Er…
One of those yellow pushbutton kedu type switches is by definition a direct on line (DOL) connector (switch) though the convention is that the word "starter" indicates that an appropriately sized overload device is included. As several have said, yer gets yer no volt release (NVR) function either way.
The IET wiring regs (BS7671) determine that a overload protection device must be fitted to automatically disconnect the supply to a motor in the event of overload (usually overcurrent) if the motor is over a certain size. From memory that size is 0.375 Kw (1/2 HP). A motor thermal overload relay is a far more sensitive device than any of the usual types of MCB in that it is designed to imitate the thermal characteristic of a motor and monitor its recent service history as well as the presence of an instantaneous fault. An MCB – even of the various different types (A, B, C or D) – is a different beast entirely..
Small overloads do exist, but below 0.375 Kw it's a bit of a lottery, as the current/load characteristic of small induction motors is a black art, and needs to take into account the phase angle of the load current. So protecting a small (sub 1/2 HP) motor with a plug top fuse isn't ideal, but is probably as good as it gets without major complication.
Using DOL starters on single phase is easy enough, provided the coil voltage for the maintain/NVR function is 230 volts not 400 as it might well be on a starter designed for three phase use. Remember to double back the load current through the spare poles of the overload on a three phase starter used on single phase so all three poles of the overload see the same current, as most are sensitive to current imbalance and will trip if one pole is left unused.
HTH Simon
Edited By Simon Williams 3 on 26/04/2019 14:15:37