A flame is ionized and thus electrically conductive. The circuit connected to the probe detects the conductivity.
The detector could use one of the spark electrodes as common ground. Or more likely use the burner as the other electrode. The difference in temperature could in theory form a crude diode, this would make it possible to detect short circuits and leak currents.
Thanks, Robert, that makes perfect sense to me.
The traditional type of flame failure device relied on a thermocouple providing power to a magnet in most older boilers and also the burners and oven of my gas cooker.
Edited By old mart on 07/04/2023 18:53:56
They are often referred to as "Thermocouples" so implying that at the other end of the lead the control unit detects a volyage and allows the main valve to open to supply gas to the burners.
Howard
Our boiler has just a single electrode which provides the ignition spark and detects the pilot flame. Advances in electronics, I suppose – but our boiler is over 15 years old.
I have just repaired the central heating system I recently "inherited", (and which had 6 separate faults),
During my investigations and fault finding; I learned that a flame is conductive and can be used to detect the presence or absence of a flame.
In the case of my old Potterton Netaheat 80E, nobody would give out any information, so I traced through the PCB and found that the flame sense circuit uses the ignitor probe itself to detect the flame and hold a relay over, which enables the gas valve. The ignitor is literally just a metal probe, not a thermocouple in this model.
I tried to find the fault on the board, but could not obtain a circuit diagram and ran out of time during the coldest part of the year so far, (isn't it always when the heating fails?), and bought a new PCB. Cost me £82.
I have no doubt that had I been clueless and had to call a plumber, they would have sold me a new boiler and a new pump etc…..plus labour costing probably the best part of £2,000.
Edited By John Doe 2 on 08/04/2023 09:23:18
Having designed gas boiler ignition controllers the flame failure detector uses the ionisation effect of a flame which acts like a diode. So an AC voltage is applied to the flame probe and the resultant DC voltage operates a transistor to allow the main burner gas valve to open. The controllers have to be designed so that a single circuit component failure will either shut down or prevent start up of a boiler.
Most modern domestic boilers are fan assisted so the controller first runs the fan for a time in order to clear any combustion products or gas from a previous start attempt and then tests for a change of state of the microswitch on a diaphragm air pressure sensor. If this proves OK the controller opens the pilot flame valve and begins spark ignition whilst detecting for pilot flame presence. If this is proved the controller opens the main burner gas valve and the main burner is ignited by the pilot flame. If pilot flame ignition isn't proved within something like 5 seconds the controller may immediately go to lockout and display a warning, usually a red LED, or repeat the sequence, usually no more than two times before going to lockout.
Older boiler designs used a continuous pilot flame which used a thermocouple to detect flame and hold the pilot gas valve open. Since this type of boiler contained no electronics the thermocouple although only producing a few millivolts could generate a reasonable amount of current. The coil of the pilot valve was just a few turns of thick wire and the valve would be opened manually to close the magnetic circuit. So the current from the thermocouple was insufficient to pull the valve in but sufficient to hold the valve open so providing fail safe control. If the thermocouple went open circuit, which was the most common failure mode, the pilot gas valve would close. An interlock within the valve block would prevent the main burner valve being opened if the pilot wasn't operated.
CS
I forgot to mention that it is now illegal for anyone to service a gas appliance that are not trained and certificated to do so. However like many thing " for the guidance of wise men (women) and the obedience of fools".
CS
I have a Potterton Netaheat that I have been "nurturing" for three decades, and I can confidently say that the boiler control lasts for fifteen years before it needs fixing. I conducted the fix twice in the same way, and it worked both times. I do now have a spare controller which I swap in when it fails so I have time to fix the old one and keep the newer one at "low hours".
Like John I reverse engineered the controller, and made all those discoveries. I've included the schematic I extracted below. I never thought anyone else might benefit from it, so I never posted it.
The main problem is that C2, which is an electrolytic capacitor, dries out. The flame sensor circuit is very sensitive, and it depends on a smooth DC rail from the mains to work properly. When the capacitor dries out, the supply has too much ripple and the circuit can't see the tiny (around 1nA) flame current.
The world is going to the wall, unfortunately, as we all know. I've been looked at getting my trusty boiler working from a battery and an inverter. As we know security of power provision is looking a little feeble over the coming few years.
