      I’m having to rethink the single phase 2hp motor on my lathe, it’s too powerful and eats electricity, £85 more last month than normal . I have two other motors both 1/2hp one is 3 phase and the other is single phase . I have a vfd for the 240v 3 phase . Which one would have more torque .

      Sean

      Advert
      #26337
      sean logie
      Participant
        @seanlogie69385
        #384510
        Simon Williams 3
        Participant
          @simonwilliams3

          85 quid is about 300 hours running, so that’s a month of 12 hour days. You don’t need a smaller motor you need w holiday

          #384512
          David Jupp
          Participant
            @davidjupp51506

            If rated speeds are similar, then toque will be similar at same power. Power is proportional to torque x speed.

            If one motor has significantly lower rated speed (e.g. a 4 pole motor at half the speed of a 2 pole motor) it'll produce more torque.

            The 3 phase motor will have smoother torque delivery, and the VFD brings other benefits.

            #384513
            Brian H
            Participant
              @brianh50089

              Agree with above, 3 ph every time.

              Brian

              #384517
              Mike Poole
              Participant
                @mikepoole82104

                Powerwise they are both 1/2hp so not a lot to choose between them. To go from 2hp to 1/2hp is a big change, what would the standard motor size be for the lathe? If the 1/2hp motor will drive the lathe and cut a large diameter at slow speed then you may be in luck. The VFD solution will give a more flexible drive but remember even if the VFD has a sensorless flux vector mode that can maintain 100% torque at lower speeds it does not give full power so at half rpm you will have about half power. The usefulness of belts and gears is that power is maintained at low rpm so torque is multiplied. Using the VFD and the mechanical speed reduction is probably the best of both worlds.

                Mike

                #384518
                SillyOldDuffer
                Moderator
                  @sillyoldduffer
                  Posted by sean logie on 08/12/2018 11:01:05:
                  I'm having to rethink the single phase 2hp motor on my lathe, it's too powerful and eats electricity, �85 more last month than normal . I have two other motors both 1/2hp one is 3 phase and the other is single phase . I have a vfd for the 240v 3 phase . Which one would have more torque .

                  Sean

                  Um, look for a fault or some other cause unless you've been been working the lathe really hard. At 20p per kwh £85 would buy you 212 hours continuous operation under full load. That's about 3 working weeks of 10 hour days cutting metal flat out. Depends on what you're doing of course but few hobby lathes are used like that.

                  Also motors shouldn't consume full power unless actually doing strenuous work. Unlikely on a lathe, partly because most cuts aren't that deep in tough metal with blunt tools and partly because full power is only consumed while actually cutting, which is intermittent. My lathe has an 1500W output motor but I rarely consume more than 600W during a typical cut. I'm not particularly delicate, and have hit 1400W cutting with power traverse and carbide going 1.5mm into mild steel. From memory, idling consumes about 150W, and driving the lead-screw & gearbox costs another 150W. Even so the lighting in my workshop uses more electricity than the tools.

                  If you're really using that much power to cut metal, switching to a smaller motor is a bad idea. It won't save money and cutting the same amount of metal will take proportionally longer.

                  As we're heading into winter have you been using an electric fire, perhaps leaving it on overnight to defeat condensation? Or is the lathe unusually stiff, you might have some bad bearings or a lube failure?

                  Dave

                  #384520
                  sean logie
                  Participant
                    @seanlogie69385

                    I tried to tell er indoors that the lathe isn’t what’s chewing the power it’s the bloody condenser tumble dryer 😂🤣

                    #384523
                    Phil Whitley
                    Participant
                      @philwhitley94135

                      I agree with Simon Williams, that seems like a lot of power useage. assuming 17p per kW hr thats 10.6 hours per day running and loaded! Are you really working those hours, or have you got some other electrical problem, like for instance, a faulty immersion heater which is not RCD protected? To answer your question always go for three phase, they are more efficient and deliver smoother torque than single, and with the vfd you can do soft start and speed control too. Do you have a smart meter ? there has been talk about the smart meters ability to apply higher usage to inductive loads like motors which have poor power factor, but don't know if this is really happening (yet) or not. With a VFD in circuit, this may not be recognised by the meter as actually being an inductive load. Are you on the end of a long supply line in a remote area? If so, volts drop is a possibility too. Try the 3 phase/vfd motor for a month, and see if there is a marked drop in your consumption, if not, look for another problem!

