Home › Forums › General Questions › 3 phase supply (again)
So I thought I was relatively well read regarding my options for getting 3 phase into my workshop. I'm picking up a mill so with my lathe I think that makes 5 off 3 phase motors. I was thinking it would be best to go to a rotary phase convertor. Although they are a bit expensive and a bit noisy.
I've just bumped into digital phase convertors whilst online. They seem ideal so why are they not as popular as the VFD's?
Example I've been looking at
Edited By colin hamilton on 12/01/2022 21:03:46
I think you may well need one for each machine ? You would need a heavy duty supply ie 32A Noel.
If it's a digital version of the older style rotary converters, then you won't need one for each machine so long as the total power consumption of the machines running at any one time are within the limits of the converter.
The advantages would appear to be no messing about or rewiring of your three phase machinery, only needing to buy one for your entire workshop.
The dissadavantage as I see it would be price and not being able to customise control for individual machines as you could if each had it's own VFD.
I think that in effect they are just VFDs, except maybe not variable frequency!
Colin
All VFD drives can act as digital phase converters as described by your link. They just need to have protection circuitry and short term overload capacity sufficient to handle the switch on and off transients and starting surge associated with Direct Online switching of the motor with the VFD already running at 50 Hz.
For practical purposes that means the VFD rating needs to be about 4 times that of the motor being started. So you need to buy a 4 hp VFD to run a 1 hp motor. Which is an expensive way of going about things even here and now when VFD electronics have dropped considerably in real terms. In general accepting a bit of run up time is a trade-off for a much less costly device. For industrial standards of reliability you need something a bit better than the general run of protection components too.
That said the idea works well when properly done and used within its limitations. I have a 10 hp Plug'n Play system from Drives Direct which has worked just fine for me over the last decade and more. Basically a Teco V/F type VFD modified to give 420 V (nominal) output with a neutral and, presumably, other tweaks to make it reliable. I have set of smoothing chokes hung off the back to help make its life easier. Largest motor is 3 hp and I never have more than about 7 hp worth of motors running at once. Actual power drawn will be less than nameplate as the hydrovane compressor is about the only thing that gets near to full power. So its working well within its theoretical limits. But even then its not having a terribly easy life. Drives Direct say it will start a 5 hp motor. Not it my workshop it doesn't.
Not cheap! At todays prices the 8 VFD boxes I'd need to buy would be more than price competitive if I didn't need to change a two speed motor as well. Although my box has done me well I'd not go that way today.
I'm uncertain about the boxes sold by JFK. They look to be lower end off the shelf 220 volt in 380 volt out Chinese VFD boxes. Probably pretty respectable performers at what they are designed to do, most likely speed reduction control on things like air conditioning fans et al. But whether they have active devices, protection circuits and capacitors able to cope reasonably long term with the thumping transient loads associated with direct-on-line starting of machine motors may be open to doubt. Long term, reasonably bullet proof performance is expensive. Even at China Inc prices.
I'd derate by a factor of 5 and always start the motors running light if I were to get one. I'd not risk a two speed motor.
Frankly at todays prices individual machine VFD boxes is the way to go. If you have a two speed motor bite the bullet and switch to a 4 or 6 pole single speed one to help torque hold up at lower speeds.
You will never see name brand makers producing such devices as the market isn't really there. Home Workshop and some smaller light industrial outfits are about the only people having the need to run several smaller motors on the cheap by converting single phase.
Clive
PS John Haine
They are VFDs. Just with a clever marketing makeover to exploit the inherent overload capcity of a big VFD to run smaller motors direct online.
Edited By Clive Foster on 12/01/2022 22:42:19
Edited By Clive Foster on 12/01/2022 22:42:59
Thank you all for your responses.
Clive- thanks for taking the time to giving me so much detail, it is very informative. I thought they were looking good value for money but I wasn't considering the requirement to oversize to accommodate the starting current. This is a shame and disappointing as it should be taken into account by the manufacturer. I do think that a digital phase convertor could be the ideal solution, perhaps it just needs a couple of years to mature.
Clive I may come back to you for a chat about 2 speed motors once I know specifically what I've got (I pick the mill up this weekend).
Cheers Colin
So you need to buy a 4 hp VFD to run a 1 hp motor.
Simply not true. Most good manufacturers will rate their VFDs for the motor output stated. Motors are clearly not 100% efficient, thus needing more imput than the rated output.
