Posted by Emgee on 08/01/2017 11:30:48:
Posted by Rick Kirkland 1 on 08/01/2017 09:49:29:
And before ANYBODY starts shouting about the onsite guide, that is ALL it is, , a guide. I look at certificates where the column asking for the " max Zs permitted under BS7671" is put down as one of the figures from a table in the onsite guide. TOTALLY WRONG.
Edited By Rick Kirkland 1 on 08/01/2017 09:51:16
Hi Rick
If the Zs table (A41.1to A41.6?) in the on-site guide is copied from and the same as that included in BS7671 why is it wrong to enter the Max Zs permitted for the cct by reference to a table of values ? provided of course the correct part of the table is selected for the type and rating of the protective device and maximum disconnection time for the cct.
The cct measured Zs value will be written in the relevant column in the test readings to check compliance.
Emgee
I have to admit I am not clear what Rick means, the on site guide tables are not the same as BS7671 as the on-site has a 0.8 correction factor to take into account conductor temperature. I wonder if he is referring to Cmin, I don't have the latest copy of the guide to check if that is now included in the tables.
Or maybe Rick is refering to circuits with RCDs where Zs can exceed this figures (but Zln should not….). Actually that is something that has always annoyed me, the certs (and hence what most people test) concentrates on Zs, completely ignoring that it still needs to work with a Line-Neutral fault.
EDIT: but yes, Rick's post above mine and Russell before that are right, I am also going to shut up now 
Edited By Toby on 08/01/2017 12:00:05