With this boiler control the flame sensor depends on an earth connection and it needs significant capacity. If you run the boiler from an inverter you will find that the flame sensor fails even though the pilot is alight. To resolve this issue when using a battery inverter you will need to do two things.
1) Ensure that the boiler earth is connected to the physical earth for your property.
2) Connect the inverter neutral output to the earth that goes to the boiler.
If you do these two things, then a Potterton Netaheat can operate from a battery inverter, even when there is no electrical supply to your home. In these circumstances, the law may not need to get in the way of your probable need for basic hygiene.
Edited By Andy Ash on 08/04/2023 11:33:33
Andy, that is a brilliant and very nicely drawn circuit diagram ! Much better than my spidery and confused efforts !
I could have done with yours about 6 weeks ago to fix my own system, but nobody will allow that information, even though it is just electronics, and not touching the gas side at all.
I don't quite understand where Q1, Q2, Q3, get their other supply rail from? The mains neutral feed is one side and presumably 39V is created across C2 by Z1, but the circuit seems one legged to me ? Where is the current return path from the collector's side ? I think that is where I got confused with the circuit and was forced to give up.
I think your inductor, labelled (?), in series with the spark transformer primary is actually a spark gap. I think C8 charges up until it can jump the spark gap which sends a pulse through the transformer.
Ah well, at least I can fix the old board now to keep as a spare..
Edited By John Doe 2 on 09/04/2023 10:32:08
The supply to the transistors is is via diode D1. They are running from a negative supply with respect to ground. The mains neutral (connected to PNP transistor emitters) is connected to earth at the mains supply.
Robert.
Ah, sorry, me being dim. I assumed "FL" meant flame probe. It means fused live. Makes perfect sense now.
Edited By John Doe 2 on 09/04/2023 19:51:20
Even the gas-fitters find it difficult to obtain information.
A lot of the boiler manufacturers will refuse to allow anyone – qualified or not – to repair the electronics, only to replace the whole board at £(several hundred) a time. So they do not issue manuals and components.
if you wonder why plumbers, electricians, etc., seem to charge so much for so "little" try thinking how you would run a business, or how much you really cost to employ. Not your Gross Pay, your charge-rate. I think mine was something like twice GP.
If they are GasSafe, HETAS, FENSA, etc., registered it costs them a considerable sum of money annually, in fees and lost income, to maintain. A big company like British Gas can pick up the tab but a sole trader has either to shoulder the burden from his own pay or spread it around his invoices, within "Labour Charges". Money for old rope for the accreditation companies!
When I had the front of my home re-pointed recently I was surprised not by how much but by how little, relatively, it cost, with the scaffolding hire as well.
I have just repaired the central heating system I recently "inherited", (and which had 6 separate faults),
During my investigations and fault finding; I learned that a flame is conductive and can be used to detect the presence or absence of a flame.
In the case of my old Potterton Netaheat 80E, nobody would give out any information, so I traced through the PCB and found that the flame sense circuit uses the ignitor probe itself to detect the flame and hold a relay over, which enables the gas valve. The ignitor is literally just a metal probe, not a thermocouple in this model.
I tried to find the fault on the board, but could not obtain a circuit diagram and ran out of time during the coldest part of the year so far, (isn't it always when the heating fails?), and bought a new PCB. Cost me £82.
I have no doubt that had I been clueless and had to call a plumber, they would have sold me a new boiler and a new pump etc…..plus labour costing probably the best part of £2,000.
Edited By John Doe 2 on 08/04/2023 09:23:18
I cut my eye teeth on Netaheats and the Abergas HTM boilers as a gas service technician in the Early 1980's. 90% of circuit board faults were the main relay failing. The Abergas was the first Domestic unit to use the flame rectification system in the mid to late 1970's . Common though when instant shut off was required for large industrial burners and mid range package systems they could singe ones eyebrows drastically if they took more than a millisecond to detect a flame outage. Now, flame rectification detection is probably the most common flame failure device used in room sealed chambers
Edited By Fred Jolly 1 on 27/04/2023 22:54:55
I forgot to mention that it is now illegal for anyone to service a gas appliance that are not trained and certificated to do so. However like many thing " for the guidance of wise men (women) and the obedience of fools".
