Stuart Bridger20/03/2017 21:58:21
151 forum posts
6 photos

If you check out the table on p98 of the yaskawa manual, it states that .55kw (listed as 1.1 kVA) is unit is suitable for up to 0.5 HP motor and delivers 3A max. So it does look like you are under sized. A 1.9kVA unit will give you 5A output, suitable for a 1HP motor.

Regards

Stuart

Neil Wyatt20/03/2017 22:10:05
avatar
Moderator
9275 forum posts
468 photos
58 articles
Posted by John Stevenson on 20/03/2017 21:26:16:

What's with this kVA?

Seeing as no motor I have seen list the spec in kVA only amps why would anyone want to read the spec in kVA when the direct comparison in AMPS is on the plate ???

I think the reason is you can make a half-horse power inverter sound like a three-quarter horse power inverter if you use kVA instead of kW.

What's not to like? crying

Neil Wyatt20/03/2017 22:15:45
avatar
Moderator
9275 forum posts
468 photos
58 articles
Posted by Stuart Bridger on 20/03/2017 21:58:21:

If you check out the table on p98 of the yaskawa manual, it states that .55kw (listed as 1.1 kVA) is unit is suitable for up to 0.5 HP motor and delivers 3A max. So it does look like you are under sized. A 1.9kVA unit will give you 5A output, suitable for a 1HP motor.

Regards

Stuart

Indeed, the 0.6kVA one is for motors of up to just 250 watts.

Neil

Brian Oldford21/03/2017 08:36:45
289 forum posts
4 photos

Wow! Loads to think about there. I'll get some answers to the various questions from folks trying to help asap. The evidence so far strongly suggests I simply need a bigger VFD, Many thanks for all the contributions.

Toby21/03/2017 13:29:24
112 forum posts
17 photos

fwiw, the motor on my Meddings drill is 0.75HP and is rated at 1.7A FLA for 440V star and 3A FLA for 240V delta. Running it as delta from an inverter (with about 240V out) and the inverter (a yaskawa) reads 1.7A no load and around 1.8A when drilling a 1" hole through steel. So it never gets anywhere near its 3A FLA.

So yes, 5A means there is something wrong.......

(btw the inverter I use is a Yaskawa J1000 (0.75kw/0.4kW)

Edited By Toby on 21/03/2017 13:30:34

Neil Wyatt21/03/2017 13:42:40
avatar
Moderator
9275 forum posts
468 photos
58 articles
Posted by Toby on 21/03/2017 13:29:24:

fwiw, the motor on my Meddings drill is 0.75HP and is rated at 1.7A FLA for 440V star and 3A FLA for 240V delta. Running it as delta from an inverter (with about 240V out) and the inverter (a yaskawa) reads 1.7A no load and around 1.8A when drilling a 1" hole through steel. So it never gets anywhere near its 3A FLA.

So yes, 5A means there is something wrong.......

Running the motor on a low voltage may be part of the problem, if the motor isn't getting up to speed it will draw extra amps despite the lower voltage.

Neil

Muzzer21/03/2017 14:30:41
avatar
1896 forum posts
333 photos

Current is basically proportional to torque - with a small additional magnetisation current - and the output voltage is roughly proportional to speed. Assuming you have set up the VFD with the correct nameplate info (particularly the number of poles or base speed and the phase-phase voltage), there isn't a whole lot to get wrong.

You can develop a significant motor current (torque) at low speed but the corresponding motor voltage will be low, so the net corresponding (real) power at either the input or the output will be low. The % efficiency of a modern VFD will be in the high 90s at rated output and obviously will be zero at stall.

The reason for specifying VA is because motors are fairly inductive (poor power factor) and the phase current isn't in phase with the drive voltage. The shaft power is developed by the real power (W), while the reactive power is basically recirculated. The power factor at the VFD input is fairly close to unity (not least due to legislation), so the big discrepancy between VA and W only really arises on the output.

