Posted by Phil Whitley on 22/04/2019 17:51:12:
In the interests of electrical correctness, ther are one or two things in daves post I must take issue with, because we are all here to learn, everyday is a school day, and safety matters in electrical installations.
The point you make about the plug fuses being there to protect the wiring and not the appliance is partly semantic, and electrically incorrect! The fuse or MCB which protects the ring (or radial) is the coarse protection, the fuse in the plug is the fine or selective protection, and although no fuse will protect against electrocution, it is there to isolate the appliance in the event of a fault, thus stopping the risk of a localised fire at the appliance by isolating it from the ring. Take the instance where a double insulated vacuum develops a fault and begins to draw excessive current. There will be no tripping of the RCD, because the current in live and neutral are the same, and let us assume that the fuse in the Vacuums plug is 13A, with a fusing factor of about 1.2 for a cartridge fuse. When the current rises to 15.6 amps, the plug fuse will rupture, and disconnection will occur. Now let us look at the same situation from the point of view of the ring main, it only sees a current flow of 15.6 amps, but if additional load on the ring takes the total load on the ring to more than its protection (fuse or MCB) then the whole ring will be dissconnected, before the cables in the ring even get warm. there is no situation in an otherwise correctly wired installation where the ring will overload to the point of ignition. Also note in the above example a vac should be fused between 5 and 10 amps! I do know however, and have read in publications which should know better, that "the plug fuse is not there to protect the appliance" and semantically, it is not, it is there to prevent temperature rise in the appliance getting to ignition level, it is there for safety, but it does NOT protect the ring main from overload, that is what the fuse or MCB in the consumer unit does.
You could argue that the ring main is even more suited to todays low current applications, but please note that the immersion heater should NEVER be put on a ring main!
Now to my main point, as I mentioned above, fusing factor! I am now retired from the electrical industry, but I have installed many consumer units and distribution boards that use MCB and RCD protection, all done without going too deeply in to the technical side of MCBs. Indeed I have just completed the installation of the 3 phase and single phase distribution boards in my own workshop.In the older Wylex and similar rewirable fuse consumer units the fuse has a "fusing factor" which is given as a figure used to calculate at what current the fuse will actually rupture and isolate the circuit. For rewirable fuses, it was originally set at 1.5, IE a 10A fuse would blow at 15amps, and we did experiments in the college lab to prove this was the case. Since my original training, that figure has been increased to 1.8, and even 2 in some cases, won't go into it here as I am already long winded
but looking at the actuall tripping currents for MCBs, which I had assumed would be much closer to the rated current and thus provide "better" protection I find to my surprise that the following applies.
Type B 3 to 5 times rated current.
Type C 5 to 10 times rated current
Type D 10 to 20 times rated current
Type K 8 to 12 times rated current
Type Z 2 to 3 times rated current
As you can see this means that a rewirable fuse is far safer than an MCB, in that it will isolate a circuit reliably at a lower current, and when you add to this the fact that an MCB DOES NOT FAIL SAFE, you can understand that the new (new new corrected reprint) book of latest regulationd now requires all consumer units to be metal clad and installed in such a manner that an internal fire cannot escape the enclosure. I am really glad to be out of an industry where good engineering has been thrown to the wind, and regulations, which used to be made by senior engineers, are made by wet nosed uni graduates and electrical equipment manufacturers. rant over!
Apologies for the long quote but the whole context needs quoting and preserving.
'electrical correctness' is not a word I would use to describe significant parts of what is said above.
Holding the view that rewireable fuses are 'safer' is staggering, they are by nature always slower in operation, they are prone to abuse, unreliability and early failure
The 3 to 5 times rated current for a type B MCB, and similarly for the other types is for a fault clearance time of 0.1 seconds. At around 2 x their rated current they will trip in around 2 minutes
A BS1362 plug top cartridge fuse rated at 13A requires around 150A to clear a fault in 0.1 seconds
Rewireable fuses are long since deprecated. Cartridge fuses or MCB's are the norm worldwide because they are good sound reliable and dependable engineering practice.