A general query about welders/transformers and MCBs in the workshop.
I have a stick welder which trips the MCB when powered up, I think due to the quick saturation/inrush current.
The Backstory
When we moved over to Buxton, I had a new garage/workshop built, with single phase supply fed off the house dis board via a suitable armoured cable. (Can't remember now, I think 10mm².) My builder is also a qualified sparky, and all wiring is correctly tested, recorded, and registered.
The house end of the cable is terminated in a C40 breaker in a spare non-ELCB position on the normal domestic board.
It terminates at the garage end on a new 12 way dis board with ELCB protection supplied at this end, so I don't trip anything in the house.
Amongst the facilities in there, I have a dedicated 16A socket to run a 110v transformer. Originally I bought an ex -WD 1.5 KW torroidal one, but the fast saturation was enough to trip a D16 breaker, I didn't want to go to anything higher as I don't want to trip the breaker in the house board.
I duly replaced it with a 2KW conventional transformer running off a C16 and all now OK with that side of things. The chap I bought the torroidal one off demonstrated it at his house; it ran fine off his D16, but it was much further away and a far older install. My cable runs are quite short and have good low impedance(s) all round.
I later picked up an older oil cooled stick welder, with the intention of running that off another dedicated 16Amp socket. The (different) seller ran it off an MCB, rather than a fuse, again I believe a D16, but said that he just needed to power it up initially at one end of the current adjustment, and then after the transformer had saturated, he could weld at all of the available ranges without a problem. He ran it in his other workshop via a fused outlet.
Unfortunately, at my workshop it trips a D16 breaker on power up. I'm again wary of going too high, as I don't want to risk tripping the C40 at the house end.
The 16Amp sockets are each fed with 2.5mm² twin and earth, radially to dedicated MCBs, so the cable should be good for 20A
I guess I could try a C20; I'm the only user working in there at the time, so wouldn't actually be welding simultaneously whilst running a 110v grinder etc.
I'm aware I'd have to consider the 3HP compressor kicking in whilst I'm welding.
I'm confident that the welder isn't actually faulty, as I've had a play with a megger, so I think it's purely a speed of saturation problem, with a large inrush current causing the tripping; I suspect it would be fine running off proper old fashioned 16A fuse wire.
I have a smaller 140A SIP stick welder, and a 140A Cebora MIG which work fine in the same workshop off a conventional 13A ring main fed from a B20
Does anyone have any useful suggestions please?
I know we have folks on here who actually do/did workshop/industrial electrics for a living, so experience is better than me studying the trip curves of various MCBs.
I also appreciate that it's not good for the MCBs to keep tripping them, so I've limited my experiments thus far.
I know you can get a slow starter for electric motors, but for welders???
Cheers Bill