  • #22909
    ianj
    Participant
      @ians

      Alspa VF( VF 2004A ) converter manual/instructions

      Advert
      #133246
      ianj
      Participant
        @ians

        Hi.

        I've been given a Alspa VF (model VF 2004A) 230VAC single phase in to 230vAC 3 phase out, but there is no instruction manual with it. Does any one have a copy of the instructions I could buy ? I hope to use this converter for the main motor on my mill ( dual voltage)

        The coolant pump on my milling machine has the following information on it:-

        3 phase

        380/220 volts

        .12/.22 amps

        what would be a typical value of the capacitor needed to run it from single phase ( I have configured it for DELTA 230 v working) Also what type of capacitor is used ( I've read that an electrolytic is not suitable)

        I have tried a 30uF and the motor runs but appears to soon get hot.

        Regards Ian

        #133252
        Sub Mandrel
        Participant
          @submandrel

          Is it not possible to run it off the converter as well as the mill? I thought you could do this with some types of converter.

          Neil

          #133257
          KWIL
          Participant
            @kwil

            My suds pumps run from the same lines as the motor, all on 3 phase, Compared with the spindle motor the suds pump goes unnoticed.

            #133263
            ianj
            Participant
              @ians

              Thanks for the replies.

              If I have the suds pump working off the converter/inverter the speed will be altered as I vary the spindle speed, also I understand that you should not have any switches/relay contacts between the inverter o/p & motor, therefore the suds pump would be running all the time the spindle motor is running.

              Ian

              #133278
              Gray62
              Participant
                @gray62

                Ian,

                For your suds pump, a 3-4 uf capacitor should be fine, my 1/8 HP suds pump is running on a 4 uf cap and it never gets hot.

                You need a motor run type of capacitor, these are non-polarised. A electrolytic cap is not suitable in this application.

                Also ensure that the cap is rated at least 300v. Most run caps are rated at around 450v, certainly nothing less than 250v.

                CB

                Edited By CoalBurner on 21/10/2013 17:58:19

                #133355
                ianj
                Participant
                  @ians

                  CB.

                  Thanks for that. I've had it running using a 3uf capacitor for 3 hrs & it just gets aired.

                  Ian

                  #133365
                  Sub Mandrel
                  Participant
                    @submandrel

                    A Ian, I assumed you probably had a rotary converter, as you didn't say it was an inverter.

                    Looks like you are sorted now though,

                    Neil

                    #133375
                    ianj
                    Participant
                      @ians

                      Neil.

                      Yes it's my fault by mixing up converter & inverter & confusing people !!

                      Ian

                    Viewing 9 posts - 1 through 9 (of 9 total)
                    • Please log in to reply to this topic. Registering is free and easy using the links on the menu at the top of this page.

                    Advert

                    Latest Replies

                    Home Forums General Questions Topics

                    Viewing 25 topics - 1 through 25 (of 25 total)
                    Viewing 25 topics - 1 through 25 (of 25 total)

                    View full reply list.

                    Advert

                    Newsletter Sign-up