If the VFD load were purely resistive, the VA and W would measure the same. Conversely, if it were purely inductive, the VA would be high and the W would be zero - and the VFD input power would only have to cover resistive losses.

When you are designing a VFD, the DC bus voltage is generally well defined and the main critical parameter is the output phase current. With IGBTs, it is the average AC phase current that matters. With a FET output stage it would be RMS current - but 200V and 400V class VFDs use IGBTs.

Murray

Brian Oldford21/03/2017 14:56:47
289 forum posts
4 photos
Posted by Neil Wyatt on 21/03/2017 13:42:40:

Running the motor on a low voltage may be part of the problem, if the motor isn't getting up to speed it will draw extra amps despite the lower voltage.

Neil

I'm gradually getting there. Quite right Neil, the extra current is caused due to the lack of back emf because of the low revs.

Brian Oldford21/03/2017 14:58:51
289 forum posts
4 photos
Posted by Muzzer on 21/03/2017 14:30:41:. . . . .

The reason for specifying VA is because motors are fairly inductive (poor power factor) and the phase current isn't in phase with the drive voltage. The shaft power is developed by the real power (W), while the reactive power is basically recirculated. The power factor at the VFD input is fairly close to unity (not least due to legislation), so the big discrepancy between VA and W only really arises on the output.

. . . . .

Murray

For those with an electronics background CIVIL.

Brian Oldford21/03/2017 15:02:10
289 forum posts
4 photos

I'm in the process of borrowing another (higher rated) inverter and (in my bits box) have found a spare 1/3HP 3 phase motor which will easily re-wire to delta. I'll report back when I have some more results. Thanks again for all the valuable input.

Andrew Johnston21/03/2017 15:05:43
avatar
3031 forum posts
355 photos
Posted by Brian Oldford on 21/03/2017 14:56:47:

I'm gradually getting there. Quite right Neil, the extra current is caused due to the lack of back emf because of the low revs.

For an induction motor surely the speed is primarily determined by the supply frequency (and number of poles), not by applied voltage. So if the motor is not getting up to the speed expected for the supply frequency then there is something wrong, probably with the motor. Does the motor get hot?

Andrew

Neil Wyatt21/03/2017 15:28:29
avatar
Moderator
9275 forum posts
468 photos
58 articles
Posted by Andrew Johnston on 21/03/2017 15:05:43:
Posted by Brian Oldford on 21/03/2017 14:56:47:

I'm gradually getting there. Quite right Neil, the extra current is caused due to the lack of back emf because of the low revs.

For an induction motor surely the speed is primarily determined by the supply frequency (and number of poles), not by applied voltage. So if the motor is not getting up to the speed expected for the supply frequency then there is something wrong, probably with the motor. Does the motor get hot?

Andrew

My guess is that a motor run at less than half voltage (110 instead of 240) will slip a lot and therefore be a lot less efficient.

N.

john fletcher 121/03/2017 16:09:37
302 forum posts

Are you absolutely sure you have the motor configured in DELTA. I know you said in para 3 that you had been careful , a mate of mine said the same when he altered a motor, then we found he was wrong, we all make mistakes. I have the same inverter (pre owned as the car salesman would say) running an old 746 watt motor, no problem. Have you got all the setting correct, especially the voltage. As some member here may recall, I had the inverter for 4/5 years but couldn't get motor to run below 500rpm, try as a may. Later, I requested assistance here and a member told me I had a particular item set at 50 instead of zero, job done, I was very grateful, I had overlooked the same problem many times.John

Joseph Noci 121/03/2017 16:46:57
48 forum posts
127 photos

Hi again Brian...Joe again...

You have not answered any of the questions I put to you...I think you need to at least verify that the inverter is set up OK, esp the Voltage versus Frequency curve. That should at least be set to the 50Hz general application factory settings to start with. Then a good test is to set the inverter output to 50Hz and try to measure shaft RPM. If it is what you expect, then all the issues mentioned related to motor not achieving speed, back EMF, etc are moot.. In which case there is either a mis-wiring issue, which I would strongly suspect.

