think I got this now,

                    power IN neutral to 13

                    Power IN live to 1st E.stop through and onto next E.stop through and back to 23

                    Power to motor live 24

                    Power to motor neut 14

                    And leave the link in place from A1 to 24

                    #408406
                    Robert Atkinson 2
                    Participant
                      @robertatkinson2
                      Posted by Grant Allen 1 on 09/05/2019 12:13:38:

                      So I think I got this now,

                      power IN neutral to 13

                      Power IN live to 1st E.stop through and onto next E.stop through and back to 23

                      Power to motor live 24

                      Power to motor neut 14

                      And leave the link in place from A1 to 24

                      Not quite.

                      This would run power through all the e-stops. A combination of your scheme and Johns is the best compromise. If you have a E-stop right next to the KDJ 17 wire it in series with the input as you describe. Then wire any additional E-stops between A1 and 24 as John's diagram shows. It's a debatable point but I would swap the live and neutral on Johns diagram so you don't have 240V live with a high current fuse running to all the e-stops.

                      The problem with Johns circuit is that it relies on the KDJ 17 working properly. If the closest E-stop is wired in series with the supply then if you press the normal stop and it doesn't work you will naturally hit the nearest E-stop which will. The remote E-stops still rely on the KDJ 17 but you generally won't be using them because the normal stop was broken.

                      Robert G8RPI.

                      #408409
                      Andy Carruthers
                      Participant
                        @andycarruthers33275

                        Robert is right

                        You want to protect the KDJ17 switch by putting the E Stop Switch first, this is shown in the middle of the three pictures, live feed to the left, live output to KDJ17 in bottom picture

                        Hitting E Stop Switch must prevent all live feed to downstream circuitry

                        #408410
                        Grant Allen 1
                        Participant
                          @grantallen1

                          So…

                          Live in to e.stop next to kjd17 then to 13

                          Neut in to 23

                          Neut out 24

                          Live out 14

                          Extra stop 4ft away neut 24 link through e.stop back to A1 link.

                          #408418
                          Andy Carruthers
                          Participant
                            @andycarruthers33275

                            wiring diagram.jpg

                            Assumes terminal post numbers are correct from the above information

                            The "hold on" relay is internally wired to Neutral, just needs a Live supply to A1

                            Edited By Andy Carruthers on 09/05/2019 13:34:36

                            Edited By Andy Carruthers on 09/05/2019 13:40:46

                            #408420
                            Grant Allen 1
                            Participant
                              @grantallen1

                              Doesnt that diagram put the live on the wrong side ?

                              #408422
                              Andy Carruthers
                              Participant
                                @andycarruthers33275

                                The diagram reflects the wiring in the photos and correctly represents how the Emergency Stop Switch protects the KJD 17 and Load

                                Please PM if you think there is an issue, always willing to be educated

                                #408425
                                Grant Allen 1
                                Participant
                                  @grantallen1

                                  Following diagram which has been drawn. Any additional stops replace the small ink wire from 24 to A1 yes

                                  #408431
                                  Andy Carruthers
                                  Participant
                                    @andycarruthers33275

                                    I have read your latest comment several times and am struggling to grasp what you mean

                                    If you wire your switches as per photos and wiring schematic your wiring will be functionally correct and provide the best protection

                                    #408434
                                    Mike Poole
                                    Participant
                                      @mikepoole82104

                                      The estops should switch the coil of the NVR not the full load current of the motor.

                                      Mike

                                      #408438
                                      Grant Allen 1
                                      Participant
                                        @grantallen1
                                        Posted by Andy Carruthers on 09/05/2019 14:41:59:

                                        I have read your latest comment several times and am struggling to grasp what you mean

                                        If you wire your switches as per photos and wiring schematic your wiring will be functionally correct and provide the best protection

                                        I've wired it up to the diagram provided. The only thing I was trying to say was the extra e.stop that's 4ft away simply replaces the link wire then when pressed it would break the current, or have I got that wrong.

                                        In relation to Mike's comment that's gone straight over my head. Please elaborate

                                        #408440
                                        Mike Poole
                                        Participant
                                          @mikepoole82104

                                          In john swift 1s schematic diagram the coil of the NVR is controlled through the estops button and the motor load is switched by the contacts of the NVR. The NVR contacts will be designed to reliably make and break the load current. An estop button is designed to switch the current of a control circuit and is unlikely to break the full current of the motor without being damaged. The coil of the NVR is a very small load and will not damage the contacts of an estop type button. Andys suggestion will put the full load of the motor through the estop contacts which could damage the contacts when operated.