CS
Incorrect. The gas safety regulations state that one must be competant to work on gas fittings (this includes appliances) competency would be decided by a court of law in extreme circumstances.
One only needs to be a certified and registered if doing such work in the course of trade or buisiness
Even the gas-fitters find it difficult to obtain information.
A lot of the boiler manufacturers will refuse to allow anyone – qualified or not – to repair the electronics, only to replace the whole board at £(several hundred) a time. So they do not issue manuals and components.
if you wonder why plumbers, electricians, etc., seem to charge so much for so "little" try thinking how you would run a business, or how much you really cost to employ. Not your Gross Pay, your charge-rate. I think mine was something like twice GP.
If they are GasSafe, HETAS, FENSA, etc., registered it costs them a considerable sum of money annually, in fees and lost income, to maintain…….
That's a fair comment.
My beef is telling even trained and qualified electronics engineers, that we may not legally work on a control board.
If there is a minor fault on a board, the "Gas" technician puts in a whole new board at enormous cost, when the fault might have only been a £4 relay or a 40p capacitor for example. Fine, the Gas technician does not have the time or the skills and knowledge to fault find a PCB and solder in new components, but those of us who do are prevented by the manufacturers not releasing the information and forcing us to pay huge sums.
My other beef is that in my experience of the last three houses we have owned; the central heating systems have been installed in a very slap-dash way, with very poor pipe runs, in the sense of restricted flow, and components thrown in as quickly as possible, rather than being logically laid out, and no thought given to maintenance of, or replacing components. Floor joists weakened by installers cutting them in the wrong places for pipes. Also the use of push-fit water pipe couplings, which only have a life of around 20 years owing to the O rings failing. Very quick to install but when they start to leak and water comes through your lounge or kitchen ceiling, meaning you have to tear out the plaster board, fix the leak, and then replace, re-plaster and redecorate…………
I don't mind paying high prices for good quality, but I object to high prices for terrible quality or terrible work.
I just know that had I been a little old lady with no technical knowledge when our boiler failed; the gas technician would have pretty much forced me to have a new boiler supplied and fitted for about £2,000 because "the old one was beyond repair"…….They typically add a 60% surcharge on new items they supply too.
Nope, it is all working beautifully now – much better than when we moved in, and the cost of components was about £85.
I know this thread is over a year old but just wanted to convey my thanks to Andy Ash for the diagrams.
I also have a 30+ year old Netaheat that has had occasional controller problems.
Apart from the dry joints that were reflowed many years ago, one infrequent issue is with the pilot ignition.
The fan starts, pressure is detected and the pilot valve operates but no spark.
You can see this from the fact that the gas discharge device on the controller does not spark.
The cure for me is to brush all the collected dust etc from both sides of the board around R14 and C8.
I think either the gas discharge component is ageing or the dust build up is slightly conductive meaning that C8 never gets charged to the breakdown voltage. You don’t need much conductivity around a 22M resistor to make a difference.
This boiler has out lived one fan, two pumps and three main controllers (one of which was a recent Wiser which went pop (literally) one morning).
We’ve even had the gravity hot water replaced by a Megaflow. It was only after the Wiser was installed that I discovered the safety motorised valve in line with the heat exchanger on the cylinder was not electrically connected!
Posted by Clive Steer on 08/04/2023 10:58:07:
I forgot to mention that it is now illegal for anyone to service a gas appliance that are not trained and certificated to do so. However like many thing ” for the guidance of wise men (women) and the obedience of fools”.CSIncorrect. The gas safety regulations state that one must be competant to work on gas fittings (this includes appliances) competency would be decided by a court of law in extreme circumstances.
One only needs to be a certified and registered if doing such work in the course of trade or buisiness
But Fred, Regulation 3 includes this provision:
(1) No person shall carry out any work in relation to a gas fitting or gas storage
vessel unless he is competent to do so
And para 83 covers DIY:
83 Anyone who does work on a gas fitting or gas storage vessel must be
competent to do so (whether or not they are required to be a member of an
approved class of persons). Therefore, do-it-yourself gas engineers and those
performing favours for friends and relatives all need to have the required
competence. The level and range of competence should match the full extent of
work done, but needs only to be sufficient for and relevant to that work
I’m sure what defines competency could be challenged in a court, but the HSE expectations are pretty clear, so I’d expect a home maintainer who caused an accident to get short shrift!