Cheaper ‘hyped’ VFDs may not have that extra capacity.
Starting current only applies for a very short duration and ALL VFDs have a short-duration overload capacity capable of starting motors in nearly all situations. They would trip on over-current if starting was not acieved.
Lastly, oversizing by four times may, in many instances, mean that some safety features could not be programmed (like the maximum safe operation current).
The main difference (apart from price) is that the converter type do not offer anything other than instant three phase supply at 415V. No soft start, or programmable operation.
Now, a single VFD (as they adverise) could certainly be used to drive all your machines at the same time – but that would need to be oversized, by a large factor, for the total additive powers of the motors driven – and would not offer any programming possibility. The only advantage would be the idling power of the VFD would be minimal – not like that of a converter!
Those ‘smaller’ motors would likely not include motors greater than a third (or so) power of the inverter, unless the largest motor were started first.
My advice would be to stick to another VFD to add to your present inventory. Remember, too, that with one failure you lose either one drive (at present) or all of them if using the “plug’n’play” single inverter, when the replacement cost difference would be very substantial.
I am running 5 VFDs at present and would not even consider changing them for a single unit.
A friend is looking at something similar that makes 380v from 220-240v input, but can go up to 60hz, not just the 50hz as the input voltage. So it replicates connecting to a 3phase power supply 380v 60hz. The one he is looking at is not intended to be variable on the 380v output. He has a Hardinge small milling machine that has a constant torque 2 speed motor.
Is there any more information on the units in your link? My simple search came up with not much. Be nice to look at a user manual for one.
Thanks Neil
not done it yet
If you want to use a VFD type box as a 50 hz utility supply substitute and simply switch the motor on with the VFD already running you do need something like 3 or 4 times oversize to reliably handle the starting currents. Don't forget that a voltage doubling VFD already has significantly reduced voltage headroom and over-current capacity compared to one having the same input and output voltages.
If you were to make an electronic device specifically to run at 50 hz and permit direct on line motor switching at any load the motor can start there are, probably, ways of cutting the effective over rating needed. Even so you will need internal components much huskier than a VFD needs.
But if using a VFD box 4 times is about right if you want to reliably start up under full load. Bottom line is that VFD design is optimised to soft start and ramp up from zero to whatever RPM is set without exceeding its internal current ratings. Hook a VFD onto a stiff load like a compressor and you may well find that there is a minimum acceleration ramp time below which the VFD cannot meet the motor demands when bringing the load up to speed so it either stalls out or settles at half speed. Modern vector drives have torque boost settings to give a bit more oomph in the mid range to avoid half speeding. There are good reasons why torque boost shouldn't be the normal setting.
Direct on line starting is just a more extreme example of this, effectively "zero" ramp time. So you need a unit designed for much higher powers to avoid falling foul of the internal settings. For obvious reasons the VFD box has to operate in Voltage/Frequency mode rather than the much more efficient Vector Drive mode which again doesn't help the overload issues.
My Smart & Brown 1024 VSL lathe has no clutch so the motor always starts under load. With a heavy job in the chuck the big Plug'n Play box is clearly working hard to get the 3 hp motor up and running despite its 10 hp rating. Generally if I have a heavy job mounted I'll start another machine first. Usually the drill. The running 3/4 hp motor provides a useful mechanical energy store to draw on as indicated by a slight slow down of the drill. Lathe start up is perceptibly faster. Not an ideal situation so heavy jobs usually go in the P&W which does have a clutch
Just have to accept that you are using a device that is designed and optimised for a different job so you are not going to get theoretical best performance whatever you do.
Clive
Neil
Apart from Phase Perfect and similar devices which are built as industrial 3 phase utility replacement devices with corresponding costs, all these boxes are based on VFD internals so stepping up to 60 hz should be no problem. Certainly the (expensive) ones from Drives Direct will do the deed.
Have to accept that 220 to 380 /420 volt boxes inevitably loose voltage and overload current headroom when compared to normal same input and output voltage devices. But the 50 to 60 hz change will have no noticeable effect.
Clive
Edited By Clive Foster on 13/01/2022 13:12:27
So I phoned the company I linked to and had a chat with them. Of course they are very keen on their product but he explained that they are VFDs that have been reworked specifically to be an alternative to a rotary phase convertor. They are sized to deal with the starting currents of the machines so you don't need to go for the big multiple. His advice is to round up to the next size up.