It would help the diagnosis though if you could answer some of my questions related to the fault displayed, and the mode of the fault...

And of course a connection to utility mains supply would help eliminate the inverter as a culprit..

Generally ( within limits) applied voltage does not affect speed, but reducing the applied frequency ( hence rotational speed) does require that the applied voltage be reduced as well ( that's why there is a V/f curve that needs tailoring for motor types..) in order to match the back EMF, and that is why the torque falls off so badly at low RPM.

Regards

Joe

Brian Oldford21/03/2017 17:52:37
289 forum posts
4 photos

Right gents. I'm 99% sure I've cracked the problem. Once again thanks for all the ideas and input.

I rewired the 1/3HP motor to delta, connected it to the inverter, set the relevant parameters so they passed a sanity check, powered it up and it spun up perfectly and I was able to vary the speed both below and above 1425rpm by varying the output frequency.

I then put the inverter back onto the 3/4HP motor and did a bit of voltage monitoring and also discovered the motor is failing to spin up properly. This phenomena is something I missed the first time round. What I'm getting is massive voltage droop (because of the excessive load) preventing the motor spinning up to produce a decent back emf to limit the current. i.e. the inverter was trying its darndest to deliver the goods but the motor was just that little bit too much and was eventually having to self protect its transistors.

Not having experience of the soft start properties of these inverters produce added to the confusion in my mind.

I'll report back again, hopefully with a happy ending to conclude this tale, when the bigger inverter arrives.

Brian Oldford26/03/2017 15:16:30
289 forum posts
4 photos

Just a quick note as an epilogue to this tale/learning curve. The larger VFD is connected to the 3/4HP motor and, once the VFD was configured correctly the motor spun up perfectly and was controllable from less than a few hundred rpm to 20% over-speed (60Hz).

The smaller inverter has been allocated to the Dore Westbury mill.and will be brought into use once the existing single phase 1/4HP motor has been replaced with the 1/3HP three phase one. Fortunately all motors were four pole.

Once again thanks for all the useful hints and tips from the many posters on this thread.

SillyOldDuffer26/03/2017 15:31:01
1083 forum posts
253 photos

Thanks for the feedback Brian - well done you!

As a matter of interest how much current does the new vfd say the motor is pulling?

Ta,

Dave

Brian Oldford26/03/2017 22:00:58
289 forum posts
4 photos
Posted by SillyOldDuffer on 26/03/2017 15:31:01:

Thanks for the feedback Brian - well done you!

As a matter of interest how much current does the new vfd say the motor is pulling?

Ta,

Dave

A quick check "off-load" says it's less than 1A/phase when driven at 50 Hz.

I'll live with than

All Topics | Latest Posts

Please login to post a reply.

Email News - Join our newsletter

Love Model Engineering? Sign up to our emails for the latest news and special offers!

Latest Forum Posts
Support Our Partners
Ausee.com.au
emcomachinetools
Eccentric Engineering
Meridienne Exhibitions Ltd
Reeves 2000
TRANSWAVE Converters
Advertise With Us
Allendale Electronics
PaulTheCad
ChesterUK
Warco
Subscription Offer

Latest "For Sale" Ads
Latest "Wanted" Ads
Get In Touch!

Do you want to contact the Model Engineer and Model Engineers' Workshop team?

You can contact us by phone, mail or email about the magazines including becoming a contributor, submitting reader's letters or making queries about articles. You can also get in touch about this website, advertising or other general issues.

Click THIS LINK for full contact details.

For subscription issues please see THIS LINK.

Digital Back Issues

Social Media online

'Like' us on Facebook
Follow us on Facebook

Follow us on Twitter
 Twitter Logo

Pin us on Pinterest

Visit the Model Engineer
Exhibition website

Model Engineer Exhibition