you are correct Rob, the individual (narrower) switches are over current breakers (called MCBs or miniature circuit breakers) and the one at the end (normally double width) is an RCD (residual current device or earth leakage breaker). The RCD being in series with all the MCBs.
The RCD is almost certainly 30mA rated so is specced to trip if there is 30mA flowing to earth for more than 200ms or 40ms if more than 150mA. Often the actual leakage required to trip it is as low as 20 to 25mA.
This leakage is measured as a difference between the line and neutral currents, the assumption being that what is "missing" must have flowed to earth. So the trip can be caused by either a line to earth fault or a neutral to earth fault (neutral is rarely at exactly earth potential).
There are two main reasons why this can happen.
1) a capacitive link between live (line or neutral) and earth. This can be just capacitance in motor windings or it can be caused by a fault.
2) a low resistance to earth from the line or neutral, normally caused by a fault or breakdown in insulation. Quite often caused by damp or water ingress. Or, in the case of a motor a short (or partial short) of a winding to the motor core.
Unfortunately these things are hard to find without specialist test kit. You need to be able to measure insulation resistance at at least 250V and also measure mA leakage currents with peak hold to detect startup pulses.
One thing to watch is that it might not be just the fan that is causing the problem. There could be (in fact probably is…) a general earth leakage from other devices on the affected circuits. Most electronic goods have noise filters on which cause a small earth leakage. It might be that your "background" leakage is say 20mA and it works fine. But plug in something with an additional 5mA leakage and it suddenly trips. This can unfortunately make fault finding harder!
All that said, I would start with the basics:
1) a visual inspection of all the wiring, switches, control circuits and the motor. Any sign of damage or contamination by water or dirt, oil etc?
2) If you have a multimeter, check the resistance from line and neutral to earth, with the unit switched on(but obviously not connected to the mains!). If there are any electronics inside that will complicate things so you might have to disconnect various bits and test them in isolation. Also make sure it is really switched on. Any no volt release switches will obviously complicated things. Any resistance less 2MOhms is suspicious in my view (although you need to be down to around 10kOhm to cause a trip).
3) call an electrician
although be prepared for the electrician to say "the fan is faulty, replace it" so you might be better off with an appliance repair man.
I hope this helps…..
Toby