Competency requires:
81 Gas work should only be undertaken:
(a) by a person who has successfully completed an industry-
recognised training course followed by assessment of
competence. Training that leads to assessment of competence in
safe gas work should be recognised by the industry’s standards
setting body; or
(b) in the case of a currently or previously registered person, where
they have proved competence through a certification scheme; or
(c) for those working at premises that fall outside the scope of the
Regulations (see regulation 2(4) and associated guidance), by a
person who has successfully completed an appropriate full
training course followed by assessment of competence.
82 Training should be of a standard to enable a gas engineer to achieve
competence in the safe installation, purging, commissioning, testing,
servicing, maintenance, repair, disconnection, modification and
dismantling of the gas systems, fittings and appliances with which they
are working. This should include an adequate knowledge of:
(a) relevant associated services such as water and electricity;
(b) the potential for exposure to asbestos;
(c) the dangers these may give rise to;
(d) the precautions to take
I haven’t done an Industry Recognised Course, or had my Competence assessed (ie, shown I understood the training). Therefore I don’t touch gas boilers, even though I’m fairly familiar with how they work.
A particular problem with gas is the amount of damage that can be done. A tiny leak can cause a room to fill with an explosive mix that goes bang when triggered by an equally tiny spark. The explosion can be powerful enough to demolish a semi-detached pair, and that results in serious bother even if no one is killed.
Remember Ronan Point? Cooker installed by unqualified gas fitter, who connected it with an unapproved brass water fitting and cracked it by over tightening…
Ronan Point is interesting because the damage is out of all proportion to the rather small explosion that caused the collapse. It turned out that although the design that should of stopped walls from popping out was on the weak side, the British Workman, had frequently failed to fill the joint with concrete, preferring sweepings and old fag packets instead. For reasons unexplained, no foremen or inspectors had checked the joints. Incompetence galore, people not doing their jobs properly…
Dave
Although working on gas appliances may not be illegal if there were a “incident”, proving you had the required competence, in court, may be very costly. If you thought a gas fitters’ hourly rate was high wait till you have to engage a Barrister.
Re-soldering dry joints in a controller, which is a fairly common fault due to the thermal cycling they experience, is probably OK and low risk. However replacing any components associated with the “safety” circuit is more problematic as replacements must match the original exactly. Some components used by controller manufactures were specially made or selected for their designed function. For instance relays used on controllers may have their pull in and drop out currents different to those of normal commercially available types to ensure that they could be considered fail safe. Similarly their contact size and spacing may be larger to ensure the contacts can’t weld. Without reverse engineering the circuit and determining what components are involved in the safety circuit replacing any component may produce subtle function changes. It isn’t always about what the circuit should do but what it mustn’t do that is more important and how does one test for that. Those who have designed “fail safe ” products will know how a special mindset is needed plus exhaustive testing by someone not associated with the design phase.
CS
I agree with you, Clive, and it’s not always understood that working on boiler controls should be considered as working on the gas appliance.
To your point about “fail safe” and in relation to this particular thread, I note that the design has considered two particular instances of single point of failure.
Resistor R10 is presented as two parallel components as is Zener Z1.
My board is version 3 and it would be interesting to know if earlier versions incorporated this.
My assessment is that failure of R10 could lead to detection of a flame when there isn’t one resulting in the main burner being engaged.
In my case, the fault is with the spark ignition resulting in the pilot valve being open but the pilot not ignited.
There is no designed protection against this case (timeout, duplicate circuit etc).
I assume that the resultant gas escape is not considered unsafe because the fan is running and forcing the limited unburnt fuel out of the boiler.
By extension, it can therefore be assumed that the ignition circuit is not a safely critical area and thus can be worked on by DIY ‘specialists’.
…
I assume that the resultant gas escape is not considered unsafe because the fan is running and forcing the limited unburnt fuel out of the boiler.
By extension, it can therefore be assumed that the ignition circuit is not a safely critical area and thus can be worked on by DIY ‘specialists’.
