Oh. Check your speeds as it will only probably run at 2/3 speed on 230v and will probably stall if any load is applied.
Extract from Inverter drive website. The motor must now be considered as a 230V x 29Hz motor as far as data entry into the Inverter Drive is concerned. The Full Load Current will be that stated on the nameplate for 400V.
If the maximum speed is set to 50Hz or more, the Motor may possibly reach these speeds, but it will become progressively "Under-Fluxed" (Torque will reduce). However, this will only be evident if the Motor is fully loaded. If it is, the Motor will look for more current to meet the load. A correctly set Inverter will provide protection against over-Current by reducing the speed automatically to bring the load current under the maximum set.
It is important to note that when the Inverter output voltage does not match the Motor rated voltage, the drive should match or exceed the Motor full load current (not kW).
The link to your inverter is blocked by my malware software so could not check it out. You will need to really study your VFD settings to get much use out of that motor.
I hope this has not put the cat amongst the pigeons. 
regards
Edited By Oldiron on 06/12/2019 14:31:16