I do like the idea of these. Perhaps someone on here who is both knowledgeable and a doubler go give them a ring and give them a prope grilling on the subject and report back😀
I am using a modified Teco from drives direct sold as a 'digital phase converter' It works perfectly well and has no problems with DOL starting any and all of my three phase machines. before that, I used a very second-hand, unmodified DDanfoss VFD fed from a step-up transformer, which also did the job perfectly well until one of it's current transformers suffered a failure.
Modern VFDs which have IGBT output stages and current sensing to protect from inadvertent overloads cope with this sort of use with no problems whatsoever. The urban myths about needing a separate one for each motor and all the rest of it are just that:- urban myths. They date from the '80s and are no longer relevant.
Clive,
That particular VFD that Colin has listed states it will manage a single 5.5kW motor. So certainly not needing a VFD rated at four times its power for starting. I agree that for a workshop the total power of the VFD would need to considerably exceed the workshop load. The actual size might need some careful consideration. Indeed, that £700 unit may not be adequate for his application (but he won’t be using everything at the same time). My VFDs can ramp up to the set speed PDQ – unless I program in the soft start. – and they would (should) cope with that instantaneous short term overload
Also, we don’t know whether Colin’s present drives are 240 or 415V. I expect they are currently 230V, so likely wired delta. Some of those motors may not be so easily converted to star, although if modern motors they will simply need the connections changed over.
I expect a large 230V plug’n’play inverter would do the job, without going to 415V. A lot depends on whether all his drives have running protection, too, as they would need it if they are typically powered through a 230V VFDs and are protected by the VFDs. No programmed speed changes available, either – unless all the drives change speed at the same time.
Personally, I think it is a non-starter – unless money is available to burn for no great advantage. Setting up from the start is likely a fair possibility – but not to change so much, for so little extra, and with a lot less flexibility. I most certainly will not be even considering changing my workshop to 415V with a single VFD, but it is everyone’s choice.
As for three phase converters – you can keep thm!
Edited By not done it yet on 13/01/2022 17:09:35
not done it yet
We seem to be getting at cross purposes here.
There is a vast difference between simply starting a naked motor with only a plain shaft to drive and starting one under load.
If you wish to use one of these VFD boxes as a transparent substitute for mains utility three phase it needs to be able to direct online start a motor under the same maximum load as it can manage when fed proper three phase. My experience suggests that the four times derating is prudent to be sure things will always work.
There can be no dispute that under the right conditions a considerably more powerful motor can be handled but defining right conditions given the myriads of potential applications and motor designs is flat out impossible. Possibly the best that could be managed in the real world is for the supplier to define maximum naked shaft motor and maximum fully loaded motor powers. Not going to happen for all sorts of reasons. If its even practical.
My experience with my 10 HP Plug'n Play box is that the 3 hp motors on my Hydrovane 502 compressor and Smart & Brown 1024 lathe are capable of making the box work very hard. Almost certainly pushing it close to the single motor start up limits defined by the overload protection programming.
Under sub-zero conditions the Hydrovane motor does the rurrm-rooom-rummm sound speed hunt as it struggles to pull through the middle of its speed range. Accompanied by nicely flickering shop lights. I know from experience with a similar compressor running with the motor connected in delta off a name brand VFD that the rurrm-rooom-rummm is right on the edge of overload trip for a properly set-up vector drive VFD without torque boost enabled. That one overloaded out maybe one time in three under sub zero conditions. Enabling torque boost was a complete cure. Not such an issue for the bigger Plug'n Play box, which will have considerably more built in overload margin than the matching 3 HP VFD had, but clear indication things are working hard.
If I attempt to start the 1024 with the reeves drive set to maximum direct drive speed contactor chatter due to volt drop in the line feeding the controls accompanied by workshop light flashing is almost certain. My machine has 220 volt contactors running direct off one phase so clearly there is a good deal of voltage drop. Run up is noticeably slower even allowing for the chatter. Something I don't do unless an emergency stop has bollixed plans.
The one time I inadvertently started the 2 hp two speed motor on the P&W lathe with the clutch engaged the box really didn't like it. Realising my mistake immediately I de-clutched about half way through run up and the motor spun up as normal. Two speed motors are notoriously inefficient during start up so its likely that if I'd just left the clutch in the box would have hit its overload limits.
