Some where in my memory bank is pressure testing the air cooling systems of high power radio and radar transmitter output valves such as the VT 98, I'm not sure how this was done, my information source(Dad) is nearly 40 years gone.
Ian S C
That's right. It's easier to measure air-pressure than air-flow in these systems, so air flow was inferred from the pressure drop between the input and output.
To measure air-flow through the valve, the effective output is inside the cabinet, not atmospheric. The pressure difference equivalent to the required flow would be established by the designer, and maintenance guys would periodically check that the cooling system was operating at that pressure without having to power down the transmitter. Partial blockage of the input filters, or fluff building up in the outlet or the valve's base or cooling fins all show up as off-specification pressures that would require a power-off clean-up.
A manometer is a cheap and way of occasionally measuring pressure differentials; the alternative is to fit a pair of permanent Bourden gauges.