      Hi all went to turn lathe on today and vfd flashed and then tripped the electric now it doesn’t work it powers up but when flick switch to start lathe it says error 1 which is power protection any ideas is there an internal fuse?

      Advert
      #26411
      kevin large
      Participant
        @kevinlarge76611
        #393243
        John Rudd
        Participant
          @johnrudd16576

          They dont usually have any internal fusing.

          Inrush current limit is usually done with a thermistor feeding the bridge rectifier, bus caps.

           

          If you disconnect the motor from the outgoing terminals, is the error still present? If so, then the vfd is in need of repair.

          What make/model is it?

           

          Edited By John Rudd on 27/01/2019 17:15:40

          #393245
          Nick Hulme
          Participant
            @nickhulme30114

            The most likely failure point for electronics is when powering on.
            I have Siemens VFDs which have been working for over 15 years and were ex-industrial when I bough them, I don't power off VFDs.

            #393255
            ega
            Participant
              @ega

              I have a TECO VFD which failed after some time in service; I returned it to the supplier who "replaced the fuse".

              I s there a consensus for leaving VFDs powered on?

              #393258
              AJW
              Participant
                @ajw

                Interesting point about turning off.
                I find myself if stopping machinery for perhaps taking measurements or changing tooling turning the speed control down to zero.
                Only ‘turning off’ for more extended periods, then powering down completely for lunchtimes.

                Alan

                #393274
                Nick Hulme
                Participant
                  @nickhulme30114
                  Posted by AJW on 27/01/2019 18:18:19:
                  Interesting point about turning off.
                  I find myself if stopping machinery for perhaps taking measurements or changing tooling turning the speed control down to zero.
                  Only 'turning off' for more extended periods, then powering down completely for lunchtimes.

                  Alan

                  Use the VFD Stop rather than turning the speed control down, best case no difference, worst case your potentiometer calibration is off and you overheat something. 

                  When I referred to powering off I meant just that. 

                   

                  Edited By Nick Hulme on 27/01/2019 20:30:24

                  #393288
                  Anonymous
                    Posted by ega on 27/01/2019 17:46:37:

                    I s there a consensus for leaving VFDs powered on?

                    No, if they're properly designed turn on and turn off at the start and end of the day isn't an issue.

                    Andrew

                    #393290
                    Mike Poole
                    Participant
                      @mikepoole82104

                      Industrial VFDs are powered up 24/7. A maintenance manager who was not an engineer insisted that 600 robots were powered down during non production hours to save on electrickery, on power up a high level of failures were experienced which was very expensive in parts and time to fix the breakdowns. Equipment in good condition will not have a problem surviving a power cycle but it will expose anything that is not in its best working order. The power saving trial was soon dropped as the part failure and repair time was not worth the minuscule power saving. I suspect the attrition experienced would have improved as the parts that were weak were eliminated but after spending ten of thousands on spare parts the trial was abandoned. Personally I would prefer to power my workshop down as it is unmanned most of the time and as things do not always fail safe I feel more comfortable minimising the risk. I would rather have a device failure than a fire in my workshop.

                      Mike

                      #393301
                      Peter Spink
                      Participant
                        @peterspink21088

                        I have four VFDs in the workshop and each takes around 15 watts on standby.

                        I reckon that’s about £70 a year 😳

                        #393569
                        kevin large
                        Participant
                          @kevinlarge76611

                          Hi all had a look inside vfd today there are 2 little round things like a lolly on 2sticks one looks burnt if I can find out what they are may be able to solder in new ones will try an figure out how to put a picture on

                          Edited By kevin large on 29/01/2019 16:00:13

                          #393597
                          Ex contributor
                          Participant
                            @mgnbuk

                            2 little round things like a lolly on 2sticks

                            Could be NTC inrush current limiters – these are a highish resistance cold & heat up when the current to the rectifier & capacitors flows (at a reduced level, due to the resistance). As they heat up, the resistance reduces towards zero. Their purpose is to "softly" charge up the capacitors on start-up & some types look as you describe.

                            I have had a couple (in small power supplies) that have gone pop & failed open circuit, so no current flows. There should be a part number on the side of the device – hopefully still readable if it is burnt – that should allow identification & replacement. A search for NTC inrush current limiters will get hits to Franell, Mouser, Digikey etc.

                            HTH

                            Nigel B

                            #393664
                            John Paton 1
                            Participant
                              @johnpaton1

                              t lighting also)+1 for using an inverter. I put a single phase motor in mine and had the power table reconnected for single phase. The main motor was never satisfactory and made a most unpleasant hum which resonated round the workshop with nullls and maxes in certain locations of the room.

                              Changed back to 3 phase with VFD and it's been a revelation – silent and so nice to get the exact speed you want. I have a rotary lever with ball end on the front panel and can adjust this with my knee while operating the feed handles. Magic!

                              I did just have to rewire the panel to separate the single and three phase circuits ( mine has Lovolt lighting also)

                              John

                               

                              Edited By JasonB on 30/01/2019 13:17:58

                            Viewing 13 posts - 1 through 13 (of 13 total)
                            • Please log in to reply to this topic. Registering is free and easy using the links on the menu at the top of this page.

                            Advert

                            Latest Replies

                            Home Forums General Questions Topics

                            Viewing 25 topics - 1 through 25 (of 25 total)
                            Viewing 25 topics - 1 through 25 (of 25 total)

                            View full reply list.

                            Advert

                            Newsletter Sign-up