VFD overload protection integrates current, voltage and time to, ideally, protect the box from letting the magic smoke out if a short circuit, or near short circuit, occurs either at start up or when the motor is running. There is no way of knowing what the programming of any specific box is but when using in this manner we have to be sure that the start up surge won't exceed the programmed limits. In the real world 3 times derating seems to be OK with the Teco boxes used by Drives Direct. If, as I suspect, the boxes supplied by JFK are made for lighter duty applications the overload settings will almost certainly be relatively lower so 4 times derate is prudent if you expect to start a motor on full load.
Obviously if you know you aren't going to draw heavy single motor starting loads then a smaller box will do. But folk like us aren't really in a position to know what the real loads will be and how they interact with the programming of the box we have bought. Easy to underspecify. I'm on 3.3 derate and can clearly get quite close to the edge without being silly.
Clive
Clive,
You are missing some things. While using a VFD as a phase converter may work, it is far fom ideal. Apart from the start-up load issues switching loads on a VFD can generate significant voltage transients. These can damage the drive just over-sizing the drive is not good enough to prevent this. VFD's are also not intended to have long leads as would be required if wiring to several machines. This can daamage the drive and will also radiate excessive interference. Almost all VFDs have limitations on powered connection and disconnection of loads and on the length of leads on the VFD output.. These should be observed. Use one VFD per mchine.
Colin,
VFDs are popular because they allow control of the speed, torque, ramp speed (accel and decel) etc but cost litttle more than a phase converter
VFDs do however require one drive per machine.
Rotary phase converters are completely out of date and very inefficent. Not a minor consideration with the rising cost of electricity.
Robert G8RPI.
…
All VFD drives can act as digital phase converters as described by your link. They just need to have protection circuitry and short term overload capacity sufficient to handle the switch on and off transients and starting surge associated with Direct Online switching of the motor with the VFD already running at 50 Hz.
For practical purposes that means the VFD rating needs to be about 4 times that of the motor being started. …
…
A misunderstanding of how VFDs work I think.
A 1HP VFD is designed to run a 1HP motor. The customer doesn't have to allow for surges when looking at ratings because VFD electronics provide a soft start.
The built-in soft-start is one reason why 3-phase to 3-phase VFDs are almost always used these days to drive stop-start 3-phase motors such as fans, lifts and machine tools. By only rationing the motor with just enough power to start it turning and then ramping up relatively slowly, the VFD avoids the massive surge caused when a motor is walloped with power by an ordinary switch or contactor. Managing the surge current is a considerable cost saving, and it means the VFD and associated wiring don't need to heavy duty.
Digital Phase Converters aren't the same as Variable Frequency Drives, Digital Phase Converters are single frequency, outputting whatever the input is, 50 or 60Hz. Their wiring is similar to the Idler Motor method of creating a third-phase, but instead of a noisy, wasteful thicko motor the third phase is generated electronically.
The first two phases are provided directly by Line and Neutral. The single-phase input is also rectified to charge a large capacitor with high-voltage DC, which is then converted electronically to imitate the third phase. In effect the phase of the Line Input is delayed by 'n' degrees to create the third phase. Roughly like this:
Two of the phases are directly connected to the motor, so there's nothing to get hot or go wrong with them. The third phase is more complicated, because it needs a hefty DC power supply, and beefy electronics to switch the output in time with Line frequency, but later.
The electronic phase shifting would be smarter than my diagram implies. Probably a microcontroller monitors all three phases and actively manages the phase shift for best results on every cycle. As microcontrollers are a bit slow, it may be phase shifting is done by something fast like a field programmable gate array, which would push the price up.
Advantages:
Disadvantages:
Whether Digital Phase Converters end up in a home workshop or not depends on cost. In the recent past, they've been expensive, but I see a few units costing less than £1000 are on the web now. It's usual for early adopter electronics prices to start sky high and then plummet as soon as the item becomes ordinary. Maybe these things about to become consumer items. VFDs were Unaffordium not that long ago and now look at them.
Dave
Neil
Apart from Phase Perfect and similar devices which are built as industrial 3 phase utility replacement devices with corresponding costs, all these boxes are based on VFD internals so stepping up to 60 hz should be no problem. Certainly the (expensive) ones from Drives Direct will do the deed.
Have to accept that 220 to 380 /420 volt boxes inevitably loose voltage and overload current headroom when compared to normal same input and output voltage devices. But the 50 to 60 hz change will have no noticeable effect.
