Posted by Brian Wood on 20/03/2017 18:04:51:
Hello Dave,
I wired out the supply to my workshop with 6mm armoured cable. The total cable distance from the consumer unit and destination is comparable to yours and voltage drop calculated at under 5 volts. Remember to buy 3 core cable so that you have a copper cored earth, the armour is steel sheathing and not really good enough for a reliable earth. and will get failed if you put it up for test certification.
You will also need the appropriate size of glands at each junction point.
Regards
Brian
I'm not sure your advice about not using the armour as a protective earth is quite right there.
If you use SWA, it would certainly be bad practice not to use the armour as an earth conductor. It is very much more than sheathing. Indeed it is the very definition of an electrical protective earth. It is virtually impossible to damage a phase conductor without first cutting the protective sheath. The very act of encircling the phase conductors with the earth offers a method of electrical protection and essentially guarantees fast circuit breaker action if the cable is accidentally cut.
There is much uncertainty out there on this matter, so lack of awareness can be excused. One thing is certain, poor implementation will not be excused by mother nature under fault conditions.
People have generally noticed that corrosion can set in at glands and where the outer plastic sleeve becomes damaged. This can compromise the earth bond, and provide less than adequate protection.
Some recommend using an additional copper earth conductor inside the armour, others an additional copper earth conductor outside the armour.
Both schemes have problems;
1) If the armour is electrically damaged then neither scheme can guarantee to expose the earth conductor to the phase if the cable is cut. If the digger bucket scrapes along the length of the conductor then phase can be exposed without shorting to the protective earth. One is dependent on soil resistance to operate the circuit breaker in this situation, and it is not good.
2) If the parallel wired copper earth conductor leads an electrical test operative to believe that the armour is intact during test, then no-one may know that the armour has actually become damaged.
In conclusion; if the armour is not good enough to do the job because of corrosion, then it has not been monitored and maintained properly.
In most cases there is no reason why a steel wire armour cannot perform the function of a protective earth. If the calculations show that the armour can trip the fault circuit in the prescribed time, then my opinion is that it is safer only to use the steel wire armour.
Like all engineered installations it is important to periodically check and maintain equipment to ensure safety.