Posted by Emgee on 04/02/2022 10:04:39:
Posted by petro1head on 04/02/2022 09:12:13:
Don't have any understanding of these relays, how would it protect the motor?
By reducing the start up current to allow the use of a Fast acting fuse rated close to the motor plate flc.
Still IMO best to have the protection of an overload set to flc.
Emgee
I, for one would not rely on a fuse for protection as some can quite easily remain closed circuit at approaching 150% of their load rating, for longer than one might expect – particularly the usual BS1362 spec. type that has some considerable thermal resilience but is not specifically rated as slow-blow.
The way to go is as Noel pointed out (virtually?) at the beginning of this thread. Common sense, simple, effective solution to motor stalls/overloads – provided the overload settings are set up properly, of course.
At one place where I worked, there were several hundred (possibly over a thousand) motors, ranging from 6000 to fractional horse power. None were directly protected by fuses. Nearly all were fitted with thermal overloads within the starter, or other overload protection. I suppose one might say it is is simply the industrial standard for operating electric motors.
Fuses were there to protect the wiring from the supply to the machine, not to protect the motor.