                      Phil

                      #384524
                      Phil Whitley
                      Participant
                        @philwhitley94135

                        well you said it Sean!!! a condenser tumble dryer with a blocked or partially blocked condenser spray will chew away for hours and not dry clothes at all! they are a fundamentally crap idea! chuck it out and get a ducted outlet one.

                        Phil

                        #384528
                        Neil Wyatt
                        Moderator
                          @neilwyatt

                          Ha! You are probably the person who needs a smart meter – I knew there was one!

                          Wouldn't hurt to get a smart plug and test various appliances to see how much they really use.

                          Neil

                          #384529
                          Phil Whitley
                          Participant
                            @philwhitley94135

                            Good idea Neil!

                            #384532
                            Clive Foster
                            Participant
                              @clivefoster55965

                              Plenty of smart plugs on Amazon, and probably E-Bay too, for around £12 to £20. I shall get one if and when I have an issue that simple maths and specification data won't resolve.

                              Before buying tho' do verify how much space and where is needed. Most of them look as if they will at least partially obscure the switch. CPC (Farnell) sell a nice looking one with the display and control buttons below the plug part so the cable hangs down over it. D'oH. Supposed to be professional outfit yet sell summit with such an obvious design blooper. A mistake that obvious makes you wonder how good the innards are.

                              Clive

                              #384533
                              Phil Whitley
                              Participant
                                @philwhitley94135

                                Read this Sean!

                                https://www.mumsnet.com/Talk/products/214863-tumble-dryer-condenser-or-vented

                                I do not make the claim for the crapness of condenser dryers lightly, it is based on the experience as a repairer of vastly extended drying times and large electricity bills. some very expensive ones may have a slight edge over ducted when they are new and working correctly, but that doesnt last for long as the condensing system spray tends to block up with limescale, fluff or grit from the water supply, and of course the only way you know it is not working efficiently, or indeed at all, is by the drying time getting longer and longer, This seems to apply even more to the combined washer/dryers which are an absolute pig to repair, and usually fail again in pretty short order. they are a good idea IN THEORY, but in practice they take much longer to dry clothes, and therefore use more power. Try convincing a customer who bought the all singing and dancing expensive wash/dry machine that it is working correctly and then get called back when she finds she can only get one wash dry cycle in a day, and the clothes are still damp. The latest ones use heat pump technology (refrigeration) to condense the water andalso have "vigorous condenser cleaning" which flushes all the lint out of the condenser, which is another problem that most suffer from but this has an energy cost too., This is why among the top ten efficient tumble dryers you only find 2 condensing ones, and one of those is at number ten! For all us mortals who cannot afford to buy Siemens ar Miele, stick to ducted, and avoid washer dryers like the plague!

                                https://www.sust-it.net/energy-saving/tumble-dryers

                                #384537
                                Simon Williams 3
                                Participant
                                  @simonwilliams3

                                  All joking about tumble driers aside, the OP has raised an interesting question regarding the relative efficiency of single and three phase motors.

                                  Given that a single phase motor is a fairly nasty electrical load, but a three phase motor on a single phase supply suffers the conversion inefficiency of the VFD, there's likely not much to choose between them in terms of converting cost of electricity into work done.

                                  Does anyone have any in situ estimates of the actual efficiency of power out over power in for the sort of size motor (1 – 3 HP say) we are likely to encounter in a home workshop?

                                  Best rgds Simon

                                  #384539
                                  Phil Whitley
                                  Participant
                                    @philwhitley94135

                                    Short answer is No Simon, I have only installed a couple of VFD's for a friend, as I have three phase in my workshop. You would have thought that the soft start would avoid the sudden loading of a motor starting, but I dont really know. Time to use what my old boss called the "tong testers"< A clamp meter, and do the maths!

                                    #384541
                                    Phil Whitley
                                    Participant
                                      @philwhitley94135
                                      #384543
                                      Mark Rand
                                      Participant
                                        @markrand96270
                                        Posted by Phil Whitley on 08/12/2018 13:31:20:

                                        Read this Sean!

                                        https://www.mumsnet.com/Talk/products/214863-tumble-dryer-condenser-or-vented

                                        I do not make the claim for the crapness of condenser dryers lightly, it is based on the experience as a repairer of vastly extended drying times and large electricity bills. some very expensive ones may have a slight edge over ducted when they are new and working correctly, but that doesnt last for long as the condensing system spray tends to block up with limescale, fluff or grit from the water supply, and of course the only way you know it is not working efficiently, or indeed at all, is by the drying time getting longer and longer.

