"Electrical correctness' is not a word I would use to describe significant parts of what is said above."
Holding the view that rewireable fuses are 'safer' is staggering, they are by nature always slower in operation, they are prone to abuse, unreliability and early failure.
Staggering eh? do you have any evidence for this, I did mention they are prone to abuse, and you certainly cant fight stupid, but the vast majority of the British housing stock that was wired or rewired between the late fifties to the eighties still has rewirable fuses, and is very unlikely to be upgraded unless extended. Since these rewires were done, the number of electrical housefires fell dramatically (Rospa figures)
The 3 to 5 times rated current for a type B MCB, and similarly for the other types is for a fault clearance time of 0.1 seconds. At around 2 x their rated current they will trip in around 2 minutes
Interesting, so why are they catching fire? Could it be because of the vast numbers of chinese made mcbs on the market?. the introduction of fully metalclad CU's and fire sealed cable entries means that already, there are serious problems. Incidentally 2x the rated current for a 2 minute trip is longer than a rewirable, even at 1.8 fusing factor!
A BS1362 plug top cartridge fuse rated at 13A requires around 150A to clear a fault in 0.1 seconds
It may require that to clear in 0.1 seconds, but requires much less than that to clear in 1 second. I have tested this at college many years ago under lab conditions. The IEE set the fusing factor for an HRC cartridge fuse at 1.2 times the rated current, are you saying they were wrong?
Rewireable fuses are long since deprecated. Cartridge fuses or MCB's are the norm worldwide because they are good sound reliable and dependable engineering practice.
Explain this "deprecation", lets hear some thoughful logical reasoning if you are going to comment at all. Is it "sound reliable and dependable engineering practice" to fit a device as sole means of overcurrent protection that has no failsafe capability and can, and does stay in the on position in the event of an internal failure, and will carry current till it literally catches fire because the next line of protection is the 100 amp service fuse, which (according to your calculations)will need 1153amps to blow in 0.1 seconds, here is the clear illustration of the reason for the introduction of the Metalclad CU. IEE regs used to state that "No mechanical device or circuit breaker shall be fitted in any final sub circuit as the SOLE means of protection" In other word, use an MCB or other circuit breaker by all means, as long as it is backed up by a similarly rated fuse, ok use a cartridge fuse if you must, but electrically they are only a little better than a rewirable, although harder to fit the wrong size. To say they are "the norm worldwide" is just silly, they may be the norm worldwide IN NEW INSTALLATIONS, but that is all. The UK has the safest and most modern system in the world, and we still have a majority of "legacy" installations. I have shown that MCB's, under certain circumstances, are much less safe than fuses, and the IET regulations upgrade to metalclad (which used to be common anyway in large domestic commercial and industrial installations) and their introduction of Potential fault current calculations shows that they are literally firefighting the problem!
I stand by what I said, which is based on 50 years of practical experience of a wide range of domestic, factory and heavy industrial installation, faultfinding and maintenance You are entitled to your opinion.
Phil