Clive
Edited By Clive Foster on 13/01/2022 13:12:27
Hi Clive,
I don't need to ring them. The simple fact that they do not publish a datasheet, never mind an instruction manual on their website means I would not even bother.
Almost certainly the units pictured do not comply with UKCA electrical safety and EMC (interference) regulations. If they have modified them then they will have to re-qualify them.
I'm not too sure about drives direct either.
Robert G8RPI.
So I thought I was relatively well read regarding my options for getting 3 phase into my workshop. I'm picking up a mill so with my lathe I think that makes 5 off 3 phase motors. I was thinking it would be best to go to a rotary phase convertor. Although they are a bit expensive and a bit noisy.
I've just bumped into digital phase convertors whilst online. They seem ideal so why are they not as popular as the VFD's?
Example I've been looking at
Edited By colin hamilton on 12/01/2022 21:03:46
Colin I think that unit would be suitable for your purposes. If as some are stating about heavy load start up, which I doubt you will have then simply fit a soft start unit to that piece of kit.
We fitted soft start units to all heavy compressors at Nestle. The Ingersol Rand Hydrovane compressors had backup Circuit breakers at 150 Amp, so very large units. They were even fitted to all the Air con unit compressors.
Even if you had say a large gearbox in mesh you could unload just for start up purposes
Steve.
So I thought I was relatively well read regarding my options for getting 3 phase into my workshop. I'm picking up a mill so with my lathe I think that makes 5 off 3 phase motors. I was thinking it would be best to go to a rotary phase convertor. Although they are a bit expensive and a bit noisy.
I've just bumped into digital phase convertors whilst online. They seem ideal so
Colin I think that unit would be suitable for your purposes. If as some are stating about heavy load start up, which I doubt you will have then simply fit a soft start unit to that piece of kit.
We fitted soft start units to all heavy compressors at Nestle. The Ingersol Rand Hydrovane compressors had backup Circuit breakers at 150 Amp, so very large units. They were even fitted to all the Air con unit compressors.
Even if you had say a large gearbox in mesh you could unload just for start up purposes
Steve.
Steve thanks for this
Edited By colin hamilton on 14/01/2022 06:27:14
SillyOldDuffer
Nice diagram and explanation of a proper digital phase converter. Thats the sort of thing Phase Perfect in the USA make. By far the best solution technically but very much not cheap, inevitably so. Guess they'd be starting at £4,000 + for a 10 hp box if they came to the UK.
Robert
No data, no brand name, is indeed a very big red flag when it comes to power electronics. Drives Direct seem to know what they are doing and produce boxes that work, even if there are various technical breaches of regulations involved.
I take your point about VFD boxes not being designed for long cable runs and the potential for radiated interference. Mine sits right next door to about £800 worth of box containing hefty chokes and other smoothing devices which nicely deals with those issues. Probably also provides a bit more back isolation protection for the VFD from any motor and switching issues.
That said I've always been a bit sceptical as to whether significant high frequency transients can routinely survive being hooked up to a running motor with its considerable mass of copper and iron along with all the magnetic effects associated with being, effectively, a rotating transformer.
Sitting directly driving an open line now is …..
Hello I'm your aerial today, what can I radiate for you! ….
Basic checks suggest that my smoothing box deals well with any potential radiation issues.
Steviegtr
Putting a soft start box in line to help reduce current demands when starting up under load is an interesting idea. Not sure if its viable as an economy soft start box is very similar in price to a simple VFD of the same power rating. Individual VFD boxes are likely to work out cheaper overall unless you only have one nasty load. The economy soft start boxes only work on one phase so there is a risk that the phase imbalance will trigger the overload programming.
Bottom line is that the only affordable source for the electronics needed to make the sort of device we are discussing are VFD boxes. Although not specifically designed for the job some such capability is inherent which can be exploited even if its officially mis-use. So it just boils down to finding something that will tolerate this mis-use to do the job we want at a viable price.
My experience is that a sufficiently husky VFD box with appropriate smoothing can work very well and reliably when used as a substitute for line power. It may not be strictly to code but it is safe and non-interfering. The key is sufficiently husky. Trying to pare down to you exact needs "today" is risky. Ultimately we are using a device out of its specification so it pays to be gentle.
Clive
A funny thing happened just now, I've had to sit down to recover. I agreed with the whole of a post by SoD.