                                        What water supply? who buys a condenser tumble dryer without a heat pump these days? Ditto, don't people clean the filters?

                                        #384545
                                        Mike Poole
                                        Participant
                                          @mikepoole82104

                                          As a machine tool motor in a home workshop is most likely to spend much of its time only lightly loaded then its efficiency is going to be poor. Rather like the optimistic fuel consumption figures for a motor car are only realised under ideal conditions an electric motor will only reach its maximum efficiency under optimum conditions. I think cutting the plug off the tumble dryer would have the the most impact on your electricity bill (and mine).

                                          Mike

                                          #384549
                                          Tim Stevens
                                          Participant
                                            @timstevens64731

                                            Don't forget that when any motor is running idle its efficiency is ZERO.

                                            Tim

                                            #384556
                                            Phil Whitley
                                            Participant
                                              @philwhitley94135

                                              mark rand, that is exactly what it says in my post! their poor showing in the efficiency stakes, and the extremely high retail cost (£825.00 for the Siemens) shows how efficient they actually are! heat pumps may work, but add to complexity,. A ducted TD takes already warmed air from your house, heats it some more, it absorbs the moisture in the clothes, and then gets thrown out the duct, a condenser one has to cool the air down to its dew point every time it is cycled, then reheat it the actual efficiency gain is very marginal at best, as is witnessed by the poor results in the league table. I wonder if it would last long enough for you to save the difference in retail price, I very much doubt it!!

                                              #384559
                                              Phil Whitley
                                              Participant
                                                @philwhitley94135

                                                Oh, and no,people generally dont clean the filters, thats why they catch fire, that and abysmally crap design!

                                                #384626
                                                Mark Rand
                                                Participant
                                                  @markrand96270

                                                  Sean, an important question that no one has asked yet:- What lathe is it?

                                                  1/2hp is suitable for a Myford sized lathe, but 3/4 is better for even an ML7 (I speak from experience). A lathe that's sized for a 2hp motor is not going to be happy with larger work or more aggressive cuts if hobbled by a 1/2hp motor.

                                                  In terms of power consumption, the losses of a 2hp single phase motor will be greater than those of a 1/2hp single phase motor or 3ph motor + VFD, but the difference is likely to be no more than 25-50W. I.e.. 3/5 of 5/8 of F-all, as one of my colleagues used to say.

                                                  The suggestions of getting a plug in power meter are your best bet. They are cheap these days (especially when Aldi or Lidl have got them on sale, but also from a number of online sellers), and can give you a good idea of just what in the house is eating the power.

                                                  Before you do anything else though, have you got an immersion heater that someone's turned on? smile o

                                                  #384633
                                                  ChrisH
                                                  Participant
                                                    @chrish

                                                    Sean – I think the cost and torque issues have been answered adequately already. What you need to decide is what do you want to run and how big a motor does your lathe require.

                                                    As described here, 3 phase motors are smoother running and the VFD brings benefits like soft start-stop and great speed control via a variable resistor input to the VFD to state but two.

                                                    Having both my lathe and my mill/drill are on 3 phase via a VFD, the latter an upgrade from 1 phase, so to me the choice is a no-brainer, but you pays your money and takes your choice, as the saying goes!

                                                    Bon chance as they say across the ditch.

                                                    Chris

                                                    #384692
                                                    not done it yet
                                                    Participant
                                                      @notdoneityet

                                                      First question might be : what power motor was on the lathe, before the last month?

                                                      Second is where the power has been used. Our leccy bills always go up in autumn/winter. But not by £85 each month.

                                                      Regarding condenser or vented tumble dryers – at least the heat rejected by the condenser type heats the property – not just rejected to the .

                                                      Jumping to unsubstantiated conclusions is often proved wrong on proper analysis of the situation.

                                                    Viewing 25 posts - 1 through 25 (of 52 total)
                                                    • Please log in to reply to this topic. Registering is free and easy using the links on the menu at the top of this page.

                                                    Advert

                                                    Latest Replies

                                                    Home Forums General Questions Topics

                                                    Viewing 25 topics - 1 through 25 (of 25 total)
                                                    Viewing 25 topics - 1 through 25 (of 25 total)

                                                    View full reply list.

                                                    Advert

                                                    Newsletter Sign-up