That’s two ‘assumes’ both of which could be wrong! Years ago I did a full course on the danger of assumptions, where the point was rammed home by telling us to always render ‘assume’ as ‘Ass of You and Me’. Anyone stating an assumption was sent away to clarify it, either by confirming the assumption was a fact, or, if that was impossible, by recognising it as risk. Risks are managed, whereas the failure of an assumption comes as a surprise. Also told to be suspicious of ‘facts’, because humans often confuse them with opinions, beliefs, misunderstandings, folklore, fake news, and lazy jumping to conclusions. Many things claimed to be facts are assumptions.
Here’s another likely assumption. When eeeps boiler was designed, it was for a given service life, after which it was expected to be replaced. The service life is governed by wear and tear on the mechanicals, corrosion, ageing of the electronics, condition of the burner, cost-cutting compromises and other characteristics of the system. Likely a commercial boiler is safe only on the likelihood that it will be replaced as soon as the cost of a commercial repair is uneconomic. All bets are off in the very unusual event that an increasing risky boiler will be kept going well beyond it’s service life with patch repairs.
Another consideration is efficiency. Old boilers weren’t particularly efficient when new, and efficiency tends to decline with age. Given the ever rising cost of gas, it’s likely that eeep would have saved money by fitting a modern boiler 15 years ago…
Keeping stuff going by repair and restoration is great, but keep an eye on the big picture. As a whole, is the device being mended still safe? Is the work worthwhile. With something like a Myford lathe the answer is almost certainly yes. A 30 year old gas boiler is in a different league: Carbon Monoxide is extremely poisonous; there’s a serious gas leak and explosion risk; the control system is moderately complex, and includes safety critical factors. This is all in addition to the usual plumbing and electrical hazards.
Dave
eeeps assessment that the ignition circuit is not part of the “safety” circuit is correct. So replacing the gas discharge device in the ignition circuit is low risk. If the wrong device is fitted the spark rate may become faster or slower resulting in less reliable ignition but shouldn’t affect safety.
At the time, 1985, when I designed a boiler controller a British Gas technician, working for their approvals section would take our product, unsolder every component and reconnect it using tinned copper wire “stalks”. They would then open or short every component in turn and note the circuit reaction whilst it was operational and also when starting from cold. The reaction they were looking for was that the boiler would shut down and restart would not be possible. This only applied to the “safety” section of the overall design.
All electronic and electro-mechanical components had various failure mode classifications. For instance a metal film resistor could fail O/C but regarded as not able to fail S/C. However a wire wound or solid carbon resistor could fail O/C or S/C. This failure mode also applied to capacitors, inductors or semi-conductors such as diodes and transistors. Relays were largely regarded as fail safe provided any possibility of welded contacts or arc over were addressed by using an appropriate safety margin. In one design I saw a special feature of a relay was used to provide safety. In the circuit the relay, which controlled the main gas valve could be held by the flame sensing circuit but the circuit couldn’t provide sufficient current to pull the relay in. Basically the relay, which looked like many others, had a larger gap than normal between the moving pole-piece that operates the contacts and the main coil pole-piece. A subtle but critical difference and I’m sure other controllers used similar tricks or novel arrangements to achieve a safe but cheap and reliable product.
CS
A lot of points covered in this revival
1/ it is interesting that unlike certain electrical work (part P), gas work does not require any notification. This means there is no record of the work.
2/ One ssue not mentioned if you DIY and something goes wrong is that your insurance may be invalidated.
3/ The spark gap breakdown voltage may increase with age due to a number of mechanisims. These include electrode erosion and decay of any radioactive material that is sometimes added to stabilise the the breakdown.
4/ I agree with Clive on parts subsitution. You don’t know the full reasons for component selection especially safety components. As an example I once designed a controller for a set of 3 halogen lamps (used for a non-lighting application). The mains power was switchd by a relay. As many will know filament lamps have a high initial (inrush) current. Having 3 halogen lamps in parallel does not help. I selected a particular version of a standard size relay. This had siver cadmium contacts specifically designed for lamp loads (today I’d use a solid state relay) and cost about three times a standard model. The only difference was one letter in the part number and a amber rather than clear cover. It was a standard part of many of the products the company made. The PCBs where assembled in house. As there was a relay and software (PIC) control I included a thermal switch on the lamp housing to prevent overheating in the case of failure. After a couple of years we got a few failures on new machines. The first were fixed by the field service technicians but when they failed again I was asked to look. As soon as I saw the PCB the problem was revealed, the relay had a clear cover. Production had decided to do a component cost review and decided to fit the “identical” cheaper relay. The subsequent rework and replacement programme, we had machines all over the world, cost a lot more than the saving on relays.