There is only a current surge when starting an induction motor direct offline because full voltage is applied with the motor not turning. A VFD should control the applied voltage to keep the current within the set parameters. There should be no need to select a VFD of four times the rating. A little over the motor rating may be helpful if using a speed/over-current tradeoff to overcome short terms overloads when running.
My understanding of digital phase converters is the same as SoD. They create two phases from the incoming supply and create a third phase using a half bridge and PWM drive, which is then filtered to provide a sinewave output.
I've got a couple of VFDs on my CNC mill, but for the rest of the workshop I solved the problem once and for all by installing a 3-phase supply. This is particularly useful as some of my machines have two speed motors, and star-delta switching in one case.
Andrew
A funny thing happened just now, I've had to sit down to recover. I agreed with the whole of a post by SoD.
…
Bound to happen sooner or later, like those monkeys eventually typing Shakespeare…
Dave
I thought I was having a bit of deja vu – this was all discussed before in this thread
A funny thing happened just now, I've had to sit down to recover. I agreed with the whole of a post by SoD.
There is only a current surge when starting an induction motor direct offline because full voltage is applied with the motor not turning. A VFD should control the applied voltage to keep the current within the set parameters. There should be no need to select a VFD of four times the rating. A little over the motor rating may be helpful if using a speed/over-current tradeoff to overcome short terms overloads when running.
My understanding of digital phase converters is the same as SoD. They create two phases from the incoming supply and create a third phase using a half bridge and PWM drive, which is then filtered to provide a sinewave output.
I've got a couple of VFDs on my CNC mill, but for the rest of the workshop I solved the problem once and for all by installing a 3-phase supply. This is particularly useful as some of my machines have two speed motors, and star-delta switching in one case.
Andrew
It's unusual but I have to disagree with you a bit Andrew,
VFDs are intended to be permanently connected to a motor and control start-up currents when they are commanded to start the motor. Even if set to maximum speed at turn-on there is some ramp up. Some also increase the current limit during ramp up at maximum rate. If you turn the VFD on and then switch a load onto it the only protection is the over-current. This is a fault condition and exceeding it will trip the drive off-line. Thus it has to be set high and may also be part of the 4x oversize recommendation. Of course setting the current limit high means the motor is no longer protected against over-load.
Starting a smaller motor first has also been mentioned on this thread and even running an un-loaded motor permanently connected is suggested by some sources. Not very efficient.
I'm not making this up I've had a serious look at and experimented with using VFDs as 3 phase converters. Just the amount of filtering required to tame the emissions when running off load was a show stopper.
Robert G8RPI.
Home › Forums › General Questions › Topics
Started by: jon hill 3
in: Related Hobbies including Vehicle Restoration
Michael Gilligan
Started by: Richard Simpson
in: Model Boats
JasonB
Started by: JohnF
in: Hints And Tips for model engineers
JohnF
Started by: David George 1
in: CAD – Technical drawing & design
David George 1
Started by: Jeff Barnett
in: Help and Assistance! (Offered or Wanted)
Bob Worsley
Started by: Steve355
in: General Questions
Steve355
Started by: peak4
in: The Tea Room
Howard Lewis
Started by: Dell
in: The Tea Room
Michael Gilligan
Started by: David Deaville
in: General Questions
Stuart Smith 5
Started by: Chris12
in: Beginners questions
MarkS
Started by: ell81
in: Beginners questions
noel shelley
Started by: ell81
in: Beginners questions
Martin Connelly
Started by: JasonB
in: The Tea Room
Diogenes
Started by: Steve Hunt
in: Help and Assistance! (Offered or Wanted)
Steve Hunt
Started by: glynboy12
in: Beginners questions
noel shelley
Started by: colin hamilton
in: General Questions
Michael Gilligan
Started by: Richard Simpson
in: Miscellaneous models
Richard Simpson
Started by: Vic
in: Workshop Tools and Tooling
Nicholas Farr
Started by: Richard Simpson
in: Stationary engines
Howard Lewis
Started by: Steve355
in: General Questions
dk0
Started by: Peter Neill 1
in: Workshop Tools and Tooling
Pete
Started by: Chris12
in: General Questions
Chris12
Started by: John MC
in: The Tea Room
Robert Atkinson 2
Started by: Michael Gilligan
in: Electronics in the Workshop
Michael Gilligan
Started by: Greensands
in: The Tea Room
blowlamp