Running multiple motors from a single VFD is common in industry, especially on pump stations and Fan type cooling towers.
Generally ALL manufacturers recommend:
All motors are started together.
VFD rating to be equal plus 20% to sum of all motors stalled rotor currents.
If motors are to be started and stopped individually on the VFD OUTPUT side ( VFD is not shut down during motor switch-over), then , for example, if two motors are used on one VFD:
The motors must be of the same rating.
At least one motor must always be running.
If of dissimilar ratings, only the SMALLER motor may be stopped and started on the VFD output side, while the other is running. Doing it the other way around results in a massive load-dump condition,with resulting high voltage fed back into the VFD.
If only ONE motor is left running, it can only be stopped by shutting the VFD down , NOT by disconnecting it ( via a contactor for example) on the VFD output side.
This all has to do with load dumping, and the VFD sensing the current demand and adjusting the PWM frequency of the output voltage, and hence the RMS value of the output 3 phase AC waveform. Suddenly disconnecting the load results in a massive jump in voltage, invariably popping the VFD outputs. Likewise, disconnected a high rating motor while a smaller rated one is still connected will result in large current flow for some hundreds of milliseconds, as the VFD adjusts its output – most often triggering and over-volt condition, and shutdown.
Also, it is mandatory that each motor is fitted with overload relays/sensors, as the VFD can no longer perform that function with multiple motors.
You may get away with flouting these recommendations, but probably not for long..
Joe