                                          Mike

                                          #408443
                                          Andy Carruthers
                                          Participant
                                            @andycarruthers33275

                                            Mike – You are right – on reflection, the E Stop Switch current rating is 12A @250V so unlikely to be damaged with the loads I have

                                            #408445
                                            Grant Allen 1
                                            Participant
                                              @grantallen1

                                              Wired up with the e.stop in same box, reading the latest I'm running a .37kw motor so di I need to be concerned ?

                                              I now need to know how to wire up an additional e.stop, going of Robert's advice would I replace the link wire with an e.stp?

                                              #408451
                                              DMB
                                              Participant
                                                @dmb

                                                Mike,

                                                I asked the forum for advice on the above, some months ago. One reply gave me Axminsters wiring which did not work. I did not buy mine from Axminster, got it from Hong Kong, identical appearance and eve same part no. Another reply gave me a different circuit which did work and has done ever since. Description follows.

                                                Mains Live in to terminal 1 on emergency button. Live out terminal 2 from button to terminal 13 on stop /start. Live out terminal 14 to motor.

                                                Mains Neutral in to start/ stop terminal23. Terminal 24 out to motor.

                                                Whilst it works, have I got it wired correctly?

                                                John

                                                #408517
                                                john swift 1
                                                Participant
                                                  @johnswift1

                                                  The reason I connected the switched live via the E-stop switch to A1 is

                                                  An accidental short between A1 and neutral or earth will blow the mains fuse

                                                  If you had live to terminal 13 and neutral to terminal 23

                                                  an accidental short between A1 and neutral or earth would energise the coil when the E-stop switch is open

                                                  assuming the mains supply is not protected by a residual current circuit breaker

                                                  kjd17  e-stop wiring.jpg

                                                  john

                                                  #408525
                                                  Nicholas Farr
                                                  Participant
                                                    @nicholasfarr14254

                                                    Hi, I agree with John Swift1 diagram. The E-stops should only control the coil of the KJD17 and if you want more than one E-stop, then they should all be connected in series with the one shown. Protection of the KJD17 should be via a fuse or circuit breaker which feeds the supply to it, as suggested and non of the load current should go through the E-stops as Mike Poole said. One advantage of this is that the only way the motor will start is by pressing the start button and unless the KJD17 is or has been seriously overloaded, it is unlikely to fail and so if you get a power cut during use, every thing after the KJD17 will be in a safe mode when power is restored.

                                                    Regards Nick.

                                                    Edited By Nicholas Farr on 10/05/2019 07:17:57

                                                    #408527
                                                    Robert Atkinson 2
                                                    Participant
                                                      @robertatkinson2
                                                      Posted by Mike Poole on 09/05/2019 15:52:39:

                                                      In john swift 1s schematic diagram the coil of the NVR is controlled through the estops button and the motor load is switched by the contacts of the NVR. The NVR contacts will be designed to reliably make and break the load current. An estop button is designed to switch the current of a control circuit and is unlikely to break the full current of the motor without being damaged. The coil of the NVR is a very small load and will not damage the contacts of an estop type button. Andys suggestion will put the full load of the motor through the estop contacts which could damage the contacts when operated.

                                                      Mike

                                                      This is not strictly correct. For the sort of loads we are talking about here a decent E-Stop switch can handle the full load and still stop the motor if the no-volt release fails. 16A rated 2 pole E-stop switches are readily available. This primary E-stop is close to the NVR. Additional, remote E-stop switches can be wired in series with the NVR coil. The switch side of the coils should be in the neutral side so the wiring is not connected to a high current live. A short to ground will disable the remote e-stop (test them once a month if you are worried) but will not cause a fire as a live feed might. If you do put the remote switch connection of the holding coil in the live a fuse should be fitted at the source end. There is no advantage in fitting the E-stop local to the NVR in the holding coil circuit rather than the power. The suggested dual power and holding coil wiring costs no more and gives redundancy. Personally I would not trust a cheap Chinese NVR as my final safety device.

                                                      I have designed E-stop, guarding and interlock systems for robotic machines to meet European and North American safety standards so do know a bit about this.