The use of two components when one would give the same nominal “headline” value can be for a number of reasons including increasing a secondary parameter such s power or voltage or for reliability / safety / regulatory reasons. For the latter three you can’t tell by looking at the component datasheet. Only the designer knows for sure. Even fitting a “better” component can affect them.
Again a practical example. Forty years ago I designed a conditioning circuit for an aircraft fuel gauging system. As it had a connection inside the fuel tank it had to meet fuel tank non-ignition / intrinsic safety requirements. Normally compliance would be shown by testing but test house availblity and first flight dates did not align. So I suggested showing compliance by design and analysis to a (non-aviation) intrinsic safety standard. Much to the surprise of the “old hands” the regulator acceped this approach. The circuit ran off 28VDC and the input circuit was a small fuse followed by a 33 Ohm power resistor and a 36V 10W zener diode (spike supression). At a nominal supply voltage of 28V even a short circuit of the diode would only result in 0.85 amps flowing. However the fuse was rated at 3.15A. The circuit also had two resistors in series with the connection to the fuel tank each would limit the current to less than the minimun ignition current. Two were required to meet the requirement that no two failures could cause excess current to flow (there is a lot more detail to this). All went well and the aircraft was certified. A few years later, after I’d left the company (it had changed ownership) they contacted me to ask for a change to the fuel gauge calibration as they had changed the wing structure. I said OK but needed a spare conditioner and the test box to validate the change. When I opened the conditioner I noticed that it had a 0.5A glass fuse fitted. On questioning they said their sub-contract assembly house for the conditioner had noticed that the 3.15A fuse would not open even on a short circuit and the unit only drew 0.25A they suggested a change to 0.5A. They obviously had not been given the safety analysis. The only reason for the fuse was to meet a requirement in the intrinsic safety standard for a “sand filled ceramic bodied” fuse approved to a specific standard. The lowest rating allowed by that standard was 3.15A so I had to use that. By changing it they had technically broken the safety of the system. In reality the system was safe, the specific fuse was required becuase the non-aircraft standard considered that the DC supply might be accidentally connected to the high energy 240V mains supply. Obviously this does not exist on the aircraft. The aircraft in question was the NAC-6 FieldMaster / FireMaster.
Robert.
Home › Forums › The Tea Room › Topics
Started by: Martyn Nutland 1
in: Workshop Techniques
simondavies3
Started by: Vic
in: The Tea Room
Speedy Builder5
Started by: Roderick Jenkins
in: CNC machines, Home builds, Conversions, ELS, automation, software, etc tools
renardiere7
Started by: Arthur Jones 2
in: Locomotives
Macolm
Started by: leov
in: Manual machine tools
Diogenes
Started by: kinross1
in: Manual machine tools
teamricky
Started by: Mick Bailey
in: Materials
old mart
Started by: richard1989
in: Beginners questions
Vic
Started by: Andy Brocklehurst
in: General Questions
old mart
Started by: tomread12
in: Introduce Yourself – New members start here!
tomread12
Started by: mfengine1
in: Books
Norman Blackburn 1
Started by: Turbine Guy
in: Stationary engines
Turbine Guy
Started by: MarkS
in: General Questions
Nicholas Farr
Started by: jamesrot
in: General Questions
Colin Bishop
Started by: Brahma
in: Beginners questions
old mart
Started by: Ketan Swali
in: General Questions
MarkS
Started by: teamricky
in: Workshop Tools and Tooling
Neil Lickfold
Started by: MarkS
in: General Questions
JasonB
Started by: Arthur Jones 2
in: Locomotives
duncan webster 1
Started by: Taris Jewell
in: Manual machine tools
Taris Jewell
Started by: Speedy Builder5
in: Workshop Tools and Tooling
Pete
Started by: Ian Parkin
in: Electronics in the Workshop
Robert Atkinson 2
Started by: Alistair Robertson 1
in: The Tea Room
old mart
Started by: old fool
in: The Tea Room
old mart
Started by: IanT
in: Manual machine tools
old mart